Customer Question
Valiant ga92-100 Contractor's Assistant:...

Valiant ga92-100

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Today

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I changed the pressure relief valve

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 11 months ago
I replaced the pressure relief valve on my furnace (Valiant ga92-100) and now it won't come on automatically, I can push the relay on the aquastat to get it fire up but that's the only way, and it cuts off when I release relay
Answered in 43 minutes by:
10/21/2017
HVAC Technician: Gaztech, HVAC Technician replied 11 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 939
Experience: Owner at Gaztech
Verified

.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,826
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Do you still need help? If so I need a picture of the wiring connections on the Aquastat/relay

Click on the link below for info on posting pics here

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

Ask Your Own HVAC Question
Customer reply replied 11 months ago
I'm not in front of unit at the moment, I will send the pictures later today
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago

Ok, also need to know if this boiler has a vent damper and how many thermostats on thesytem? Get back with these answers when you post the pics

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago

Try jumping the T & TV terminals on the control (top left). Does the relay pull in?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
No
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago

I'm well aware of how the control functions. If the circulator doesn't turn on when you jump T & TV you need to replace the control.

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Which control
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago

The one in the pic. Looks like a Honeywel L8148E.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 11 months ago

Do you have more questions?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
Have a weil Mclain Ultra 230 that keeps shutting down
Have a weil Mclain Ultra 230 that keeps shutting down for temperature sensor. The supply temperature rises above the shut off value of 190 then the boiler shuts off blowing off excess pressure through… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My oil boiler Dunkirk empire II with burner Beckett by
Hi. My oil boiler Dunkirk empire II with burner Beckett by Honeywell is about 6 years old. Was working fine untill pipe got frozen (thermostat in the room failed) and burst. The pressure was lost and … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
I replaced the TACO 007 circulator and the 30psi relief
i replaced the TACO 007 circulator and the 30psi relief valve, refilled the system and fired up the boiler, bleed the radiators and the system heated fine but the pressure relief is dripping prety ste… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
Hi I have a Weil McLain Oil fired boiler (wgo). The temp of
Hi I have a Weil McLain Oil fired boiler (wgo). The temp of the boiler is running up to 225 degrees. When the temp comes down to around 200 the boiler kicks on. The temp then falls to 180. It rises to… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
Hi Billy, I hope this finds you well. Today I inspected a one-year-old
Hi Billy, I hope this finds you well. Today I inspected a one-year-old propane fired Baxi wall furnace model HT 380. What is the AFUE and does this boiler has a built-in thermal control or LWCO? Thank… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a honeywell aquastat relay l8148e. It seems the low
I have a honeywell aquastat relay l8148e. It seems the low heat limit is not working properly. When the thermostat calls for heat the boiler kicks on and will bring the water temp up to 195. The probl… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My boiler pressure relief valve dripping, need help!
My boiler pressure relief valve drips a small amount every day. I replaced the old pressure relief valve with the same model and which matches what is called for in the installation guide. The tempera… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
I have a Honeywell L8148E Auastat on my Slant Fin Boiler.
I have a Honeywell L8148E Auastat on my Slant Fin Boiler. It occasionally it emits a loud whisle type noise. I notice if you take the cover off the Auastat there is a lever that if pushed will stop th… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
i have a weil mc clein 105 btu gas furnace water is coming
i have a weil mc clein 105 btu gas furnace water is coming out of 30 psi relief valve line furnace running at 200 and 40 psi i changed valve and tank 2 years ago what do you think?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have an old Burnham boiler model P5-W-22AN. I replaced the
I have an old Burnham boiler model P5-W-22AN. I replaced the pressure relief valve two years ago and everything seemed to be working fine. When I fired it up a month ago the valve started kicking out … read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
If two of the three relief pipes are leaking water (approx.
If two of the three "relief pipes" are leaking water (approx. 2 ounces a day), what can be the problem? How to fix? Again: it's a 6 year old Weil McClain system...the water heater is Gold 40 Gal. mode… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
I am not getting hot water, it is warm, though. I have a Superstor
I am not getting hot water, it is warm, though. I have a Superstor SSU-45 with the temp set to 140 degrees. I have a Weil McClain (sp) gold series with a Honeywell Aquastat relay L8148a set to 200 deg… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
Hello, I have a Bock residential oil fired hot water heater
Hello, I have a Bock residential oil fired hot water heater with a honeywell aquastate, I want to install a water to water heat exchanger on a loop between the pressure release and the spicot, is ther… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have hot water base board heat in my house with three zone.
I have hot water base board heat in my house with three zone. It is a oil fired furnace. Twice in the last 24 hours the hot water relief valve has popped. When it popped it released a ton of steam. It… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
I have a Burnham hot water heat system. It has a Honeywell
I have a Burnham hot water heat system. It has a Honeywell AQUASTAT RELAY type L8148E. The system was down. When I would turn it on the water Temp would come up but no circulation. I checked voltage t… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
slant/fin boiler. oil fired cast iron,not the pressure release
slant/fin boiler. oil fired cast iron,not the pressure release valve, but water running jout every time the furnance runs… read more
Rick
Rick
HVAC Supervisor
24,826 satisfied customers
i was changing some windows in my living room when i saw steam
i was changing some windows in my living room when i saw steam coming from the basement. i went down and discovered that the release pipe letting out lots of steam. i had the release valve changed but… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.