My carrier evaporator keeps on blowing the 3 amp fuses. I…

Customer Question
My carrier evaporator keeps...

My carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

For about a week now, luckily, I have 2 units.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Filters, good but the thermostat is one of those Carrier Performance Edge but when I removed the thermostat from the wall, it fell off and the wiring harness, which is a small plastic part with two wires in it. The wires came off.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes. I am EPA and TDLR in the state of TX.

Contractor's Assistant: Anything else we should know to help you best?

Do I replace the wiring harness or do I do a visual inspection of the thermostat wire?

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 35 minutes by:
10/10/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, yes it is likely that you have two of the 24vac control wires stuck together or a bad printed circuit board.

Tell me if the fuse was blowing before you did all of those parts replacements, or after you did those replacements.

.

We can go from there without a time limit

Ask Your Own HVAC Question
Customer reply replied 10 months ago
The outside fan wasn't on so he, the home owner, replaced the contactor. He then noticed he didn't have 24 volts to the thermostat. He then called me over. I checked the capacitor, which was bad and I changed it out and I went to the evaporator and noticed that the 3 amp fuse was blown. I changed out the fuse and went to the thermostat and noticed,that it was 2 different gauge of wires connected.
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, ***** ***** an untrained home owner elects to just start changing out parts, often wiring mistakes are made, and you will not know which wiring mistakes, but you will notice the blown fuse.. And that is where you are on this situation.

There is never, ever, 24volts measurable at thermostats without a C wire attached, most do not have a C wire, so that red 24vac + wire can be hot, but it will not read with any voltage, so then on that basis the home owner makes more changes and possibly introduces more mistakes... then when you arrive you have no idea on earth what was done or correctly or incorrectly.

.

attach a photo of the thermostat wires shown connected to the thermostat, and the same wires where they attach inside the furnace or air handler, and a photo of the wiring diagram glued to the inside of the blower access door, and I will prescribe a few tests.

.

Use the 'add files' link next to your send button to get those photo's to me, they must be exceedingly well lit and focused

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Ok, I will.
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Use the 'add files' link next to your send button in this dialog box to get the photo's to me, we can go from there.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XL 1200 that will not turn on. I turned the
I have a Trane XL 1200 that will not turn on. I turned the thermostat off and then back on and heard the "click" as if a resister was trying to turn on the AC, but the outdoor unit will not do anythin… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Aloha from Maui, hot today no a/c. neither air handler or
Aloha from Maui, hot today no a/c. neither air handler or compressor will run. checked thermostat, no 24 volt input. checked contactor at compressor, have 250v power but no voltage at contactor coil i… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a carrier ducted air conditioner that is about ten
Have a carrier ducted air conditioner that is about ten years old and is blowing a control fuse in ceiling unit but only after about 30 minutes of normal operation? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem RGPT-07EBRQR furnace and a Rheem central air.
I have a Rheem RGPT-07EBRQR furnace and a Rheem central air. Starting today the furnace control borad transformer blows the fuse if you put the thermostat in the cooling mode. The furnace board is a 6… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier FE4 system that has a 3 amp fuse on the
I have a carrier FE4 system that has a blown 3 amp fuse on the control board, the infinity control thermostat won't come on… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an American Standard heat pump thats 8 years old. I
I have an American Standard heat pump thats 8 years old. I have two systems chained together so have 2 stages for heat and 2 for AC. My 5 amp fuse blows immediately almost daily. The system works fine… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heat pump based heating system died overnight. Robertshaw
heat pump based heating system died overnight. Robertshaw stat said -AC. No power at stat. Checked 24v transformer - good. Found blown fuse on control board and replaced. Still won't fire up… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a goodman self contained ac only. The unit does not
Hi I have a goodman self contained ac only. The unit does not turn on. I checked power and there is 240 v coming in to the unit. On the contactor the other side there is no power. The contactor is not… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Carrier 38eyg024300 outside unit and a Carrier fa4bnf030
We have a Carrier 38eyg024300 outside unit and a Carrier fa4bnf030 air handler. Our thermostat is a Nest 2 that has performed flawlessly for 2yrs. PROBLEM: Currently, the outside unit will cycle on fo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call
I have a 17 y.o Carrier gas furnace w 3 ton AC. When I call for AC thru the 'stat the indoor fan blower doesn't work and neither does the outdoor compressor/fan. When I open the indoor service panel a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Can a certified TRANE tech help me? 5V fuse keeps blowing
Can a certified TRANE tech help me? 5V fuse keeps blowing on Trane XR80 Setup: -Trane XR80 model DD1C120A9541A Furnace -Trane 2TXCC049AC3HCAA sitting on top of the XR80 (49,000 btu?) -Carrier 38TKB048… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My central AC Nordyne was not working from time to time and
My central AC Nordyne Miller was not working from time to time and then a week later failed completely; I thought it is the capacitor since nothing worked on the outside unit and I replaced it. Still … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a carrier heat pump. having problems in the air handler
I have a carrier heat pump. having problems in the air handler mod # XXXXX keeps blowing the 5 amp fuse on the control board. Replaced board, ran fine for about a hour, blew the fuse, replaced, blowed… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our Central Coleman EB20B unit has stopped working. It iced
Our Central Coleman EB20B unit has stopped working. It iced up then would not restart after it deiced. How should I test the thermostat? I'll test the 3 amp fuse with an ohmmeter. Thank You Ken Rohm… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My AC unit just stop running. We replaced the contactor and
My AC unit just stop running. We replaced the contactor and capacitor a month ago. I press the carbons n the contactor together and the unit starts. Could it be that the contactor was defective or is … read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump.
I have a Model #38YCC048-301, SN #2901E25036 Carrier Heat Pump. I was away on business for a week and shut it off completely. When I returned I energized the entire system, ie: Breakers, etc. The ther… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
carrier FY4A; PCD 5 amp fuse continues to blow; where do I
carrier FY4A; PCD 5 amp fuse continues to blow; where do I look for the short that is blowing this fuse?… read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
Attended service call for Carrier RTU Moel 48TJE008-511QE.
Attended service call for Carrier RTU Moel 48TJE008-511QE. No Function Unit Dead Found 5 Amp Blown Fuse on Control Board replaced fuse unit Ran For few minutes & went out again.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x