I have old Compressor using R22. I replaced: 1)

Customer Question
HI! I have old...

HI! I have old Bryant Compressor using R22. I replaced: 1) timer/deforst brd, 2) Deforst Stat, 3) 24V Contactor, and 4) 24v Reversing Valve coil. At blower unit, replace burned out transformer and connected new thermostat.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Question: Now it runs in AC cooling mode and compressor comes on, but in heating mode, it seems to only heat with electrical element and the compressor not coming on?

Contractor's Assistant: Do you plan on doing the work yourself?

Actually had 2 repairmen come, one replace transformer and another diagnosed timer/defrost brd as bad... So I replace all items, except transfomer.

Contractor's Assistant: Anything else we should know to help you best?

Question, In heat mode, is there a temperature sensitivity before the compressor should kick in? Like there isn't enough temperature differnce?

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 7 months ago
Problem: When I turn on to heat, blower works and hot air from vents, except compressor not coming on. So I believe it's heating ONLY by electric coils. When should compressor kick in, after 5-minute, right? But not coming on....
Customer reply replied 7 months ago
what could be the problem with compressor???
Customer reply replied 7 months ago
If problem is with the replaced transformer (gone bad again), I'd expect that in AC mode compressor also would not function, but it does!
Answered in 19 minutes by:
9/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like the O/B terminal on the thermostat is not connected properly... I need the brand and model number of the new thermostat, and a photo of the wire connections there, I need to know which color wire attached to each terminal on the OLD thermostat... you can attach those here using the 'add files' link next to your send button.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Will do!
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Great, I will be here

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I noticed on 1st Flr wiring, W2 (or White) is jumpered at Aux and E (emergency heat) and black is wired to "C" which cheaper thermostat does not have....
Customer reply replied 7 months ago
Phil, any advice to offer? Try other thermostat or something else to check?
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

Hello, tape the old C and L wires.

Try the system as you have it wired in both heating and cooling modes, the outside unit should run in both cases, the largest copper tube connected to the outside unit should be cool in cooling mode and hot in heating mode.

Let me know how that goes in the simplest terms possible we can go from there

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Taped wires but didn't work to get compressor to engage during heat mode. Unsatisfied with advice and ending service!
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

These things are far far from simple, it takes several steps to get it right in many cases, let me know if you would like to continue or not, we can go from there

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Not continuing!
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago

These things are far far from simple, it takes several steps to get it right in many cases, let me know if you would like to continue or not, we can go from there. I have been here now for 7 years, with 8,600 questions answered, with a 98.4% success rate..

Ok, goodby in that case sorry it didnt work out

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
This house is missing the circuit breaker for the disconnect
This house is missing the circuit breaker for the disconnect for the outside ac unit. What do I need to get to repair this?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a 4 wire thermostat and upgrading to a thermostat
I have a 4 wire thermostat and upgrading to a thermostat that requires a common wire. There is an additional wire but I don't think it's connected to the hvac system. I live in an apartment and the fu… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
452 satisfied customers
My cental air is not working in my home. the unit outside is
my cental air is not working in my home. the unit outside is running , but no air is coming out of my vents … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a Lennox HS19-411u-79 air conditioner. It has started
I have a Lennox HS19-411u-79 air conditioner. It has started to drain water out of the overflow pipe along with the regular pipe that leads outside ( this part of the unit is enclosed) will drop for h… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a HoneywellHPA-24X. I CHANGED THE FILTERS and now I
I have a HoneywellHPA-24X. I CHANGED THE FILTERS and now I cannot get it on again. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I replaced my thermostat with a programmable one of the same
I replaced my thermostat with a programmable one of the same brand, with same labeling on pins. I didn't have to move any wires. I turned off breaker for air handler and compressor before replaced. Ai… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I live in Florida and a good HVAC is essential. We were
I live in Florida and a good HVAC is essential. We were quoted for a 3 ton 14 Seer new system. Our current one is made by Rheem but is from 1994 and we badly need a new one. The vast majority of our q… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,796 satisfied customers
I have just installed a new copeland compressor ( model
I have just installed a new copeland compressor ( model zr48k53-pfv-7me)and it won' start. Looks like it is wired right. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just bought a house and I turned the air on and it is
I just bought a house and I turned the air on and it is coming out but doesn't seem to be circulating I went outside and the outside unit isn't even on or running … read more
David Bowden
David Bowden
Owner
845 satisfied customers
I have a rheem air exchanger RBHC It is suspend. Ed from
Ed from floor joists in step space with springs on one end. Just bought this house and my building inspector says I should put blocks under to keep from vibrating, but it seems to me it was suspended by springs for a reason … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
60 satisfied customers
Apt AC & Heat system controls are not working properly.
Apt AC & Heat system controls are not working properly. Seeking manual to explain how to reset controls for IF90-371 programable thermostat … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I just tried to switch out pump on taco 00 circulating pump
I just tried to switch out pump on taco 00 circulating pump and had New seal in place and bolted down tight. When I turned it on it had a couple drips after opening valves. When I turned hot water on … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rite Temp 8022 Thermo stat. Thermostat. Takes 20-50
Takes 20-50 pushes on Temp decrease to get temp to drop… read more
David Bowden
David Bowden
Owner
845 satisfied customers
Just switched out my IFC and went to start the heater but
Just switched out my IFC and went to start the heater but i'm getting a 6 flash error code for a "115 volt AC power reversed/improper ground". I have a trane 80xe furnace with a 50A55_843 a new univer… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
452 satisfied customers
Model 12hpb48-14p led1and led2 are flashing. compressor unit
model 12hpb48-14p led1and led2 are flashing. compressor unit will not come on. air handler fan works in manual. what does this mean? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Vegetables freezing in crisper and cold water is not working
Vegetables freezing in crisper and cold water is not working but ice maker is … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
How do I replace the battery's. How do I get cover
How do I replace the battery's . How do I get cover off.Thermostat is 10 years old. Similar to th2210DV1006 PR … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I can't get my gas fireplace pilot to light even though
I can't get my gas fireplace pilot to light even though there is gas up to valve. No gas comes while depressing pilot control. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,796 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x