Customer Question
I have a air...

I have a air temp furnace that was installed last summer, it worked fine through the summer and winter season, I tried cutting the heat on and it won't light. The inducer motor comes on the hot surface ingitor glow bright but the gas valve is not opening - the diagnostic lights are alternating which means 1 hour locket, but the unit is not re-cycling

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

Yes I kill the power over night and the same thing happened

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, I brought the unit last year but can't find the warranty

Contractor's Assistant: Anything else we should know to help you best?

I have been trouble shooting it for 3 days now, I checked to see if I had 24 V going to the gas valve and it did, also I have continuity on the valve

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
11/7/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,401
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. Is the gas on to the unit?

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Then you either have a bad gas vlave or a clogged burner orifice. The burner adjacent to the igniter. I asked about the gas because it's very unusual for a gas valve to fail so soon. But it does happen.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Rick I'm driving
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Ok, then you shouldn't be typing

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Right! I will hit you back
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

OK

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have trane model ycc042f1m0bc outside in north carolina. no
have trane model ycc042f1m0bc outside in north carolina. no heat coming out. opened panel, fan is working immediately upon turning it on. Not sure if that's blower or induction fan. Can hear spark goi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have Gas Rheem furnace that does not heat. At the very end
Good morning, I have Gas Rheem furnace that does not heat. At the very end of last winter season it stopped working. The AC has worked fine this summer but when I went to take a look at it this weeken… read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
I have a rheem furnace model rgvg-07eamgr. When heat is called
I have a rheem furnace model rgvg-07eamgr. When heat is called for, the induction fan comes on and the hot surface igniter glows but burners don't come on. When it recycles, burners may come on but no… read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
Sounds like I have the same problem but put in a brand new
Sounds like I have the same problem but put in a brand new flame sensor. 2 flashes and not lighting… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a heil sp80 furance which doesn't seem to ignite consistently.
I have a heil sp80 furance which doesn't seem to ignite consistently. the inducer motor turns on and the pressure switch clicks and sends signal to the gas valve ,but one time it will fire in about a … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
lennox g26 propane furnace. no gas through gas valve. i don't
lennox g26 propane furnace. no gas through gas valve. i don't think it is getting 24 volts, if i checked it correctly. bad board?… read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
I have a trane xe90 tuco 80c942a i recently had the hot serface
I have a trane xe90 tuco 80c942a i recently had the hot serface igniter replaced furnance ran for a day now wont light inducer motor runs igniter glows but no gas from burners to light… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Amana Air command 80 Heater. Blower turns on, Glow plug lights
Amana Air command 80 Heater. Blower turns on, Glow plug lights bright but 3 or 4 times a week I will not hear the slight click of the gas being fired. The glow plug will keep going bright then off unt… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My gas furnace will not ignite. Here is the initial cycle.
My gas furnace will not ignite. Here is the initial cycle. Post reset, a call for heat is made. The inducer motor spins up. I hear a click (pressure switch), another click (gas valve opening) and gas … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
i have an older model ruud furnace the model number on the
i have an older model ruud furnace the model number on the plate is R-24-SCU the serieal number is XXXXX i can turn thermostat up to above room temperature and i hear a click and can hear gas flowing … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Coleman model DGAA077BDTA serial no. XXXXXXXXX 77000 input
Coleman model DGAA077BDTA serial no. XXXXXXXXX 77000 input with hot surface igniter. This is a mfg. housing furnace and has been in service for 8 years. Near the end of the heating season last year, t… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi. I have an older DMO Industries Model HDS-80M furnace that
Hi. I have an older DMO Industries Model HDS-80M furnace that works - however, this past winter it started to emit what smells like raw gas from the exhast just after it starts up. The smell dissipate… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
You helped me with a 1988 Rheem 80 Plus. Model # RGDE 07NMAGR
You helped me with a 1988 Rheem 80 Plus. Model # XXXXX 07NMAGR AG5D307. Draft induce fan starts, hot surface glows bright yellow and gas valve only gets around 16 volts and does not open. There is no … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I just asked a question but failed to direct it to you at first.
I just asked a question but failed to direct it to you at first. 2 weeks ago you helped me with a 1988 built Rheem 80 Plus. Model # XXXXX 07NMAGR AG5D307. Draft induce fan starts, hot surface glows br… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a ruud silhouette ii that stops at step 6 of the below
I have a ruud silhouette ii that stops at step 6 of the below sequence, so I'm not sure if the gas valve is opening. 1. Draft inducer blower starts. 2. Draft inducer switch proves pressure. 3. Ignitio… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My mobile home Coleman Evcon gas heat and ac will not ignite.the
My mobile home Coleman Evcon gas heat and ac will not ignite.the ac works ok. Model DGAT075BDD-SER.NO.954235732.iT WAS WORKING GOOD LAST WINTER. THANKS [email protected]… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane TUC040C gas furnace. It has been installed
I have a Trane TUC040C gas furnace. It has been installed for about 9 years. The furnace runs on propane. The last few seasons the furnace would not light after 3 tries and would need to be reset. The… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently tried to turn on the furnace and the igniter glowed
I recently tried to turn on the furnace and the igniter glowed but the burners did not ignite and the green light started blinking..it worked fine this summer in air conditioner mode...is there a rese… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x