Condensate pump for a-c in split system ran continuously and…

Customer Question
Condensate pump for a-c...

Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on.

Contractor's Assistant: Did you check the furnace's filters?

I changed the furnace air filter in July.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

No, just trouble shoot.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
10/3/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,802
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, is the condensate pump sump dry or is it completely full of water, if its completely full it may be the type with a float switch that shuts off the AC when its full

Look into that, we can go from there

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Condensate pump is completely dry. I forgot to mention that Honeywell emailed me earlier in the morning and told me the furnace was not communicating with the thermostat, which shows nothing, just a black screen. When we found that the noise we heard was the condensate pump continuously running , we pulled the plug on it. The furnace will not come on.
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, ***** ***** of course is with the thermostat, OR the printed circuit board it is connected to inside the furnace....not at all an easy diagnosis.

.

A technician would simply attach a known good thermostat, and if that allowed the system to work would replace your thermostat.. if that failed he would replace the printed circuit board inside the furnace/air handler.

(after checking to make sure all of the wire connections were correct and that the 3 amp fuse in the printed circuit was not blown etc.)

.

Its time to locate the 'Finish and Rate your expert' link to close the question.... unless you would like me to coach you on a deeper diagnosis using a multi meter, that will take a few hours, there is no additional charge...

In that case you would also need to rate my work so far positively so that I do not loose my shirt going the extra mile for you on this.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,802
9,802 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,802 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Gibson furnace, split system model #JS5BD-030KA. ac was
Gibson furnace, split system model #JS5BD-030KA. ac was running fine, putting out cold air but now the air is luke warm. What should I check … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,802 satisfied customers
I had Honeywell RTH9580 thermostats installed in my Florida
I had Honeywell RTH9580 thermostats installed in my Florida vacation home last fall. This summer, the Lennox air handlers have been sweating in the a/c closet and dripping. A fan blowing on the units … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Goodman 3 ton split system. The attic air handler
I have a Goodman 3 ton split system. The attic air handler (fan) is running. Have checked the voltage on the thermostat and reads 27V. The voltage to the condenser is 27V. I have replaced the capacito… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am installing a new rheem split unit I wired everything
I am installing a new rheem split unit I wired everything except the b on thermostat to condensor I can't get the contactor to engage … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,802 satisfied customers
New lennox electric ac/heat unit - a/c ran fine all summer,
new lennox electric ac/heat unit - a/c ran fine all summer, turned on heat yesterday, runs one minute cold air and shuts off for about one minute, and comes on again for about one minute cold air, and… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,802 satisfied customers
I have a 5 Ton Lennox R22, Can I change the condenser to
I have a 5 Ton Lennox R22 , Can I change the condenser to "only" a 4r10 or does the furnace also need to be changed. Thank u… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox heat pump system, about 12 yrs old. It runs
I have a Lennox heat pump system, about 12 yrs old. It runs at night and morning, but once afternoon temp rises, the compressor stops working and no longer cools. Lennox authorized repairman has been … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,802 satisfied customers
Scott. Trying to trouble shoot my Honeywell VisionPro TH9421C1004.
Hi Scott. Trying to trouble shoot my Honeywell VisionPro TH9421C1004. This afternoon the screen just went blank. Can't get it to come back to life… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
why is my lennox cx34-44 producing water in the winter when
why is my lennox cx34-44 producing water in the winter when the furnace is running. The drain line runs through the attic outside and it freezes causes the reservoir not to empty then the furnace stop… read more
V12Tech
V12Tech
252 satisfied customers
I have a TH61101D1006 thermostat and it has just gone blank,
I have a TH61101D1006 thermostat and it has just gone blank, obviously no AC/Heat control. So, I do what?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,802 satisfied customers
The trouble shooting indicates the Primary or Secondary Limit
The trouble shooting indicates the Primary or Secondary Limit Switch is open. I cannot find where these switches are. The Model number is: 80MGF-7. Is there somewhere I can go to show me where these a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
White Rodgers thermostat type 1f89-211 This morning
White Rodgers thermostat type 1f89-211 This morning it was blank and the cac would not function. I put two AA batteries in the empty battery slot. This made it read ambient temp but nothing else. I de… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
What Is Best Solution for me for filters for home HVAC Systems I
What Is Best Solution for me for filters for home HVAC Systems? I live in a 1940s stone house under trees with a long-haired cat, so lots of dust in my home. I am currently replacing filters in my gas… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Coleman Furnace w/ AC. Its a split system on a Manufactured
I have a Coleman Furnace w/ AC. It's a split system on a Manufactured Home built in 1986 This has been a very reliable system. My question concerns the heat and air fan. Just today the fan quit blowin… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
In My furnace when I turn temperature up to turn on Heater,
In My furnace when I turn temperature up to turn on Heater, I hear FAN, and physically checked little motor there is spinning, but I do not see heat kicks in. To turn on the heat I have to turn off th… read more
Bill
Bill
High School or GED
318 satisfied customers
I have a Coleman Gas Furnace Model #DGAT090BDD, SERIAL XXXXXXXXXXX The
I have a Coleman Gas Furnace Model #DGAT090BDD, SERIAL XXXXXXXXXXX The furnace works fine, however the fan goes off and on continually. Finally, it will stop. The air conditioner that is connected to … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
Where is the filter on the Trane XB 1000 Is it in the air
Where is the filter on the Trane XB 1000? Is it in the air handler? The unit is approx 4-5 years old and I don't believe the filter has ever been changed. My current problem is when I turn the split u… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a york heat pump, and its now needing its 3rd pump
I have a york heat pump, and it's now needing it's 3rd pump replacement, the unit is only 6 years old, and I'm really tired of paying 600.00 per year to get the pump replaced. Is there anything I can … read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x