My Kelvinator furnace keeps throwing a power problem code…

My Kelvinator furnace keeps throwing...
My Kelvinator furnace keeps throwing a power problem code (flashing green and red lights). I pulled and checked the fuse and it was OK. When I re-installed the fuse it started up and ran for a couple of minutes and then throws the same code. I changed the fuse, but it continues to do the same thing. If I pull the fuse and put it back in the furnace will run for a minute or 2 and then stop. The furnace is about 5 years old.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
10/15/2017
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, one minute while I get some information together.

Ask Your Own HVAC Question

When that happens you actually just have a bad board. The board is thinking there is a power issue to the unit. Normally when that happens it is just a bad voltage reading chip on the board. Replace the board on the unit with the flashing lights on it and you will be good to go. You can double check the power to the unit, but I doubt that is causing this issue.

All I ask is please select the ***5 STAR RATING*** using the link at the top of your page before leaving, that is the only way I am credited through the site, tips are appreciated.

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 9 months ago
Okay, I ordered a new board and it will be here tomorrow am. I will try that and get back to you. If all works out good, I will be sure to leave you a 5 star rating. I did check the power and everything looked good and it reset again and came on. It acted like it tried to fire up, but once the igniter would start glowing, the board would click after a moment or two and then the igniter would shut down. It does this a few times and then the no power lights would start flashing again. Does it still sound like the board?
Phone call session started

Yes bad board.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
18,712 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My a/c system just stopped. My Honeywell thermostat does not
My a/c system just stopped. My Honeywell thermostat does not show the current house temperature just "--". Tried changing from A/C to heat mode but system will not turn on. My Lenox furnace appears to… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Replaced batteries in -Rodgers 1F80-51 because LCD had grown
Replaced batteries in White-Rodgers 1F80-51 because LCD had grown to dim to see. New batteries. Now furnace will not come on at all. Have tried pushing up and down temp keys together and putting batte… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Trane XV90 gas furnace. Had a Trane Clean Effects
I have a Trane XV90 gas furnace. Had a Trane Clean Effects Air Cleaner installed 5/5/15. On 5/15/15 we had an A/C chk. On 5/22/15 the furnace would not produce heat. Tried adjusting thermostat to be s… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Ran out of propane. Trying to fire the goodman hybrid
Ran out of propane. Trying to fire the goodman hybrid furnace back up. Only 32 degrees outside have set t-Stat for 71 in a house that's at 60. Both panels off, looking at lower circuit board, push loc… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Reznor UDAP 125 unit heater running on propane
I have a Reznor UDAP 125 unit heater running on propane heating my garage. Recently the heater has begun shutting off before it reaches the thermostat's set temperature. The green light flashes contin… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Bryant thermostat has no display, I opened it to look to
My Bryant thermostat has no display, I opened it to look to see if there is a battery, but it doesn't appear so. The furnace sounds operational, but no heat. What do I do to troubleshoot?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a fujitsu inverter, after a power failure the red and
I have a fujitsu inverter, after a power failure the red and green light continues to flash?… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,712 satisfied customers
my heat has failed, I have a mod. G43UF-36B-070-09 furnace,
my heat has failed, I have a mod. G43UF-36B-070-09 furnace, it was working fine until yesterday. I shut the power off to the unit for about 10 minutes, then re started it. After it ran through the pur… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hi I have a Rheem Criterion II Up until yesterday it has
Hi I have a Rheem Criterion II Up until yesterday it has worked flawlessly. It is about 7 years old and still looks new. Very clean under the covers and the filter is changed every 3 months. I just ch… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Bryant 340MAV furnace + AC not working. See 2 red quick flashes,
Bryant 340MAV furnace + AC not working. See 2 red quick flashes, then pause, then 4 slow flashes on furnace led light (24 code?). What does this mean? Is this the reason our AC won't work? Thanks for … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My problem started a few days ago.I was painting behind my
My problem started a few days ago.I was painting behind my thermostat,i replaced the thermo and fired it up.the furnace would not start.I saw the code for the secondary fuse is open,I replaced the fus… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane model #YCXO48F1HOBD. Heating problem. Flash code of 5
Trane model #YCXO48F1HOBD. Heating problem. Flash code of 5 flashes / flame sensed with gas valve off. Unit going into default / inducer and blower fans running.Checked roll out, pressure switch,and h… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a trane xr90 and a honeywell minizone. No heat, but
I have a trane xr90 and a honeywell minizone. No heat, but the fan runs. Minizone shows no calls for heat, though all zones' thermostats are set high enough to call for heat. Furnace blinks steady red… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem horizontal gas furnace in my attic attached
I have a Rheem horizontal gas furnace in my attic attached to a Rheem RCFA-HM3617AC. When thermostat calls for heat the IDM turns on a few seconds later, but only runs for approximately 5 seconds unti… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Luxaire GM9 furnace approximately 2yrs old. When call for heat
Luxaire GM9 furnace approximately 2yrs old. When call for heat is sent, the fan turns on and runs about 5 seconds then the LED goes from Green to Amber and the fan turns off. Something clicks and the … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Trane XV90 that was installed 3 years ago. We just
I have a Trane XV90 that was installed 3 years ago. We just had to replace the power transformer. Now the green status light flashes at 21 times at a one second interval, then the red light flashes on… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a American Standard Freedom 90 Dual Stage gas furnace
I have a American Standard Freedom 90 Dual Stage gas furnace that has been working fine for several years. Today instead of heat, it is blowing out cold air. When I check the internal light, with no h… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
i have a coleman gm9s080c16up11a high neffeinceny gas furnace
i have a coleman gm9s080c16up11a high neffeinceny gas furnace it blinks a code saying the limit swicht is bad has been replaced my local heating now says bad circuit board ist brand new he installed h… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x