Modine hot dawg heater is indicating system lockout? please…

Customer Question
Modine hot dawg heater...

Modine hot dawg heater is indicating system lockout? please advise

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Recently, getting into winter now and need it to work

Contractor's Assistant: Do you plan on doing the work yourself?

Yeah, hopefully

Contractor's Assistant: Anything else we should know to help you best?

The indicator light is on the honeywell, I do not have teh "standard" control board of a modine, in other word I do not have teh orange and green lights in which the manuals mention

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/4/2017
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

What is the exact model number?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I can't find exact number
Customer reply replied 10 months ago
can you please provide me with information to get out of a systme lockout on my modine hot dawg heater?
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Model is on the ratting plate usually on the back or side of unit

Ask Your Own HVAC Question
Customer reply replied 10 months ago
ok we are getting it
Customer reply replied 10 months ago
JA25163N115V 60Hz 2.13AClass E
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

The info you gave me is the motor not the unit model

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

It's on a sticker

Ask Your Own HVAC Question
Customer reply replied 10 months ago
HD30AH0134single green light on honeywell flashes 6 times, which indicates system lockout
the fan blows
I attempted reset, turning off power and gas, then turning back on
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Stand by......

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

If System lookout does not reset, this means there is a high limit swich that is not reseting itself. it is probably defective and will need to be replaced

Ask Your Own HVAC Question
Customer reply replied 10 months ago
ok thanks
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Sorry it took longer it's because I have many calls toninght, and the only tech online tonight.

Best regards

Customer/p>

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

I noticed question is still opened

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I brought a Honeywell ct31a Moline hotdawg 75,000 btu garage
I brought a Honeywell ct31a for my Moline hotdawg 75,000 btu garage heater, the package did not tell me how many wire's the device had (the heater has 5 a RWYG and a C. Will it work with out a C wire … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a modine hot dawg heater, the issue is I had someone
Hi I have a modine hot dawg heater, the issue is I had someone install it and it fired up but the fan didn't cut in so we shut it off and figured out the fan motor was gone, I got a new one and instal… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Modine Hot Dawg garage gas heater. It was working
I have a Modine Hot Dawg garage gas heater. It was working fine all this winter until last week. It stopped blowing out the heat. I have tested the blower motor and it works. I put a meter on the conn… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hello I have the Modine Hot Dawg HD45AS0111. It runs fine
Hello I have the Modine Hot Dawg HD45AS0111. It runs fine if outside temps are high but as soon as it gets really cold it will not work after 1st instance. I can get it to work by either cutting power… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a new Modine Hot Dawg Model HD45AS011 heater. I get
I have a new Modine Hot Dawg Model HD45AS011 heater. I get code 4 (4 flashes) which is "ignition Lockout". This happens after the 4 cycles of trying to ignite. I get flames through all 3 burner tubes … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have Modine Hot Dawg 60AH0134 exhaust moter keeps turning
I have Modine Hot Dawg 60AH0134 exhaust moter keeps turning on and off when there is no demand from thermostat. I have even disconnected the thermostat and it still cycles on for about 5-10 seconds an… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I purchased a Dwyer ADPS Differential Pressure Switch (ADPS-04-2-N)
I purchased a Dwyer ADPS Differential Pressure Switch (ADPS-04-2-N) http://www.dwyer-inst.com/Product/Pressure/DifferentialPressure/Switches/SeriesADPS This is to replace a Modine Hot Dawg heater vacu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I need to replace a pressure switch for a Modine Hot Dawg Heater.
I need to replace a pressure switch for a Modine Hot Dawg Heater. The original switch is a Honeywell is20256-5328. The Modine part number is XXXXX It is a .27" WC switch. This thing HAS to have a cros… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hot Dawg heater runs for about a minute burners shut down and
Hot Dawg heater runs for about a minute burners shut down and then system restars but keeps shuting down. Have replaced control board and flame sensor plus jump out rollout circuit. could the new boar… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, Ive live in a six year old ranch-style home (built
Hello, I've live in a six year old ranch-style home (built in August 2006) that I bought in October 2010 that has an E Series furnace and closed loop system. Furnace model nomenclature is E048TL111NBD… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Modine Hot Dawg heater in my garage, model HD60AH0134.
I have a Modine Hot Dawg heater in my garage, model HD60AH0134. After sitting all summer, it hasn't worked right all fall/winter. I have replaced several parts--wall thermostat, pressure switch, flame… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a hd 60 hot dawg. The unit fires but sometimes the
I have a hd 60 hot dawg. The unit fires but sometimes the circulating fan does not come on. What would be causing this?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Modine natural gas unit heater ,i believe the flame
I have a Modine natural gas unit heater ,i believe the flame sensor is faulty, is there a way to test it?… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Recently I bought a modine 75,000 hot dawg for my lower 3 stall
Recently I bought a modine 75,000 hot dawg for my lower 3 stall garage. The old heater I was replacing was a Sterling heater with same specs. It worked great until it died; heating up fast and quietly… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
A year ago we moved from an all electric home to this one that
A year ago we moved from an all electric home to this one that has a Rheem PowerVent 2. 50 gal natural gas water heater that was manufactured 10/2004. Since the water heater was in the house when the … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Bryant 90 Plus AC unit will run (fan blows, see the outdoor
My Bryant 90 Plus AC unit will run (fan blows, see the outdoor unit running) - but no cold air -- just room temp. What should I do?… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
have a rheem 90 plus model RGED-12ERAJS, the problem is that
have a rheem 90 plus model RGED-12ERAJS, the problem is that in the ac mode the indoor fan does not come on. the control board has 2 green lights and 1 orange. when power is applied, the top green lig… read more
Paul
Paul
Vocational, Technical or Trade Scho
108 satisfied customers
I have a Hot Dawg model HD 75AH0134 with a Honeywell SV9410M2902
I have a Hot Dawg model HD 75AH0134 with a Honeywell SV9410M2902 gas valve. I have a steady blinking green light when the furnace kicks on. The ignitor glows orange but no gas seems to pass through th… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.