I have an American Air Furnance Model. The code reads

Hello Pearl, I have...

Hello Pearl, I have an American Air Furnance Model . The code reads pri***** *****mit switch is open. I replaced the limit switch with an original part and the code is still saying the primary high limit switch is open?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The filter is replaced, the thermostat is new and set on 80 degrees.

Contractor's Assistant: Do you plan on doing the work yourself?

Can you advise?

Contractor's Assistant: Anything else we should know to help you best?

That’s everything....

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 20 minutes by:
10/21/2017
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,921
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

my name is Billy. There can be more than one limit and also different types.

And there is always a possibility of a bad circuit board. Do you know what and where the roll out switches are? Or can you post a pic of furnace and i can circle

Ask Your Own HVAC Question

can you please post a pic of the burner area?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Can you explain why you need the picture?

I was going to show you the other "limits" in the circuit. An open limit can be one of 3-4 switches

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok. I will go take the picture now!

standing by

Ask Your Own HVAC Question
Customer reply replied 4 months ago
In route about 10 mind away.
Customer reply replied 4 months ago
Hello??? Are you there???

First follow all the wires I made red X's at HERE

Also click ...HERE

If the limit on wall is new

And pressing center of roll out button does not reset......AND the wires marked do NOT go to another limit switch...then the circuit board is bad.

But what happens is a wire leaves the circuit board with 24volts....stops and runs through a limit, runs to another etct etc then runs back to circuit board. It is this loop that we need to check...if everything in the loop is closed and 24v gets back to board then the board is bad.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I replaced all the limit switches yet the control board is still saying pri***** *****mit circuit open. So, do we need to replace the control board? Where is the best place to order an original control board?

does the bypass include the one we couldnt get to?

Last test to see if board (seriously) :)

When you follow the wires for the limit circuit....they both end up at the plug on the board.

Can you identify these 2 wires as they leave the plug on the board?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
the wires go back to the control board. There is also, a rollout switch on the right interior side of the Furnance that has wires that tether back to the control board and the pri***** *****mit switch.
Customer reply replied 4 months ago
The two wires go to the limit switch from the control board.

ok just to confirm...the limit you replaced....the wires go direct back to board?

Ask Your Own HVAC Question

and not through another limit?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The switch on the left side is tethered to the pri***** *****mit switch inside the plenum, but there is one wire on the connector space of the primary switch that goes directly to the Control board.
Customer reply replied 4 months ago
Hi Billy, The wires are connected based on the original layout from the factory.

Thank you..

Then you will need to replace board...the rollout and limit circuit return on separate wires...so you have a bad board.

Like this one

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Billy, Where is the best place to buy an original Control board for the American Air? I sent a picture of the control board. Also, why doesn't the Control Board has an diagnostic indicator Code of when the board is bad? Is there a way to test in the future without relying on the control board indicator light?

you start at the wire leaving board carrying 24v TO the limit...and if limit is closed the 24v returns to the board and verifies the limit is closed. When the board is bad it does not recognize the 24v being returned.

The only confirmation is to verify the 24v is getting back to the board...and if board codes open limit we know board is bad.

This board is older has no provision for a "bad board" diagnostic

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I got the new control board In, but am getting diagnostic code of Pressure Switch NC Circuit Open, yet there is a brand new pressure switch on the furnace that was added today. What is causing this?

Does the pressure switch wire run to any other device or just 2 wires from board direct to ps?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
There are three wires coming off of the new pressure switch. 1 red wire goes to the gas valve, 1 blue wire that connects to the wire harness that is connect to the control board and 1 purple wire that is connected to the same wire harness that is connected to the control board.

when you start furnace does the exhaust fan start?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Billy, The exhaust fan does not start.

When you turn the thermostat to heat...and the code is blinking for pressure switch...there is a black and white wire that go to the exhaust.....can you tell me if this black and white wire has 120v between them?..is the exhaust motor warm, hot, cold, humming etc?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Billy, The thermostat is hard wired jumpered. The exhaust motor is cold. From the blower motor, the white wire is connected to the new control board at the neutral terminal section and the black wire is connected to the EAC terminal section on the control board. Where do I place the voltmeter to check for the 24 volts?

Ok that black wire will not go to EAC...It goes to IND....Unless it is listed as something else on the new board

Ask Your Own HVAC Question

Eac = electronic air cleaner (if equipped)

Ask Your Own HVAC Question
Customer reply replied 4 months ago
What does IND mean? Is that for the inducer motor on the blower? Should I switch the wire the turn the power back on?

IND means means inducer motor which is the exhaust motor.

If you have a full pic of the new board I can direct...but EAC will not have 120v when we need it.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Billy, It’s firing up, but now I’m getting code 4, which says an “airflow control circulation problem”. Never had that issue before. Do we need to increase or add more cold air return ducts?

Is blower running and heating home?

The unit is operating ok but codes circulation?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The Furnance has the only 6 “flex ducts” coming off the plenum to the heat registers which are 30 feet away from the furnance which is in the basement. There is only 1 cold air return. The furnance is an 80% efficiency with 45,000 btu’s

Ok,

You need the same sq inches in return as you have in supply.

I would actually cut a register in right off the top of furnace...dump the extra heat in basement or wherever the furnace is...It would be great to more return to furnace...easier said than done usually.

I am glad you have it fired up!

Just rate service (5 star system) to move off the active list

Billy

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I hear and see the fan turning as the heat builds up inside the plenum, but the furnance shuts off before the blower distributes the heat through the vent ducts. The furnance is behaving the same way before adding the pri***** *****mit switch, 2 new roll out switches and new control board. It’s only giving a new code for airflow now.

On the circuit board....what color blower motor wire is on HEAT terminal?

Ask Your Own HVAC Question

ok right now it is the slowest blower speed for heat.

Is there a yellow or blue wire from motor that is terminal M1, M2 or PARK?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I mean red wire on the HEAT terminal of the spade connector on the control board.

ok coming from the blower motor...there is black (which is on COOL)

Red (which is on HEAT)

White (on neutral)

Then we have 2 unused speeds...yellow and blue.

Very simply I want to swap the red wire and blue wire.

This will raise the blower speed.

Are you sure the blower that blows air out the registers is running after the burner is on for 40 seconds? The exhaust motor is attached to chimney pipe and main blower in bottom behind the panel

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I don’t see a yellow or blue wire from the blower motor terminal or anything with M1, M2 or Park.

dont the wires marked here run with the black and red ?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It’s not blowing anything out after it runs for 40 seconds. The flames burn for 3 minutes then, the furnance shuts off before distributing heat into the vent ducts. I even opened to vent ducts off the plenum to check for airflow. No heat is being distributed. The furnance shuts off.

sounds like a major electrical hit....this means the motor or capacitor is bad.

see here

Ask Your Own HVAC Question

you can, but it sounds like the motor has an issue or the capacitor...board is new...

Ask Your Own HVAC Question
Customer reply replied 4 months ago
What is the best way to test the motor? Where is the capacitor located?

the capacitor is behind the panel in the lower section usually mounted on the blower housing.

remove panel and show me what you see

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,921
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,921
22,921 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace is not heating. The diag is saying primary limit
My furnace is not heating. The diag is saying pri***** *****mit open … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a blinking number 5 on a rheem prestige furnace.
I have a blinking number 5 on a rheem prestige furnace. About 7 years old … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Air ease a95uh2v is throwing error code for high limit
air ease a95uh2v is throwing error code for high limit switch … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,921 satisfied customers
I have a 15 year old Rudd 90% plus furnace. Yes .Its not
It never goes into the ingnition spark mode.I replace both the upper and lower pressor switches this mourning.Did not change anything … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,921 satisfied customers
Lyric t5 not heating. But i'm not sure if they're correct
yes, but i'm not sure if they're correct for my type of unit … read more
Bill
Bill
Service Mgr
22 satisfied customers
Goodman furnace light flashing four times. Fan kicks on but
Goodman furnace light flashing four times. Fan kicks on but wont ignite … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 3 year old Hayward Pool Heater in our home for pool
I have a 3 year old Hayward Pool Heater in our home for pool & spa. After 3.5 years my pool tech. tells me I need a new heat exchanger, there is a leak and he tells me the exchanger is bad. They are t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Amana GHI90A30/P6983122f furnace no flame cleaned flame
amana GHI90A30/P6983122f furnace no flame cleaned flame sensor, ignitor lights ,seems to cycle correctly till ignition but no flame. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Hope you can. How do I remove a set thermostat and go back
hope you can. How do I remove a set thermostat and go back to manual … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Trying to connect to home thermostat and told incorrect user
trying to connect to home thermostat and told incorrect user ID or password … read more
Bill
Bill
Service Mgr
22 satisfied customers
Can you tell me where is the fuse box on carrier. It's
Hello, can you tell me where is the fuse box on carrier reefer … read more
Bill
Bill
Service Mgr
22 satisfied customers
My screen is blank and I can't get it to power back up.
My screen is blank and I can't get it to power back up … read more
Chris Wagner
Chris Wagner
None
12 satisfied customers
Why is my thermostat not displaying correct room temperature
why is my thermostat not displaying correct room temperature and how do i fix it … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
A/C is not working properly. The drain pan is filling up
A/C is not working properly. The drain pan is filling up with water. The system was just installed this past August.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a g5ra096c-16 (Miller/nordyne) and it won't heat past
Hi, I have a g5ra096c-16 (Miller/nordyne) and it won't heat past 22 deg c. There are no error codes on the status light … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need to replace the spark plug on a Lenox Pulse furnance
I need to replace the spark plug on a Lenox Pulse furnance model G21Q4/5-100-3. It takes a Champion FI-21500 spark plug which appears to be no longer available. What is its replacement? … read more
Bill
Bill
Service Mgr
22 satisfied customers
I have a goodman system - heating and AC model CAPF3636A6BA
I have a goodman system - heating and AC model CAPF3636A6BA Serial number:(###) ###-#### Periodically I am getting a high shrill sound - about every 10-12 minutes - only once each time. Wondering whet… read more
Chris Wagner
Chris Wagner
None
12 satisfied customers
Have a model TUH2B060A9V3VAA furnace serial # SH8436JXP7G.
have a model TUH2B060A9V3VAA furnace serial # SH8436JXP7G … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x