All right ... my furnace heater is not working brand and…

Customer Question
All right ... my...

All right ... my furnace heater is not working Bryant brand and there is a code on it ... like 33 and I am suspecting the board failure The label on the board is ... HK42FZ009 1012-940-L

Contractor's Assistant: Did you check the furnace's filters?

Hmm you mean .... the filter can cause this issue alone? I think I removed it ... and the problem was still there

Contractor's Assistant: Do you plan on doing the work yourself?

Yeah

Contractor's Assistant: Anything else we should know to help you best?

Nope ...that's it

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
10/4/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,753
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, one minute while I get some information together.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

This is likely a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

Here is a helpful video to see if you can locate the bad tripped limit on the unit.

CLICK HERE VIDEO

All I ask is please select the ***5 STAR RATING*** using the link at the top of your page before leaving, that is the only way I am credited through the site, tips are appreciated.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I just did this ... I only found one safety switch, and pulled the wires from it, so that the wires would be together, via a thin metal wire. The code 33 was still showing after I started the furnace. What's the next step?
Customer reply replied 10 months ago
Just to let you know, the cold air was blowing while the code 33 was blinking. There was no change.
Customer reply replied 10 months ago
Any answer???
Customer reply replied 10 months ago
I can’t use phone calls as I am not able to hear on the phone so detailed response is appreciated
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,753
18,753 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My furnace fan stopped running. i see a spot on the board
my furnace fan stopped running. i see a brown spot on the board above the blue resistor? its a honeywell emm3 multizone … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
Plus80v model number 315aav060110acja ... Furnace turns on
Bryant Plus80v model number 315aav060110acja ... Furnace turns on up to blower phase, burners are working then shut off before blower phase … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Having issues with a carrier 58pha 090-16 thermostat and a
having issues with a carrier 58pha 090-16 thermostat and a code 33. Months ago I removed the edge thermostat for a zwave thermostat so i can connect to my home automation system. Occasionally, the the… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
DuWayne, I came across the discussion thread It was very
Hi DuWayne, I came across the discussion thread http://www.justanswer.com/hvac/34umu-bryant-383kav-furnace-getting-error-code.html. It was very helpful with looking into the error code 31 issue I am h… read more
Jason Whatley
Jason Whatley
60 satisfied customers
My thermostat died so I bought a new one, a Honeywell
Hi - My thermostat died so I bought a new one, a Honeywell RTH6450. I got the wiring right - Red, White, Green are the connections. But now when I turn on the Bryant furnace, it reads a code 33 and th… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,753 satisfied customers
Have a Carrier furnace that is not lighting up the HSI. The
Have a Carrier furnace that is not lighting up the HSI. The ignitor ohms out as good. I unplugged the ignitor from the board and put a meter on the connection. Powered furnace up and it goes through a… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
, I have a Carrier Comfort 92 furnace and use it to heat
Hello, I have a Carrier Comfort 92 furnace and use it to heat a hot yoga studio to 112 degrees for several classes throughout the day. The heater was installed about 7 years ago and it has begun to ha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
. I gave the same problem-code 33. Only after following your
. I gave the same problem-code 33. Only after following your first steps, I get the 12 code seconds, then operation. Ignition and blower few minutes. Then it all shits off again...… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier furnace showing 33 alarm code. The filter was pretty
Carrier furnace showing 33 alarm code. The filter was pretty dirty changed it out but it won't go through ignition sequence induction and blower running… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58PAV that is short cycling. The furnace will
I have a Carrier 58PAV that is short cycling. The furnace will work fine for several minutes, burner is killed and furnace goes into shutdown (blower motors runs for x amt of time after burner cuts ou… read more
HVAC Guru
HVAC Guru
HVAC TECH
18,753 satisfied customers
Our thermostat is hard-wired, not battery run, but the readout
Our thermostat is hard-wired, not battery run, but the readout is blank. Concurrent with this strange situation is that the blower on the furnace runs continuously. I have changed the filter, thinking… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Payne furnace model PG8MAA042090 Code 33. When the air
Payne furnace model PG8MAA042090 Code 33. When the air filter is removed the furnace seems to run considerably longer, or experience no problems at all. With the new filter installed the furnace will … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant Model 373LAV048095 with a Control Board HK42FZ009
I have a Bryant Model 373LAV048095 with a Control Board HK42FZ009 that shows an error code with 2 short blinds and 1 long, I'm assuming is an error code of 21. The unit doesn't fire when tried the fir… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Bryant Series 80 Pus unit, Model 395CAV04811, it
I have a Bryant Series 80 Pus unit, Model 395CAV04811, it will fire several times but after a while it wont. Usually over night . If you turn off the Power off to the unit and turn it back on it start… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 88,000 btu Bryant furnance Model number 395CAV042091AEJA
I have a 88,000 btu Bryant furnance Model number 395CAV042091AEJA Series E Serial # XXXXX I keep showing a flashing code 13 but then later it will go to 33. I have checked and replaced my filters and … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Bryant central gas furnace that is virtually brand
We have a Bryant central gas furnace that is virtually brand new but has never worked right since we moved into our house. It will come on for a while but then shut itself down and then it will not re… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Carrier furnace/AC unit in my home. It operates on
I have a Carrier furnace/AC unit in my home. It operates on heat, not on cool. I have replaced the 5wire lead and thermostat to the control board, I have replaced the 2 wire control wire to the outsid… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58PAV070. The LED error code is flahing 12.
I have a Carrier 58PAV070. The LED error code is flahing 12. The draft fan starts. Ignitor glows. Flame starts. Heats up. Blower starts and runs 5 seconds then all stops. I swapped the pressure switch… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x