I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage control wire. I just want to make certain that I have the correct wire. My unit has three wires running into it. (See photo). The wire colors are red, black, and blue. Can I safely assume that the slightly smaller gauge blue wire is the correct one (low voltage control)?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
10/17/2017
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 707
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to Just Answer. My name is ***** ***** I'll be happy to assist you today. Those wires in the photo are all high voltage wires that go to the compressor. Can you open the panel that those wires go into and take another picture?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
but I am not at home right now. I'll do that when I return home, if it's not too dark. Otherwise, I'll do it tomorrow morning and upload it then.

Okay, thank you

Ask Your Own HVAC Question
Perfect, thank you. You see the yellow and brown wires that come through the small triangular panel at the bottom of the electrical section? Those are your low voltage wires from inside. If you remove the triangular cover you will see the connections/wirenuts.
Ask Your Own HVAC Question
Customer reply replied 1 month ago
I removed the triangle shaped guard you indicated, and I see the connections. (See photo) Now I just need to verify that the correct place to wire into for the ECL switch is where I indicated in blue (see photo) on the yellow wire. Is that correct?
What is the part # of the ECL you’re using?
Ask Your Own HVAC Question
Customer reply replied 1 month ago
Here is what I have, which does say that it should be installed on the "yellow" wire....
"The Evaporater Control Limit Switch (Retrozone p/n) ECL is a widely used freeze stat or freeze protection device designed to prevent Air conditioning coils from freezing. The ECL switch opens its contacts below 38 degrees F, and automatically resets at 50 degrees Fahrenheit. Install the ECL switch by simply snapping it on the the refrigerant "suction" line leading up to the evaporator coil located, outside of the central heat and air fan/furnace housing. Two wires lead from the ECL switch and are spliced into the "yellow" low voltage compressor wire, so compressor operation is stopped when freezing condition are approached."
OKay, yes - you will wire it on the yellow wire so that’s it will break yellow when it gets below 38. Quick question, though - why do you need to install the freeze control?
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 707
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified
Regan Land and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 1 month ago
It's a really long story... the bot***** *****ne is that we often get freeze-ups during the fall & spring for a few reasons, one of which is because I have mismatched coils, with the outside coils being oversized. The mismatch is an even longer story which boils down to money, or lack thereof. So, in order to prevent the freeze-ups and consequently lengthen the life of the comp
Customer reply replied 1 month ago
compressor, I decided to go this route fir less than $10.
Anyway, thanks for the help.
Customer reply replied 1 month ago
I forgot to verify one other thing.... Which coolant line should the sensor/switch be clamped to, the one with the insulation, or the one without? I'm guessing that's a pretty important detail.
Customer reply replied 1 month ago
The coolant line with the insulation on my unit is also MUCH larger than the other line, if that helps.
it will go on the large line with the insulation.
Ask Your Own HVAC Question
Customer reply replied 1 month ago
Great! Thanks again!
No problem, thank you!
Ask Your Own HVAC Question
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 707
707 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Question about basement insulation... It's not a problem -
It's not a problem - it's a question...we live in the Atlanta area. 3 years ago, we purchased an existing home that has a full, unfinished walk-out basement, which means that the entire north and west side of the basement is above grade. The south and east walls are poured concrete and are below grade. When we bought the home, it had zero insulation in the stud walls on the north and west sides. The concrete walls also were not insulated. However, there was faced fiberglass insulation stuffed between the floor joists in the basement ceiliing … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
On our heat pump the evaporator blower runs constant even
On our heat pump the evaporator blower runs constant even when set to auto. … read more
Regan Land
Regan Land
HVAC Technician
707 satisfied customers
The yellow wire on the blower motor through insulation. It
The yellow wire on the blower motor burnt through insulation. It appears to be 15 years old. Would it be safe to repair the yellow wire and continue to run the motor? The ground wite is hanging loose … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am told I have a leaking evaporating pan in a Lennox Model
I am told I have a leaking evaporating pan in a Lennox Model #C16-46-1FF. Iwould like to find a replacement pan. Is this possible, or can I tape crack? … read more
Regan Land
Regan Land
HVAC Technician
707 satisfied customers
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit,
I have a Mitsubishi AC unit (Mr. Slim Evaporating Unit, Model MS-A12WA). That recently started leaking a pretty significant amount of water. The water must be building up inside the unit and then at s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I'm looking for the best method and type of insulation to
I'm looking for the best method and type of insulation to use in an 1890's home that has non-uniform stud and rafter spacing that ranges from 28"- 34" on center. In this process should I use a vapor b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has
I have a Goodman CHPF4860D6AA Evaporator unit. The unit has run without problem for the last two years. Lately, it has begun to shut down and then restart on its own after about an hour or more. The l… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
What is the use of insulating suction pipe of compressor? I
What is the use of insulating suction pipe of compressor ? I mean is it useful in package units also ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
How do I check heat exchanger for blockage. Today. Sounds
how do I check heat exchanger for blockage JA: I'll do all I can to help. How long have you been dealing with this? Customer: today JA: Do you plan on doing the work yourself? Customer: yes JA: Anythi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Instaling fie insulation. Which way does the metal piece go
which way does the metal piece go to hold the baffles … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
The condensation water leaks from heat exchanger near the
The condensation water leaks from heat exchanger near the filter and comes on the ground tray. There is no blockage of any sort. What needs to be done for auxiliary condensation tray if it is cracked.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,084 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x