I have a Prestige solo 110 boiler that gets the E 02

Customer Question
I have a Prestige...

I have a Prestige solo 110 boiler that gets the E 02 lockout. In the past I have had the small explosion noise, but I haven't noticed that in some time. Do I need a new igniter, is there a kit to fix this, and do you have names of good technicians in the Boston area? Thank you.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A few years.

Contractor's Assistant: Do you plan on doing the work yourself?

No

Contractor's Assistant: Anything else we should know to help you best?

Well, it happened again this morning, and I work all day and have a parrot, so the heat can't go out. I have supplemented with electric just in case in the past few winters. It does not happen every day, but I am nervous that that may someday be the case. This apparently is a common problem so I assume you guys know the answer. Thx!

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

It is a boiler, not air unit

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
9/30/2017
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,602
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

If you've had "explosions" that's an indication of delayed ignition. The fix is usully to clean the burners. This is something best left to a trained technician. I'm sorry but I can't make a direct referral. You could try a referral service Like HomeAdvisor.com or Angie's list. There is no cost to you for these referral services.Be sure to mention the brand and model of your boiler when you fill ut your service request.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Ok
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

Do you have more questions?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
No thank you
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

You're welcome

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,602
24,602 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a TT prestige solo 110 Boiler with DHW. The unit
I have a TT prestige solo 110 Boiler with DHW. The unit works fine for heat but will not work in DHW mode. Get codes A82 and U1.35 whih are not in manuals I have. What should I check? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
My boiler is showing asoft reset and I can't reach my
My boiler is showing asoft reset and I can't reach my dealer … read more
Rick
Rick
HVAC Supervisor
24,602 satisfied customers
The prestige boiler to the circulator pump for the baseboard
the prestige boiler to the circulator pump for the baseboard hot water system … read more
Rick
Rick
HVAC Supervisor
24,602 satisfied customers
We have a prestige solo 110 which has stopped working. The
Hi. we have a prestige solo 110 which has stopped working. The display keeps cycling between 8 96, d OFF, 1 96, 5 96, d 150 (d in both cases is flashing). I haven't been able to locate this situation … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hard lockout with my triangle tube prestige solo 110 water
hard lockout with my triangle tube prestige solo 110 water boiler in my home shows E 14 error: internal control failure. Where do I do from here?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a triangle tube prestige boiler that seems to be in
I have a triangle tube prestige boiler that seems to be in a cycle of soft lockout. The power went out yesterday in the evening and I woke up in a cold house. Initially did a hard reset, giving me err… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Prestige Solo 110. ser. # ***** It will not restart
I have a Prestige Solo 110. ser. # ***** It will not restart with reset button. Upon pressing reset button, a blower will run for a few seconds and stop. Error codes seem to change. Codes noted are: O… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
why should i contract for a Lennox GWM-150IE modulating gas
why should i contract for a Lennox GWM-150IE modulating gas boiler rather than a Triangle Prestige Solo 110 gas fired boiler? (I am replacing the 12-year-old boiler on a Lennox complete heat system th… read more
Rick
Rick
HVAC Supervisor
24,602 satisfied customers
We have a Solo 110 that is 6.5 years old. It is showing a hard
We have a Solo 110 that is 6.5 years old. It is showing a hard lockout code of U1.35. There was some ice build-up on the roof vent. I would like to reset it and see if that was the problem before call… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Triangle Tube Prestige Solo boiler getting error code E28
I have a Triangle Tube Prestige Solo 110 boiler NG. I get an error code E28 (no blower signal present). I push the reset button and it will fire back up and run through the heating sequence. I checked… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
We have a Prestige solo 175 for radiant floor heat. We continually
We have a Prestige solo 175 for radiant floor heat. We continually get the flashing 9.70 and B 26 error message indicating a soft lockout. We cannot get the unit to heat our home. Can you help us with… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I hope you can help me get the right answers...I work for a
I hope you can help me get the right answers...I work for a commercial heat and mec. contractor but I am not a plumber or pipefitter and the guys I work with aren't familiar with residential systems. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hello, I need to replace the 45+ year old atmospheric boiler
Hello, I need to replace the 45+ year old atmospheric boiler in my home and have gotten prices for direct vent, modulating condensing boilers - Triangle Tube Prestige Solo 60 & 110 and HTP Elite EL-80… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Triangle Tube boiler (Solo Prestige) wont fire and has
My Triangle Tube boiler (Solo Prestige) won't fire and has a hard lockout with a E-14 error code (internal control failure). Resetting it doesn't work. what can I do?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Triangle Tube Prestige Solo 110 less than a year old.
I have a Triangle Tube Prestige Solo 110 less than a year old. In winter conditions but not summer (just when the baseboard hot water is being used) it makes a very loud noise for about 2 seconds at t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Im a contractor, not a mechanical or plumbing contractor,
I'm a contractor, not a mechanical or plumbing contractor, who needs to have this Triangle Tube Prestige 110 HE Boiler with a Triangle Tube Smart 50 Indirect water heater installed for this job. It ne… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Hello! I am in Colorado with a milled log home (Pretty airtight
Hello! I am in Colorado with a milled log home (Pretty airtight compared to regular log homes) with a heavily insulated roof and efficient window. It has 2100 square feet to be heated. Four zones. We … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x