I have old Compressor using R22. I replaced: 1)

Customer Question
HI! I have old...

HI! I have old Bryant Compressor using R22. I replaced: 1) timer/deforst brd, 2) Deforst Stat, 3) 24V Contactor, and 4) 24v Reversing Valve coil. At blower unit, replace burned out transformer and connected new thermostat.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Question: Now it runs in AC cooling mode and compressor comes on, but in heating mode, it seems to only heat with electrical element and the compressor not coming on?

Contractor's Assistant: Do you plan on doing the work yourself?

Actually had 2 repairmen come, one replace transformer and another diagnosed timer/defrost brd as bad... So I replace all items, except transfomer.

Contractor's Assistant: Anything else we should know to help you best?

Question, In heat mode, is there a temperature sensitivity before the compressor should kick in? Like there isn't enough temperature differnce?

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 10 months ago
Problem: When I turn on to heat, blower works and hot air from vents, except compressor not coming on. So I believe it's heating ONLY by electric coils. When should compressor kick in, after 5-minute, right? But not coming on....
Customer reply replied 10 months ago
what could be the problem with compressor???
Customer reply replied 10 months ago
If problem is with the replaced transformer (gone bad again), I'd expect that in AC mode compressor also would not function, but it does!
Answered in 19 minutes by:
9/30/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like the O/B terminal on the thermostat is not connected properly... I need the brand and model number of the new thermostat, and a photo of the wire connections there, I need to know which color wire attached to each terminal on the OLD thermostat... you can attach those here using the 'add files' link next to your send button.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Will do!
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Great, I will be here

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I noticed on 1st Flr wiring, W2 (or White) is jumpered at Aux and E (emergency heat) and black is wired to "C" which cheaper thermostat does not have....
Customer reply replied 10 months ago
Phil, any advice to offer? Try other thermostat or something else to check?
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Hello, tape the old C and L wires.

Try the system as you have it wired in both heating and cooling modes, the outside unit should run in both cases, the largest copper tube connected to the outside unit should be cool in cooling mode and hot in heating mode.

Let me know how that goes in the simplest terms possible we can go from there

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Taped wires but didn't work to get compressor to engage during heat mode. Unsatisfied with advice and ending service!
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

These things are far far from simple, it takes several steps to get it right in many cases, let me know if you would like to continue or not, we can go from there

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Not continuing!
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

These things are far far from simple, it takes several steps to get it right in many cases, let me know if you would like to continue or not, we can go from there. I have been here now for 7 years, with 8,600 questions answered, with a 98.4% success rate..

Ok, goodby in that case sorry it didnt work out

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
GPH1448H41 goodman 4 ton heatpump package compressor/fan not
GPH1448H41 goodman 4 ton heatpump package compressor/fan not engaging, 240v at contactor input reading 120v on each leg of contactor output but 0v nothing, natta zip whenvoltage is read across the two… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
What would make a rheem rbhc24j21sfb model blower work on On/cool
What would make a rheem rbhc24j21sfb model blower work on On/cool but nothing else engage and blower doesn't work or anything else on Auto/cool or heat/auto no contactor pulls in compressor or fan wor… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Bryant 213BNA024000BAAA 2.0 Ton Heat Pump that doesn't
I have a Bryant 213BNA024000BAAA 2.0 Ton Heat Pump that doesn't want to run right. The unit was installed in 2012 by a Bryant dealer and authorized service company. All the work below was done by the … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a goodman condenser unit that keeps blowing my transformer.
I have a goodman condenser unit that keeps blowing my transformer. I clipped a burned wire on the 240v going into the contactor from the disconnect because it kept tripping my breaker. Now my transfor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm trying to troubleshoot my HVAC system as when I turn it
I'm trying to troubleshoot my HVAC system as when I turn it to cool, the blower kicks on but the compressor/fan doesn't kick on outside. I'm getting 24v at the control board from the transformer, but … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Replace a bad control transformer on a trane residential furnace
Replace a bad control transformer on a trane residential furnace and now the fan blower will not shut off. The contactor coil in the a/c is testing as if its shorted so I disconnected power going to t… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
Bryant heat pump no apparent power to thermostat. Which wires
Bryant heat pump no apparent power to thermostat. Which wires should have voltage on t-stat wires ? Which is common ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an older model York Slit system with a Heat Pump. The
I have an older model York Slit system with a Heat Pump. The heat stoped working recently and I was told to try replaceing the T-Stat. The old t-stat was a Mercury filled bulb style and the new one is… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I just installed a honeywell touch screen thermostat and
Hi, I just installed a honeywell touch screen thermostat and the heat runs fine and the blower ran fine but then I wired in the condenser to the Y & C and every time it switches to cool it resets or g… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have heat pump condesor with 28v going to the defrost board
I have heat pump condesor with 28v going to the defrost board but the condenser will not come on in either heat or cooling mode… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Payne furnace model #394GAW036075 and a Payne a/c
I have a Payne furnace model #394GAW036075 and a Payne a/c compressor model #PA10JA030-C. I recently replaced the air filter and now the compressor will not turn on. I have "wiggled" the wires next to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Payne PH10JA036-E Heat Pump, PF1MNA Fan Coil, and
I have a Payne PH10JA036-E Heat Pump, PF1MNA Fan Coil, and Bryant TSATBBPHP01-B Programmable Thermostat. Found house cool, no power to thermostat. Found 5 amp fuse on control board in fan coil blown. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
how to wire a water control valve on and open system water
how to wire a water control valve on and open system water cool heat pump. we were sent a 24 volt dc. transfomer to power the valve.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello. By using a previously answered question and a voltmeter
Hello. By using a previously answered question and a voltmeter I was able to trace a Trane EX90 AC unit start-up problem to a blown 24V transformer. I was getting the proper voltage(s) thru all switch… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press contactor compressor comes on with indoor blower evaporator fan does not relay clicks no operation,contactor good any suggestions would … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane unit. On cool works fine. On heat blower kicks on for
Trane unit. On cool works fine. On heat blower kicks on for just a second then off right away. Replaced run cap, pc, transformer, contactor and time delay. 24v from red to white on thermostat. Contact… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a rheem 10 ton gas pack RRGF200100. The fan contactor
i have a rheem 10 ton gas pack RRGF200100. The fan contactor is not being pulled in , but the compressor comes on and starts the cooling cycle. The switching relay and the fan relay seem to be ok.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
my carrier model #38yr outdoor unit will not run neither fan
my carrier model #38yr outdoor unit will not run neither fan or compressor. indoor unit runs… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x