I have a 48gp-03609311. the gas line is open but it isn't

i have a 48gp-03609311. the...
i have a 48gp-03609311. the gas line is open but it isn't heating the air. it only runs A/C or fan
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: i checked the thermostat and it read "heat on" but only fans. regarding the filter, are you talking about the filter that is the intake from the house? or are there other filters
JA: Do you plan on doing the work yourself?
Customer: I willing to give it a try
JA: Anything else we should know to help you best?
Customer: i don't think so
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
10/23/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,562
Experience: Furnace, A/C and heat pump specialist.
Verified

Do you have an error code on control board in unit?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
where do i find the control board?

Inside air handler.Give me model on air handler

Ask Your Own HVAC Question
Customer reply replied 1 month ago
it is a Carrier 48GP-03609311

Sorry that reply was for someone else. Your control board will be in the service panel.Let me see if I have a pic to show which panel

Ask Your Own HVAC Question

THanks.Rollouts will be just above burners and have a little red button in center.Push and see if one clicks and error goes awayhttps://i.imgur.com/CGkB9sa.jpg

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I pushed it but it it still flashing 7 times

There should be several at least to or three, Did you try all of them?

Ask Your Own HVAC Question

Turn power off and back on to unit and see if error still there.If so by pass the rollout by jumping the wires together.Looking at diagram may only be one with blue wires

Ask Your Own HVAC Question

Looking at diagram may only be one with blue wires.Turn power off and back on to unit and see if error still there.If so by pass the rollout by jumping the wires together

Ask Your Own HVAC Question
Customer reply replied 1 month ago
It ignited and then shut off with two seconds after restarting. It is also still blinking 7 times. Instead of jumping the wires together, do you think installing a new roller would fix it?

It might but jumping would verify for sure before buying

Ask Your Own HVAC Question
Customer reply replied 1 month ago
ok. it started raining so i had to close up but I should be able to jump it and test

WE know what is causing issue now is the rollout.

If you have further questions, please let me know.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

To rate answer, please select one of the stars on the page.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,562
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 1 month ago
Thanks! You've been a great help. I'll probably do follow up tomorrow since it doesn't look like the rain is going to let up.
Customer reply replied 1 month ago
when the burner lights, the flames are actually hitting the rollout directly. Which is causing it to shut the gas off like its supposed to when it gets to hot

Flames should not be touching rollout.If the do we have a more serious issue.Do they touch immedialetly or only after blower starts?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
They start immediately

Flames touch rollout immediately? Do you have a pc showing location of rollout and could it have bent bumped and moved?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
But you can see in the bottom left corner of the first pic, where it is hitting the rollout

Flame should be no where near the roll out.It should only come out far end of burner and shoot into the chamber. I know you don't want to hear this but it is time to replace this furnace.If you have this much rust on burners heat exchanger is most likely shot

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Yeah, I realized it might be a bigger problem when they were hitting the rollout. I really appreciate all the help you’ve been.

Wish it were better news but would rather have you spend money to replace than wake up dead.Glad it will not stay running if heat exchanger is bad as it would produce carbon monoxide and easily kill you.

Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,562
8,562 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have Carrier Weathermaker 8000 2 stage. wanting to install
have Carrier Weathermaker 8000 2 stage. wanting to install an ecobee lite. Is it compatible? Had a HVAC tech install it but the furnace is running almost contiunuously with a very few seconds between … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a carrier split system model no. 38ydb024310 &
I have a carrier split system model no. 38ydb024310 & fe4anf002. Just replaced the thermostat with the infinity touch control. Getting error message 'outdoor unit has wrong size for indoor unit. 16kbt… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER
I HAVE A CARRIER CNPHP HVAC SYSTEM THAT IS LEAKING WATER INTO THE SAFETY PAN BELOW. THE TECHNICAIN DIAGNOSED THE PROBLEM AS THE SECONDARY HEAT EXCHANGER HAS A CRACK. THE UNIT IS TEN YEARS OLD. RATHER … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier 9200. The limit switch is popping. There
I have a carrier 9200. The limit switch is popping. There was a very dirty filter in, but that it not in now. I have checked the air inlet for both the flame unit and the fan blower are working fine. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the wiring from txu/carrier thermostat to a
what is the wiring from txu/carrier thermostat to a non-programmable thermostat by honeywell … read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
In 2003, we had a new high-end Carrier Infinity Weathermaker
In 2003, we had a new high-end Carrier Infinity Weathermaker furnace installed - Model 58MVP-100-20 (run on propane). 8 years later, in 2011 - while still under warranty (parts and labor) the main hea… read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
I have a Carrier 58STA/STX Series 140/E furnace. There is
I have a Carrier 58STA/STX Series 140/E furnace. There is flame rollout for one of the burners/tubes. Can I fix the problem by myself? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
354 satisfied customers
I have a Carrier 58MCA080 gas furnace with continuing
I have a Carrier 58MCA080 gas furnace with continuing issues. Need some help diagnosing current problem.… read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
I have a Carrier furnace 58MCA080-13112. Got home from
I have a Carrier furnace 58MCA080-13112. Got home from vacation and my furnace won't work. The inducer motor comes on and you can see the flame thru the window, so it heats heats up but the blower nev… read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have carrier furnace model CK5BXA048021AAAA that is not
I have carrier furnace model CK5BXA048021AAAA that is not heating up. … read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set
We have a Carrier A/C with Carrier TP-PRH01 thermostat. Set on hold, auto, cooling.75 dgr. A/C will run for a while and go dark.Cooling stops. eventually it will light up and cooling will begin and wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
My carrier heating heat exchanger is plugged. I understand
My carrier heating heat exchanger is plugged. I understand it is civered under a recall action. if bI purchase a new systeem 59mn7a080-20 what price drduction do I receive? … read more
airheatman
airheatman
HVAC Technician
8,562 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x