I have a 2 zone house with an oil burner, 2 air handlers and…

Customer Question
Hi, I have a 2...
Hi, I have a 2 zone house with an oil burner, 2 air handlers and 2 AC units. The system is connected to a Taco SR 503 zone controller, with zone 1 being the water storage tank, zone 2 being downstairs and zone 3 being upstairs.I want to replace the zone 2 (downstairs) thermostat with an ecobee3. I have 6 wires available already in the wall from the old system (rounded Honeywell thermostat for heat/cool).From the downstairs air handler there are 8 wires coming out.* 2 purple connected to "boiler"
* 2 orange connected to "24v valve" but are capped and not used
* white / green / red and brown (which appears to be common)The previous setup is an incredible mess of wires and I'd rather just start over.I need a walkthrough of which wires to connect to the ecobee terminals (presumably Rc / W1 / Y1 and C?) and how to connect them to the unit downstairs and the zone board.
Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
10/3/2017
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,708
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, we can do a few tests to see if the ecobee will work with your Taco SR zone controller.

.

Take a photo of the zone controller with its door open so I can see all the wires and read the letter where each wire is terminated. Post it here using the 'add files' link next to your send button, and I will mark it up with test instructions.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thanks for the reply... this is what things look like today...
IMG_20171003_011609392.jpgIMG_201...jpgIMG_20171003_011555574.jpgIMG_201...jpgIMG_20171003_111002796.jpgIMG_201...jpgIMG_20171003_011950129.jpgIMG_201...jpg
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago

Thanks

I am looking it over now... back in a few minutes

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 9 months ago

Looking at the Taco zone controller wiring those are heating only thermostats, the cooling wiring is a custom arrangement that will require a very well qualified HVAC controls specialist to be on site to sort it out for you... his bill will be in the $500 to $1,000 range if not more, and if indeed he is able to connect your ecobee to that system, This is not a 'plug and play' sort of situation.

Ask Your Own HVAC Question
HVAC Technician: Michael Ferryman,
 replied 9 months ago
Michael Ferryman
Category: HVAC
Satisfied Customers: 110
Experience: Operating Engineer at NRG Energy
Verified

you can wire any thermostat in place of the Honeywell one you are showing, what you definitely should not do is attempt to reinvent your system. Multi zone systems are typically not wired to the industry standard, for example red wires could be whatever they decided to use the red wire for. If you replace the thermostat and wire it like for like you should be in good shape. Take a picture of the back of the Honeywell before you remove it so you have something to fall back on. If you really want to rewire the system I can walk you through it but it will be extremely expensive and take likely a day or so to complete.

Ask Your Own HVAC Question
HVAC Technician: Michael Ferryman,
 replied 9 months ago

did you still need assistance with this?

Ask Your Own HVAC Question
HVAC Technician: Michael Ferryman,
 replied 9 months ago
Do you still need my help? If not can you give me a 5 star rating. Would really help me out. Thanks so much.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Michael Ferryman Your Own Question
Michael Ferryman
Michael Ferryman
Michael Ferryman
Category: HVAC
Satisfied Customers: 110
110 Satisfied Customers
Experience: Operating Engineer at NRG Energy

Michael Ferryman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,708 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am trying to find out what type of Trane system we have so
I am trying to find out what type of Trane system we have so I can properly install a smart thermostat. The exterior unit is a Trane XR - Model 4TWR5048H1000AA … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem RHLL-RM6024JA Air Handler, Looking at the
Looking at the Wiring Diagram trying to figure when is the changeover valve Color R- Hot C-Brn G-Fan W1 and W2 Jmp Totogther Y1- Yel connected to an Honeywell program hemostat R-R G-G Br-C Y1-Y W1&W2- Aux Missing the O?B Changeover valve … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am having problems replacing two old battery operated
I am having problems replacing two old battery operated thermostats with two Ecobee3 smart thermostats. A 'PAK' used to send 28V to the thermostats is necessary. I have a Carrier Weather Maker two zon… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Have a trane thermostat that is being replaced with an
have a trane thermostat that is being replaced with an ecobee3. trane has a black wire going to terminal BK. no terminal bk on ecobee3. where should this wire be connected. remainder of wires line up … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a Eveloution 95s furnace and a model 187a air
Hi, I have a Bryant Eveloution 95s furnace and a model 187a air conditioner and I would like to change the thermostat to an Ecobee3. Is that possible? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Thanks! I'm trying to connect my old thermostat with a Nest
Thanks! I'm trying to connect my old thermostat with a Nest Thermostat and I'm getting mixed answers on my wiring. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
Where is located the electrical control box on a York HVAC
where is located the electrical control box on a York HVAC MAC-MAH system? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a heat pump system with aux heat. Recently, I
I have a heat pump system with aux heat. Recently, I installed an Ecobee 3 thermostat and now appear to have no aux or emergency heat.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I installed an Ecobee3 thermostat to my Trane xv90
Hello, I installed an Ecobee3 thermostat to my Trane xv90 yesterday. I am only running heat. We do not have an AC system. The installation went great, but after about thirty minutes of running without… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I get a red light for "Heat 1" indicating my heat is on, but
I get a red light for "Heat 1" indicating my heat is on, but my T-Stats are all set to cool. I feel cold air coming from the vents but the pipe leading away from my furnace is super hot. Is it possibl… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I want to replace a 2-wire heat only thermostat (w/ batteries)
I want to replace a 2-wire heat only thermostat (w/ batteries) that's on a taco-hvac controller with an RCS z-wave thermostat so I can control via WIFI connection remotely. How does it need to be wire… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a two zone heated house built in 1999. The house is
I have a two zone heated house built in 1999. The house is equipped with a forced air furnace and air conditioning compressor. The zones are control via damper and Durozone SMZ-SW zone control logic b… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
my rheem air handler that has heat pump with auxiliary has
my rheem air handler that has heat pump with auxiliary has the terminals R C G W1 W2 Y1 - was going to try to wire it to a honeywell rth6350 - terminals listed on that are L aux/e G o/b Y R-RC - any i… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi, I have Rheem RHLL-HM6024JA air handler (Heat pump with
Hi, I have Rheem RHLL-HM6024JA air handler (Heat pump with aux heat) unit and trying to connect it to a Honeywell tst RTH7500 model. Labels from air handler is somewhat different from the air handler … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Greetings, I have two Taco 403 units connected to three zoned
Greetings, I have two Taco 403 units connected to three zoned manifolds, along with one Taco 503 connected to pumps associated with the thrre manifolds. My boiler is a Laars NTH and is located some di… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I bought a power robbing thermostat. The thermostat i had was
I bought a power robbing thermostat. The thermostat i had was non power robbing. I was only using three wires R, W, G. The new thermostat needs for wires R, W, G, and C or common. I connect the themor… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
Model RBHC-21J18SFC, serial T M 1002 05058, heat will not shut
Model RBHC-21J18SFC, serial T M 1002 05058, heat will not shut down at set temp. on thermostat. unit shuts down when set in off position. White-Rodgers 1F86-244 thermostat, similiar to Rheem series 10… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
how do I wire a baxi luna ht 330 boiler to a taco sr 503 switching
how do I wire a baxi luna ht 330 boiler to a taco sr 503 switching relay using a qaa 73to control 1 zone?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x