I installed an Ecobee3 thermostat and it was working fine

for cool air. Now when...
I installed an Ecobee3 thermostat and it was working fine for cool air. Now when there is a call for heat, my furnace is flashing 4 times on the control board. This furnace is brand new. It was installed last July. I changed the filter, opened all air vents, but the error persists. Blower is not going down, and keeps running cold air. I checked the limit switch and it's ok, multi-meter shows normal frequency. Any idea what could be disrupting the burners ?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
10/16/2017
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

What is the model number of the furnace?

Does blower run nonstop even if thermostat turned off?

Does cooling work still?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Hi,
Model number is: RGF1L060AP12MP11A
If I turn the furnace down and turn it on after 5/10 minutes, it will work normally for 1 or 2 hours. System keeps the temperature ok (around 72F), when the furnace needs to run again (like, during the night, when the temperature goes down), it turns on, but there is no heat, so the blower is running with the 'normal' air only.
So, the led on the control board shows 4 blinks. I checked on the manual and it says:
"4 RED FLASHES: This indicates that the main limit switch has opened its normally closed contacts. The control will operate the supply air blower and inducer while the open limit condition exists. Check for a dirty filter, improperly sized duct system, incorrect blower speed setting, incorrect firing rate, loose limit switch wiring or faulty blower motor. If the limit switch has not closed within five minutes, the control will assume that the blower is not functioning, will start a hard lockout and will begin to flash the 11 Red Flashes error code. Power will have to be cycled off and on to reset the control after the problem has been corrected. See “11Red Flashes” description below. If the main limit switch opens five times within a single call for heat, the
control will also indicate 4 Red Flashes and will enter a one-hour soft lockout."
As I said this furnace is brand new and works fine for cold air.

OK,

so this is the first heating season for the furnace correct?

when installed did the installer set proper blower speeds for heating?

it sounds like you need more blower speed or bigger ductwork. Is this the same size as was in previously?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I was not at home during the installation, but yes the ducts are the same from previous. The old one was really old.
It's still on warranty, should I call him back to check the blower speed ? Is there anything I can do to check it ?

you need to call the installer back and explain "it is running on limit".

The installer will adjust the blower speeds and hopefully make the unit run cooler than it is.

Right now the unit is running hotter than designed..

The wise choice is have serviced while under warranty, and do not make any changes yourself.

Billy

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Thank you Billy. I'll call them.

You are very welcome.

Please rate service (5 star system) to close.

In the event you have any questions after the unit is serviced let me know. After rating you have 30 days follow up

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,888
22,888 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I changed the ignite on my heil NDGK. It's still not
I changed the ignite on my heil NDGK. It's still not heating … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a lennox zoned heat pump and it is not heating down
I have a lennox zoned heat pump and it is not heating down stairs. … read more
HvacmanSean
HvacmanSean
Owner
HVAC
229 satisfied customers
My light keeps blinking on my oil heater. What's a few
Hi my light keeps blinking on my oil heater. What's a few problems that makes the light blink? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a new Beckett Genisys 7505 oil furnace that stopped
I have a new Beckett Genisys 7505 oil furnace that stopped working last night. I completely filled the oil tank and have reset the furnace a few times, but when I try to turn on the heat I get cold ai… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,888 satisfied customers
Aprilaire 700. Water is getting to the switch at the bottom
Aprilaire 700. Water is getting to the switch at the bottom of the unit but not proceeding up into the unit to the filter element. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
We have a new HVAC gas pack. It is a Daikin DP16GM3008041,
We have a new HVAC gas pack. It is a Daikin DP16GM3008041, 2.5T PKG Gas, 16 SEER. The filter I am using is a Honeywell Elite Allergen 10 FPR. It makes a whistling sound when the unit runs and seems re… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I am showing the e24 on my thermostat and our temp here is
I am showing the e24 on my thermostat and our temp here is going to be in single digits later tonight. I am a widow and have not idea about taking off panels on the furnace. Help … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Used stove one day and it will not light tonight. HELP. 5
Used stove one day and it will not light tonight. HELP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a rheem manufacturing company model # rkma-a060jl10e
I have a rheem manufacturing company model # rkma-a060jl10e it does not want to work. We found that the gas had been turned off to it so I turned it back on. Is there a pilot light or something that n… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I turned on my built in fireplace for the first time
i turned on my built in fireplace for the first time yesterday. I came on for 1 minute and turn back off. I could here a click every time it would turn on and off. I was leaving the house after it tur… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have XV95 and I just got a new Ecobee3. It says it's
I have XV95 and I just got a new Ecobee3. It says it's heating but I am fairly sure that only the fan is running … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have water leaking from the furnace. Actually quite a bit!
I have water leaking from the furnace. Actually quite a bit! … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a lennox heat pump with12.5 eer i bought about 25
i have a lennox heat pump with12.5 eer i bought about 25 years ago. i live in south Texas and use heat every other year. the AC works good, last month it was cold. i turned on heat pump, worked overni… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do you change the thermal high limit swtiches on a
How do you change the thermal high limit swtiches on a PTH123E35Axxab PTAC. Looks very difficult. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My signature stat thermostat is stuck, I can't raise the
My signature stat thermostat is stuck , I can't raise the temperature. Also it is showing a current temp much higher than it is. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
1 year old house in Dallas Texas. Temp outside is 15 which
1 year old house in Dallas Texas. Temp outside is 15 which is abnormally cold. Ecobee thermostats upstairs and down. Both set at 74 and can't seem to get them above 66 this morning. Dropped from 68 la… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an Aprilaire steam humidifier Model 800. It is two
I have an Aprilaire steam humidifier Model 800. It is two years old and apparently has not been serviced at all. Recent cold weather drove the humidity down to the point where we had to call a technic… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
We have a 10 year old Goodman cple 48 hvac heat pump Ac
we have a 10 year old Goodman cple 48 hvac heat pump Ac unit, breaking the tripper. My hubby wants me to find a NEW unit to replace entire system we are very very unhappy with this goodman kept capici… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x