Customer Question
Furnace worked fine last...

Furnace worked fine last spring until we shut off end of May. Turned heat on this past Saturday and would not come on. Tech came yesterday and replaced thermostat and furnace ran immediately. Today furnace will not run. Purge blower comes on for 30 sec. and then shuts down and green light flashes on control board.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat is set 5 degrees higher than inside temp., it is calling for heat, process begins as usual but stops after 30 sec. purge and green light flashes. Filter is new yesterday and furnace ran yesterday.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, I'm pretty handy - Manufacturing Engineer & I have a little knowledge about this furnace. If you think we can fix this now by doing something tonight then I'm all for it. If you think it's going to take special tools, parts, etc. then I'll call tech again tomorrow.

Contractor's Assistant: Anything else we should know to help you best?

Furnace quit last March - tech replaced "fan timer control board" and worked good until May when we had to start cycling power to furnace to get to run until it wouldn't run at all - tech then changed old mercury thermostat with new digital one and ran fine for few more weeks until heat no longer needed and then AC ran good all summer. Furnace would not start up for first time on Sunday - tech replaced thermostat again yesterday and immediately ran good until today. Propane tank full, furnace does initial 30 sec. purge but then shuts off immediately w/ green light flashing and does not continue the sequence to initiate "trial for ignition", I have tools & multi-meter.

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 minutes by:
10/18/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 11 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,897
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, one minute while I get some information together.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 11 months ago

What code is flashing on the board?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I ran out of fuel during the night so didn't shut off the
I ran out of fuel during the night so didn't shut off the furnace until that morning. I got fuel delivered but the furnace won't come on. I looked on the unit and it was flashing red so pushed the res… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,978 satisfied customers
It's freezing. Heat won't turn on. 3rd zoning board that has
It's freezing. Heat won't turn on. 3rd zoning board that has gone out... heat light blinking red … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have an interrupted ignition oil primary control
I have an interrupted ignition oil primary control product-Honeywell. Ran out of oil last night. Put five gallons in until I get a delivery tomorrow (today is Sunday). The green light is flashing ever… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Rheem Criterion II. Just replaced blower motor. Now, with
Rheem Criterion II. Just replaced blower motor. Now, with furnace control off the blower runs just fine. But (!) with the furnace turned on, the blower won't start. The pre-purge starts and clears the… read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
I ran out of propane and I just got it filled now the pilot
I ran out of propane and I just got it filled now the pilot light on my furnace wont light. It's an automatic pilot light … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Rheem 90 plus furnace installed 1995 model rgra-07emaes
rheem 90 plus furnace installed 1995 model rgra-07emaes purge fan comes on then cycles off, occasionally the igniter will heat and lite but will not burn for a full cycle.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier Performance 93 installed 5 years ago. Last week I
Carrier Performance 93 installed 5 years ago. Last week I had a new thermostat installed but problem has not been resolved. Here is the pattern since then: New thermostat installed Wed March 9th and p… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have Lennox 80uhg3-75a started only running or so mins
Have Lennox 80uhg3-75a started only running for 3 or so mins before shutting off. board showing themostat calling for heat. replaced flame sensor replaced circuit board first time after board install … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
What can be wrong with my furnace that it is turning on for
What can be wrong with my furnace that it is turning on for 10 min. and then shuts off and turns back on 5 min. later?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The blower comes on right away and the unit doesn't light and
The blower comes on right away and the unit doesn't light and I'm getting error 12 on my unit i've replaced the gas valve, flame sensor and igniter… read more
type2technician
type2technician
253 satisfied customers
my heat has failed, I have a mod. G43UF-36B-070-09 furnace,
my heat has failed, I have a mod. G43UF-36B-070-09 furnace, it was working fine until yesterday. I shut the power off to the unit for about 10 minutes, then re started it. After it ran through the pur… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hello, I have a lennox 21 pulse furnace. It was installed
Hello, I have a lennox 21 pulse furnace. It was installed in 1999 and was just maintenanced last fall. In the last few weeks, the furnace is not turning on and I notice the green sensor light is off. … read more
gmac2905
gmac2905
hvac tech
Vocational, Technical or Trade Scho
18 satisfied customers
My Lennox Pulse 21 G21Q3-80-1 occasionally would lock out.
My Lennox Pulse 21 G21Q3-80-1 occasionally would lock out. Power off/on cycle reset it. Lately it locks out at the end of the cycle more often than not. Power cycle resets it. I've watched it through … read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have an Armstrong Ultra SX 80 forced air gas furnace. The
I have an Armstrong Ultra SX 80 forced air gas furnace. The unit tries to turn on, but it seems that it acts as if there's no call for heat as it revs up and then stops after 5 seconds. Technician fro… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
We have a Lennox furnace [ Model G24M3/4-100A-2; Serial #6395C31989
We have a Lennox furnace [ Model: G24M3/4-100A-2; Serial #6395C31989 ] with a weird problem. After many visits from our plumbing/heating company over the past year in which we essentially rebuilt the … read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
Hello. I have a Trane XB90 propane gas furnace. When the
Hello. I have a Trane XB90 propane gas furnace. When the thermostat calls for heat, the furnace starts up, the burners fire, and the blower begins to cycle the air as you would expect. However, after … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
cant get the R7184B to prime oil before going off on reset.
can't get the R7184B to prime oil before going off on reset. Can't get it into the 4 min stage.. Any advice ? Bad pump?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Hunter 44860 thermostat that has not been working
I have a Hunter 44860 thermostat that has not been working correctly. This past Spring, when I switched from Heat to Cool, my blower fan ran CONSTANTLY. I called out a HVAC repairman and they put in a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x