My boiler is short cycling, sounds only the gas valve is shutting down only on for 70 sec. first cycle then 5 to 8 sec. after the call comes in.

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

Yes no change

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I changes the flame sensor first but think it the gas valve now

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 10 months ago
The boiler is a Weil-Mclain Model VHE Series 3
I have a Robertshaw 7100 DER-S7C gas valve and a 780-735 ignition control unit to replace the gas valve if it will work?
Answered in 11 hours by:
10/22/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Your unit appears to have a mercury flame sensor. So the best fix is to retro fit it with a new ignition control, gas valve and spark pilot assembly. The Gas valve you mention shows as having no pilot outlet in the manufacturer's database.

Ask Your Own HVAC Question

the ignition control is for a spark igniton pilot so it is suitable. Do you have more questions?

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 10 months ago
The gas valve that I have came with a new spark egnition pilot assembly. What makes the old system run for 70 seconds on cold start and then cycle on and off 5 to 8 seconds to satisfy the call? If the gas valve is the problem why’s it not a consistent time?
Phone call session started

Here's the wiring diagram.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
24,614 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Reset gas knob after switching gas tanks Reset gas valve
Reset gas cock knob after switching gas tanks Reset gas valve after changing gas supply … read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
Our EG boiler's flame was extinguished as the result of a flash
our EG boiler's flame was extinguished as the result of a flash flood. How do i turn it back on? Thank you, Erik… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
Weil-Mclain VHE furnance short cycles -60 secs with no
Weil-Mclain VHE furnance short cycles for 30-60 secs with no error code on ICM. Replaced flame rod. Voltage across gas valve was erratically dropping from 24 down to zero tripping the solenoid repeate… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello, Im having some trouble with the burner in my furnace
Hello, I'm having some trouble with the burner in my furnace randomly not lighting. Sometimes it works fine and other times I have to reset the thermostat a few times to get it to go. When it doesn't … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have Weil-McLain Series 9 Boiler, the pump turns on when
I have Weil-McLain Series 9 Boiler, the pump turns on when the thermosat sends signal but it does not ignight. I can how ever start it with a lighter. The gas valve and Flame sensor have were replaced… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
we have a weil-mclain VHE3 natural gas broiler that wont stay
we have a weil-mclain VHE3 natural gas broiler that won't stay lit. We have replaced the flame sensor, we have 24 volts ac coming out of transformer, the control module does not have any failures. It … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Weil Mclain CGM-4-PT furnace. The unit hust sits there
I have a Weil Mclain CGM-4-PT furnace. The unit hust sits there and it makes the clicking sound to light up but all I get it the pilot lite. The flame sensor does not seem to work. So I bought a new o… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
Where can I find a replacement for a robertshaw grayson 7100
Where can I find a replacement for a robertshaw grayson 7100 DER gas control valve? The one on my furnace turns off randomly even though the 25V control signal is present.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
have a weil mclain gas boiler from around the mid 1980s. Its
have a weil mclain gas boiler from around the mid 1980s. Its a vhe model, my problem is it goes to start glow plug goes on it goes through it s normal start up at the end the gas valve can be heard to… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
we have anat gas modle cgm -5-p series #8 the piolet is
we have anat gas modle cgm -5-p series #8 the piolet is on the circulater is running the zone valves are open the boiler dose not fire what do i check or replace? thanks Kevin… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Weil McLain boiler VHE 3 with a Mercury Flame Sensor.
I have a Weil McLain boiler VHE 3 with a Mercury Flame Sensor. One week ago burners would not ignite. Replaced the Mercury Flame Sensor White Rodgers. Furnace was working fine this week but now I have… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
I have a Weil McLain VHE (series 2) Boiler with no spark Blower
I have a Weil McLain VHE (series 2) Boiler with no spark Blower and circulator both operate have replaced relite control, TFE Fuse, preasure switch, mercury flame sensor, electrode wire, 30 second tim… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
I have a Weil Mclain VHE series propane boiler,the first time
I have a Weil Mclain VHE series propane boiler,the first time it fires it runs for approx. 1 1/2 minutes,then on 2nd fire and so on it only burns for 5-10 seconds.… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
I have a Rheem natural gas furnace that will not start. It
I have a Rheem natural gas furnace that will not start. It "wants" to start. The small fan runs to get air moving up the flue and the pilot is burning. There is a constant ticking noise like that of a… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Rheem furnace has a robertshaw sp715A ign control and 7100
My Rheem furnace has a robertshaw sp715A ign control and 7100 der gas valve. the thermostst works properly. the pilot ignites properly. The gas valve works properly while the 24v is present from the i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a weil mclain boiler Model # CG-4-P1. After the pilot
I have a weil mclain boiler Model # XXXXX After the pilot ignites the main gas valve doesn't open and the main burner doesn't fire.… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
We have a 30+ year old GE gas furnace. When the thermostat
We have a 30+ year old GE gas furnace. When the thermostat determines it's cold enough to turn the furnace on OR we manually increase the desired temperature on the thermostat, we can hear a click at … read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
i have a weil mclain vhe-6 gas furnace and it is not working.
i have a weil mclain vhe-6 gas furnace and it is not working. It is in the single digits outside and the blower is running continuously and the pilot will light and then after a minute you can hear a … read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x