I have a newer model Armstrong oil forced air furnace. I

I have a newer model...
I have a newer model Armstrong oil forced air furnace.
I want to get a procedure for getting it ready for the winter heating season. Maintenance, conditioning oil supply, etc..
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
10/15/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,045
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

You need to call your oil burner service company and have the burenr tuned up. Theyshould replaced the oil filter and vacuum the soot out of the furnace as well as doing a combustion test to properly set the burner. Air filter should be changed. Generally not need to condition the oil unless the tank is outdoors. If it's an old atnk a bottle of sludge/moisutre disperant is a good idea. There are several brands. They all do the job. Whatever you local plumbing supply house carries will be fine or you can have the burner guy treat the tank.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
The HVAC companies here locally really do not want to service this unit. They want to sell me a new natural gas furnace, which I do not the money for at this time.
I am a competent tradesperson. I have installed many natural gas boilers and furnaces for new construction. However, I am unfamiliar with oil heat, which is why I used the service to tell me how to get ready for winter use. I moved into the house in mid-winter, and it worked fine, and is working well now. I am just concerned what a normal PM is on this kind of furnace.Just call the plumber is not the answer I was looking for. I can replace the filter, it is in plain sight, and I replace the air filter several times a season. The oil tank is outside; I will treat the tank with AV-942 when I have it topped off next week.But I have questions on exactly how to do the service. Do I have to bleed air out of the line after I change the filter ? Can I judge the flame by color ? I can vacuum out the blower and duct work, not a problem. Plan to lubricate the squired cage if the bearings are not sealed. Anything else ?

I didn't say call a plumber I said call a oil burner tech. You can't do a proper tune up without very expensive test equipment. The days of eyeballing a burner flame went away 30 years ago. Whoever you buy oil from has burner techs on call

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,045
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 3 months ago
OK. Will handle it.
Regards...Ed A

Thanks for using Just Answer

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Rick was courteous and professional. However, he did not tell me anything I did not already know.
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,045
23,045 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an air temp forced air furnace. It starts by igniting
I have an air temp forced air furnace. It starts by igniting the gas but shuts off after a few seconds it says it is running normal but after a few try's it locks out … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a wei-mclain gold oil burner that stopped firing up.
I have a wei-mclain gold oil burner that stopped firing up. the blinking green indicator light is flashing. the blinking green light goes off while I press the reset button for 45 seconds until I get … read more
Rick
Rick
HVAC Supervisor
23,045 satisfied customers
We have an electric Weatherking forced air furnace in our
We have an electric Weatherking forced air furnace in our garage that isn't heating properly. It seems like only the coils one side are heating. The model #WBHA14J11SUAA serial#TMI90123573. This furna… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Ruud rgrc07erbgs natural gas furnace wont recognize flame
ruud rgrc07erbgs natural gas furnace wont recognize flame after cleaning flame senser … read more
Rick
Rick
HVAC Supervisor
23,045 satisfied customers
Installed a forced air furnace this summer in the attic of
Installed a forced air furnace this summer in the attic of my small second home in Michigan. Since it gets extremely hot up there in the summer (90+degrees) The air conditioning struggles to keep the … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Have Ruud natural gas furnace and the gas valve opens after
Have Ruud natural gas furnace and the gas valve opens after the purge does its thing and only stays on for approx 3-5 seconds. Then goes off. The flame rod sensor light never comes on. Changed the rod… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a gas forced air furnace, new, with a 8320U
I have a gas forced air furnace, new, with a 8320U thermostat. The furnace cycles on and off every 6 mins. 6 on and then 6 off. Temp is set to 72 and it's 30 degrees outside. Is that too often? … read more
Rick
Rick
HVAC Supervisor
23,045 satisfied customers
I have a Goodman forced air furnace. The blower motor was
I have a Goodman forced air furnace. The blower motor was replaced last January. It recently stopped working / over heating. It humms but I can't push start it. I tested the 10 mfd capacitor on a mete… read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
I have a Payne Forced air Natural gas furnace with a
I have a Payne Forced air Natural gas furnace with a condenser pumo on the side. the pump will not shut off. … read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
Ge gas fired forced air furnace pilot valve wont turn. Done
ge gas fired forced air furnace pilot valve wont turn … read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
Natural gas furnace: Conquest 80 Circuit board: Honeywell
Natural gas furnace: Conquest 80 Circuit board: Honeywell S9200U1000 Universal Hot Surface Ignition Integrated Furnace Controlfurnace shut of itself after around every 20 minutes, although still under… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Natural gas furnace exhaust vent has a strong propane ordor.
natural gas furnace exhaust vent has a strong propane ordor. nothing is smelled inside the house … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I'm having trouble with my forced air furnace. It's not
I'm having trouble with my forced air furnace. It's not heating my apartment as well as it should. It started just a day ago. Everything seems to be running fine. I installed a new air filter so I kno… read more
Rick
Rick
HVAC Supervisor
23,045 satisfied customers
I have a Weil McLain cg 4 natural gas furnace, the pilot
I have a Weil McLain cg 4 natural gas furnace, the pilot stays lit all the time but the furnace doesn't start … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
383 satisfied customers
Hooking up a nest thermostat, I have natural gas furnace set
Hooking up a nest thermostat, I have natural gas furnace set as emerg heat on my old thermostat, main heat set as heat pump. Always Used emerg heat. Of course a/c. I have every wire hooked to my nest … read more
Appliance Guru
Appliance Guru
17,062 satisfied customers
I need to convert my forced air furnace from natural gas to
I need to convert my coleman forced air furnace from natural gas to propane. Where can i order the nevessary oarts to convert? Model no. DGAT090800, Serial No. XXXXXXXXX Its shows for propane - drill … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My gas fired force air furnace won't blow hot air, is the
yes by following the instruction in front of the furnace … read more
Rick
Rick
HVAC Supervisor
23,045 satisfied customers
I have a rheem forced air furnace Model 3600-100ADC the
I have a rheem forced air furnace Model 3600-100ADC the circuit board is broke as it cracked when moved. What circuit board would you reccomend to get to replace… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less