My Nordyne furnace blower starts immediately when I turn on…

Customer Question
My Nordyne furnace blower...

My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame.

Contractor's Assistant: Did you check the furnace's filters?

Yes. I removed the filter entirely for a test.

Contractor's Assistant: Do you plan on doing the work yourself?

If I can. I'm pretty competent.

Contractor's Assistant: Anything else we should know to help you best?

The blower started coming on by itself in the summer time, so I shut off the main switch. At least once while I have been troubleshooting, it went through the sequence and fired properly. Now it wont't.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
9/30/2017
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to Just Answer. My name is ***** ***** I'll be happy to assist you today. Can you please provide the full model # for the furnace?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
It's M1MB077ABW
Customer reply replied 10 months ago
Serial # M1M001106168
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, thank you. I show 5 flashes is "115 vac & neutral reversed or no ground." Has there been any electrical work done recently?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
No.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, let's check in the furnace to make sure the unit is grounded first. Take a look where the power comes into the unit and see if there's a copper ground wire that connects to the cabinet of the furnace.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
ad connection is tight.8
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, let's go ahead and try to reverse polarity just to eliminate that as a possible problem. First, turn the power to the unit off, then remove the wire nuts on the two wires coming into the unit and swap them. Then turn power back on and see if you still get the 5 fashes.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Yep, still 5 flashes.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, go ahead and switch the wires back. Do you happen to have a volt meter?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I have one. It will take a few minutes to get it.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

No problem - Go ahead and test volts AC between L1 and and of the NEUTRAL terminals on the control board.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
OK, got it.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, good. Let me know what you read between L1 and Neutral on the board

Ask Your Own HVAC Question
Customer reply replied 10 months ago
No reading L1 and neutral. But I found that I can restore connection and get steady light by holding in on the connector. That seems to be where the problem is.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Yeah, signs were pointing to a bad control board. Is the terminal on the wire loose on the terminal on the board? If so, you could use a pair of pliers to tighten the connector on the wire so it fits tight on the terminal on the board. If the terminal is tight then it looks like we have a loose solder joint on the board, which would require a re-solder on the connection or a new control board.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I'll check.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago
Okay thanks
Ask Your Own HVAC Question
Customer reply replied 10 months ago
Wires seem tight, and now I can't get a connection, so it probably is a solder loose. I will remove the control board and try re soldering before replacement.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, let me know what you find

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Good afternoon - Did you have any luck finding a loose solder connection on the board?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a G61MPV-36B-071-10 furnace, Code 1-2 is on. I have
I have a G61MPV-36B-071-10 furnace, Code 1-2 is on. I have replaced the igniter and the flame sensor. The igniter never glows and no gas enters burner. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Keep getting 4 flashing red lights on the control panel,
Keep getting 4 flashing red lights on the control panel, have gone through the gas furnace lighting instructions. Same result. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem RDGD furnace. The flame led lights steady and
I have a Rheem RDGD furnace. The flame led lights steady and burners burn until main blower turns on. Then flame led starts blinking, and sometimes the furnace will shut down and then restart. I have … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
My furnace is not working correctly. I have fixed several
My furnace is not working correctly. I have fixed several items on it before, but none are working. The main blower motor comes on a few seconds after turned on and the flame sensor light is blinking … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
, I'm referencing a thread you answered 2 years ago. The
Hi, I'm referencing a thread you answered 2 years ago. The customers initial question relating to the Nordyne furnace Model: G6RC060C-12, describes my situation very closely. When you ask about a dirt… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have the weathermaster 8000 58wav110, it wouldn't turn on.
I have the weathermaster 8000 58wav110, it wouldn't turn on. I did self test and all 4 sequences went fine. I pushed reset, turned off gas and waited hours, changed the igniter . what next?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane xb80. Furnace comes on, but won't move the heat. The
Trane xb80. Furnace comes on, but won't move the heat. The small exhaust fan comes on, and the burners fire. Originally I had 4 flashes on the LED. I reset the limit switches and now they're reading a… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have had snow freezing temps in colorado the past 2 days
We have had snow freezing temps in colorado the past 2 days (-1 this am) woke to thermostat reading 44. Checked furnace and black circle thing was rotating very slowly. I went through process of dropp… read more
Joe Chappell
Joe Chappell
Building Engineer
7 satisfied customers
I have an American Standard Freedom 90 Comfort R furnace. It
I have an American Standard Freedom 90 Comfort R furnace. It has been not always heating the house. I have watched it through it's start up. It will start by firing up the gas then turning off, then f… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
hi i have a 80+, 90+ upflow furnace 703956A. the problem with
hi i have a 80+, 90+ upflow furnace 703956A. the problem with the unit is that when i turn on the unit and set it to a temp of 75. the unit fires up and goes up from the current room temp of 60 to abo… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, this morning the induction fan came on, then furnace
Hello, this morning the induction fan came on, then furnace lit, then blower came on as usual, but then induction fan keep running, then about 1 min later, flames cut off, then induction fan quit, blo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem gas furnace that cycles and starts runs for 5-10 minutes
Rheem gas furnace that cycles and starts runs for 5-10 minutes main blower shuts off small vent blower restarts and main blower restarts what is wrong… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Gibson KG6RC080C-16B furnace that is not heating... It
I have a Gibson KG6RC080C-16B furnace that is not heating... It uses Nordyne 624631-a control board and a 904081 gas valve. I am getting a constant flash from the red led on the control board. After r… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a elite model ghr26q3-75 My problem is that the furnace
I have a elite model ghr26q3-75 My problem is that the furnace will start and run for a bit then shut down it shows a error code of left led on right led slow flash I cleaned filter and then removed f… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
We have a Bryant central gas furnace that is virtually brand
We have a Bryant central gas furnace that is virtually brand new but has never worked right since we moved into our house. It will come on for a while but then shut itself down and then it will not re… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello. I have a Trane XB90 propane gas furnace. When the
Hello. I have a Trane XB90 propane gas furnace. When the thermostat calls for heat, the furnace starts up, the burners fire, and the blower begins to cycle the air as you would expect. However, after … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Tempstar DC90 Model # NUGMO75EGB1 My furnace stopped heating.
Tempstar DC90 Model # XXXXX My furnace stopped heating. It was working fine and then at the end of its normal cycle, after it purged any remaining heat, it continued to run without heat. I turned the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem Corsaire heater. The flame does not come on.
I have a Rheem Corsaire heater. The flame does not come on. The green LED blinks once (1-hour lockout) and the yellow flame LED is in fast blink mode. When I switch the thermostat on, the fan above th… read more
Ryan V.
Ryan V.
UA Local 350 Journeyman
High School or GED
6 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x