My ac was making a high pitch noise that I could hear from…

Customer Question
Hello, My ac was making...
Hello, My ac was making a high pitch noise that I could hear from inside. When I went outside to investigate the condenser fan was not turning. I turned the unit off and waited approx. 15 mins and restarted. The unit worked fine for a short while and then went back into the same mode, ie, compressor making a high pitch noise and condenser fan not turning. I have since replaced the fan motor and the unit worked fine for approx. two weeks and then back to the same condition. I replaced the dual capacitor (45uF/5uF) with no luck, same condition. I did notice that the cold line starts out cold and then sometime before the condenser fan stops the cold line warms up to approx. outside temp. right before the condenser fans stops. Does this sound familiar? Any suggestions would be appreciated.
Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 33 minutes by:
9/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,371
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, IF... that is a heat pump unit that cools in the summer and heats in the winter, it sounds like a bad defrost control board.

.

I need the full model number of the unit outside to go further.

.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Thanks, the compressor and the condenser fan both get power from the SAME T1 and T2 terminal on the big relay (called a contactor) that sends power to both the compressor and fan motor at the same time.

Primary suspect is a burnt wire at either T1 or T2 on the contactor... inspect for that.

Regarding the high pitched sound. that is almost normal if the condenser fan is not running, it should make a high pitched sound with the condenser fan is running at the same time. However the unit should have a high pressure safety cut out switch that cuts off the compressor if the fan fails.

If you can take a close up. exceedingly well focused photo of the wiring diagram glued inside the units electrical controls box, I can mark it up with trouble shooting directions.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Hi Phil, Please find attached a photo of the schematic for my ac. I noticed the picture was distorted when viewing within an email but was clear if I saved it on my computer and viewed it a jpeg viewer. I also found a sticker inside the control circuits that gives the model number and serial number for my unit. I am attaching a photo of that as well. I inspected the wires connected to the contactor and did not see anything obvious that looked burnt. The contactor button itself looked a little worn but not anything alarming. I'm thinking I will measure the voltage on the fan motor before and after stopping. I am an Electrical Engineer but I work in semiconductor testing where the power supply voltage I deal with ranges from 1.5 to 0.8V DC. I am very cautious when working around household level voltages(I am aware of how little current across the heart to start ventricular vibrillation) and I would be so embarrassed for my obituary to say EE killed by electrocution. :-)
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Thanks, ***** ***** know how your tests go.

Here is a story for you, one of the guys working for my company about 40 years ago, wrapped the 18" long extension of my socket set in electrical tape, and taped the socket on the end, then reaching gingerly between the 480v 600 amp buss bars, reached the bolts holding the 600 amp 3 phase breaker in place , he was standing on a thick rubber mat with one hand in his rear pocket (prevents current through the heart he was told)... then when extracting the extension, there was a blinding flash, and all he got back was the completely vaporized stub end of the extension, no socket, another $3 down the drain, It didn't even blow the fuses at the pole transformer.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
HI Phil, I had a professor say during a lecture that he always has one hand in a pocket when working around hi voltage circuits. It stuck with me. I can't say I always do that but it made me think about the path current will take should I accidentally touch something hot. Too bad about the socket. I bet your guy had to go clean out his shorts after that. :-)
I made the measurements using my volt-ohm meter set to 300V ac setting: with power applied to the ac but before thermostat switched to cool measuring between the Fan terminal of the capacitor to the common terminal read 0V, same reading between Herm and common. After switching thermostat to cool, contactor closed and Vfc=220V, Vhc=340V (maybe higher since I am on 300V scale, but I don't have a higher setting) The unit ran with the condenser fan spinning as normal for approx. 15 mins. My upstairs unit, which is next to the one I am having trouble with, was running at the same time. Before the fan stopped running I noticed the warm line on the broken ac was much hotter than the working upstairs unit and the cold line from the broken unit never got cold enough to sweat. After about 15 minutes the fan stopped and the reading for Vfc was zero volts while the Vhc was still 340V. The contactor was solid closed.
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Hello again, readings between herm and common a the capacitor will not produce a voltage read since they are in essentially the same line,

IF a capacitor is bad, the motor will attempt to start, get hot, then trip its internal overload... we check the amperage draw on the common going to the motor when it is first energized to determine if its attempting to start or not, it will draw its Locked Rotor Amperage (LRA) listed in the unit name plate.

If we get no amperage read on the common going to the motor in question when power is first applied, then we disconnect the wires to the motor and measure ohm reads between each of its windings, Common, Start and Run windings.

The ohm read between Start and Run will be the total of the reads between Comm and Start and Common and Run if the motor windings are good.

If we want to check the capacitor, we disconnect the wires to it, and use a multi meter with a microfarad scale to measure microfarads between comm and herm and common and fan. we check those reads against the ratings stamped on the side of the capacitor.

Good luck with it, stay in touch as needed.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,371
9,371 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,371 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
do you have a trane heat pump error code chart
do you have a trane heat pump error code chart… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
central air just started making a VERY LOUD sort of humming
central air just started making a VERY LOUD sort of humming sound - not rattling rt banging..have changed the filter...what is the problem? We have lived here for 6 years and have never had a problem … read more
Ryan V.
Ryan V.
UA Local 350 Journeyman
High School or GED
6 satisfied customers
I have a rheem prestige series furnace, that is flashing code
I have a rheem prestige series furnace, that is flashing code "66". I have replaced the filter, hosed out the A/C unit, and checked the internal blower motor fo operation, and it spins freely. What el… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
The condenser unit on our central a/c stopped working. Upon
The condenser unit on our central a/c stopped working. Upon inspection I discovered two wires on the load side of the contactor had burned completely off the spade connector. The circuit breaker never… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE
I JUST REPLACED THE CONTROL BOARD IN THE CONDENSER AND THE ERROR CODE I AM GETTING SAYS "EE" =compressor relay contacts welded … read more
Bill
Bill
Service Mgr
98 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
9,371 satisfied customers
Condenser fan going counterclockwise. Just notice it. put a
just notice it. put a new motor in it , but has differ color wiring … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Looking to buy replac ement condenser to model nac036akc3
Looking to buy replac ement condenser to model nac036akc3 serial e040516483 … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
How do I determine the reversing valve polarity of any given
How do I determine the reversing valve polarity of any given heat pump system?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
where do I hook the two wires from the condenser to the fu
where do I hook the two wires from the condenser to the furnace… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
if my goodman heat/pump / air conditioner outside unit quits
if my goodman heat/pump / air conditioner outside unit quits in high heat conditions what part likely went out… read more
Phil
Phil
Mechanical Engineer
9,371 satisfied customers
My heat pump mini-split unit has stopped producing hot or cold
My heat pump mini-split unit has stopped producing hot or cold air. The indoor fan still works, but it just blows unheated / uncooled air. It shows a P4 error code on the indoor unit. A technician che… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Fault code 179 appears on my INFINITY thermostat for
Fault code 179 appears on my INFINITY thermostat for INFINITY series condenser. Turning power on/off did not re-start system. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How do you bypass defrost control board to test if it is reason
How do you bypass defrost control board to test if it is reason why no 24 V at contactir… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x