The yellow wire on...

The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose and has 65VAC when the moter is powered up.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

We heard sparking noises for about a week. I took the cover off tonight abd saw the yellow wire bare spot sparking to the duct.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

No, I'm wondering if I need to but a new blower motor.

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
10/24/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

This should not need a new motor. Repair/tape the bad wire. As long as any worn spots are covered you should be fine.

Was the yellow wire a spare not being used?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
No, the yellow wire is 230vac common. When I moved it off the duct work, the motor no longer runs. That may have been when the wire broken completely in two. I'll repair the wire and connect the motor green/yellow ground wire to ground. It is just hanging loose.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

Just keep me posted if any further questions, but the motor should be fine.

Billy

Ask Your Own HVAC Question
Customer reply replied 9 months ago
everything seems to be working fine now. Thanks for your help.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

Thats great news. Just rate service (5 star system) to close question.

Thank you,

Billy

Ask Your Own HVAC Question
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 9 months ago

I apologize but the question is still open as it has not been rated yet. Please rate service with the 5 star system to close

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Hiel furnace with a Rodgers 50E47-843 controller.
I have a Hiel furnace with a white Rodgers 50E47-843 controller. Last summer I replaced the blower moter. Ithe furnace will not light. L1 volts are 120 to ground. L1 to TH is 95 volts but was 150 unti… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have an Armstrong Ultra V Tech 80. During call for
I have an Armstrong Ultra V Tech 80. During call for cooling, the fan will short cycle while the outside compressor continues to run. When I open the access door (without releasing the door switch) th… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Have a carrier heatpump....just recently when ac is running
have a carrier heatpump....just recently when ac is running the air coming out of vents sounds like it loses air force power for a second or so … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I just bought a new blower motor and it has a extra yellow
I just bought a new blower motor and it has a extra yellow wire. I connected everything like before, it starts to go and goes about an inch, I can also hear the relay click on, then stops. The only wi… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Carrier Model 58MCA080---17116 Series 170 Out door temp
Hello all. Carrier Model 58MCA080---17116 Series 170 Out door temp upper 20s F Home built in 2005 decent not great insulation. 2500 sqfoot colonial in South east michigan. A couple days ago the flame … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hi, I have a York oil burning furnace (Manufactures number
Hi, I have a York oil burning furnace (Manufactures number TB ********** setup as emergency heat for my standard heat pump. A few years ago my blower motor went out (GE 5KCP39NGR034 S), the bearings f… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Texas Furnace Mod VSA 072 NH3R Sometimes this happens: Normally
I have a Texas Furnace Mod VSA 072 NH3R Sometimes this happens: Normally the exhaust blower comes on, then the burner comes on, after is runs then the blower for the air ducts comes on. This is normal… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
I have an american standard furnace/ac unit. 2 days agoafter
I have an american standard furnace/ac unit. 2 days agoafter replacing my air filter which was extremely dirty, I started hearing a sound like there was a piece of debris hittin the spinning part of t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I had my Lennox Pulse furnace replaced with a high efficiency
I had my Lennox Pulse furnace replaced with a high efficiency Lennox furnace almost a year ago and the technician that installed did not check the plenum for loose insulation installed with the pulse.… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Janitrol Furnace GMP075-4 inside Burner area; flapper noise,
Janitrol Furnace GMP075-4 inside Burner area; flapper noise, Sounds like a flapper / damper opening and closing during Blower Cool Down after burner shuts down. What is this sound and how is it fixed?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
hello, I hvae a weatherking furnace mo# XXXXX I was
hello, I hvae a weatherking furnace mo# XXXXX I was repalcing the blower motor. Imark the wires for the computer but when I tried to start it the moter sparked. I placed the red wire on m1, back on co… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i have a trane xe60 furnace, recently it got really cold here.
i have a trane xe60 furnace, recently it got really cold here. I have the furnace turned on and the burners stay lit when needed but the blower shuts off then turns on, its not the thermostat because … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Bryant350MAV036080 90 Plus furnace. When I turn on
I have a Bryant350MAV036080 90 Plus furnace. When I turn on the heat the burner lights and heats up. It stays burning for about 90 seconds and then shuts off. The blower motor does not start. I took t… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
We are having a blower issue with our Heil 9MPV100j20B1 HVAC
We are having a blower issue with our Heil 9MPV100j20B1 HVAC unit. The blower will come on in the cooling mode and run for about five minutes. The blower motor quites after five minutes but the outdoo… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
i have a luxaire lp furnace that runs for about 3 min then
i have a luxaire lp furnace that runs for about 3 min then blows the 3 amp fuse down by the blower motor. what do you think is causing this?… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Having blower motor problems. Two days ago blower motor started
Having blower motor problems. Two days ago blower motor started making noise like water running. Saturday morning took apart furnace and cleaned everything. Blower motor sealed so no oil needed. Check… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
My forced air heater - Concord RPG10A36D 100A-L/A - is making
My forced air heater - Concord RPG10A36D 100A-4A - is making a subtle noise - like when the washer is unbalanced but in an enclosed room, so muffled. My thermostat was on 64 but it's 57 in the house r… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my blower motor stopped working. I smelt some electrical burning
my blower motor stopped working. I smelt some electrical burning smell before it stopped. I opened up the bottom by the blower and saw some burn marks by the top of the electrical board. I'm wondering… read more
Josh
Josh
Service Technician
High School or GED
30 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x