will you find me a wifi thermostat that will keep temp +-1 degree of my setting of 74 degree.. ?
the cut-in/cut-out will be controlled by a timer instead of a wide 4 degree temp range
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/5/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,709
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, most modern programmable thermostats have adjustable differential settings, most in the 1 to 2 degree F range, some in the 0.5F range, if yours is showing a 4 degree differential it may just be improperly programmed... get me the brand and model number from the back of the thermostat after you gently pry it from the wall and I will pull the manual for you if its available.

Also tell me what color of wire attaches to each lettered terminal on the wall mount plate that the thermostat is mounted on.... from that I will be able to specify a new thermostat.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
honeywell model rth6580wf 1001terminal wire color
W2. Wht
G. Grn
W. Org
C. Blu
Y. Yel
R. Red
Rc Jumper to R term
Customer reply replied 8 months ago
terminal---- wire color
W2. ----------Wht
G. ------------Grn
W. --------------Org
C. ----------------Blu
Y. -----------------Yel
R. ----------------Red
Rc -----------------Jumper to R term

Thanks any thermostat described as:

24volt, 2 stage heat, 1 or 2 stage cool, conventional system will work. If you want to buy it at the local hardware store, all brands are good except Lux which seems to not last as long as the others.

If I specify one you may not be able to pick it up locally.... tell me if you want to order it on line or not, if you want to wait a day or two for it to arrive from online sources I will specify one for you.... prices range between $40 and a few hundred dollars depending on features.

Tell me which features you want:

Non programmable (simplest, cheapest)

Simple programmable, more complex to program but also not expensive

WIFI enabled controlled from smart phone ( several hundred dollars)

We can go from there.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
show me WIFI enabled controlled from smart phone
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,709
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
i can not find which one has a +-1 degree for cut-in/cut-out
Customer reply replied 8 months ago
my heatset point is 71 and cool set point is 74. there is always a 3 degrees between the points

All of those thermostats have differential settings, its covered in their lengthy installation manuals... most have differentials settable to 0.5F

Ask Your Own HVAC Question

click on a thermostat, then scroll to the bottom of the page for its manuals

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,709
9,709 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,709 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a T5 -7 day programmable thermostat, RTH7560E. We do
we have a T5 -7 day programmable thermostat, RTH7560E. We do not have an owners manual. It is programmed but it is stuck on air conditioner and we cannot get the furnace to click on. It keeps flipping… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a lennox 4 ton high effiency 16 sear unit installed
I have a lennox 4 ton high effiency 16 sear unit installed 3/2016. my unit on heat not a heat pump has heat strips .the unit thermostat is set at 74 degrees now. the unit starts up and runs 3 min cuts… read more
hvacdave84
hvacdave84
53 satisfied customers
See screenshot pics and pdf attachments how do I set the
see screenshot pics and pdf attachments how do I set the Honeywell wifi thermostat to switch between heat on or cool on automatic? I have temps set at 76 and 75. see pics RTH6500WF Wi-Fi Series… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Honeywell thermostat rth2310b keeps flashing 'filter' and is
Honeywell thermostat rth2310b keeps flashing 'filter' and is at 84 degrees fahrenheit instead of the 74 we prefer. The 'p#' setup has a mystery box with day or night, one to 4 people, etc. We changed … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,707 satisfied customers
My Infinity Control thermostat was set at 76 and it kicked
My Infinity Control thermostat was set for cooling at 76 and it kicked in at 74. It rarely does that but it happened today. Most of the time it start or stops at the designated temperature. It's an in… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have the TRANE Comfort Link II XL950 Control. I had the
I have the TRANE Comfort Link II XL950 Control. I had the thermostat set at 78 degrees, and up to today the system went IDLE when the temp fell below my thermostat setting. Just recently, the fan keep… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi, I live in a recently purchased townhome in Olathe, KS.
Hi, I live in a recently purchased townhome in Olathe, KS. Very cold here for past couple weeks. Townhome built in 08 and has a White-Rodgers (non-programable) thermostat that appears to be a very bas… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
We just installed a Honeywell 7 day Programmable Thermostat.
We just installed a Honeywell 7 day Programmable Thermostat. It is not cooling. We are looking online to see if we can figure out the instructions, and still not cooling. We have determined we have a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a White Rodgers 1F80-261 thermostat. I had to change
I have a White Rodgers 1F80-261 thermostat. I had to change the batteries, and then reset the settings, which I'd never done before. I came to a setting that says 0 HI (0) and then it gives me somethi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Honeywell model TH6110D Thermostat (operating in the manual
Honeywell model TH6110D Thermostat: (operating in the manual mode) After setting the desired heat setting 74. Should the heat setting temp drop 1 degree before the the heat on indicator and furnace co… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
THE THERMOSTAT IS SET ON COOL AT 77 DEGREES BUT THE TEMP IS
THE THERMOSTAT IS SET ON COOL AT 77 DEGREES BUT THE TEMP IS 74 DEGREES. THE AIRCONDITION IS RUNNING THINKING THAT THE HOUSE IS 77 DEGREES WHEN REALLY IT IS 74 DEGREES HOW DO YOU ADJUST SO IF THE ROOM … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a dual fuel HVAV system, gas furnace and heatpump. My
I have a dual fuel HVAV system, gas furnace and heatpump. My problem over the last few years is that under a particular set of circumstances my gas furnance will come on and can't be shut down until t… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
our honeywell thermostat will not go below 74 degrees when
our honeywell thermostat will not go below 74 degrees when on AC. is there a way to reset that function?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a York PS9 thats about 5 years old. It is tied in with
I have a York PS9 that's about 5 years old. It is tied in with a York Central AC. The house is 2 stories. When the AC kicks in it appears that the furnace motor is in low gear...meaning I feel very li… read more
Joan-Mod
Joan-Mod
Private
I have a Honeywell thermostat #RTH221B1000 and cant figure
I have a Honeywell thermostat #RTH221B1000 and can't figure out how to set the temp. I don't care about day and time. PLEASE help!… read more
John
John
High School or GED
27 satisfied customers
I have and Old weil mclain gas boilers, and i set the temp
I have and Old weil mclain gas boilers, and i set the temp to 74 degrees ..When the temp get to 74 degrees, the boiler don't stop, it keeps burning...This is new thermostat..What could be the problem?… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I am a condo renter in which a new AC/heat unit was recently
I am a condo renter in which a new AC/heat unit was recently installed-to replace the prior 36-year old unit. I have had 2 days experience now with the new unit in which I set the digital thermostat t… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
What should the pressures be on a R-22 commercial refrigeration
What should the pressures be on a R-22 commercial refrigeration unit with a start up box temperature of 74 degrees and a condenser ambient air temp. of 82 degrees. Condensing unit is 3/4 h.p. and the … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x