My furnace is throwing cold air. Model m801p100cu60aaa.

Customer Question
My furnace is throwing cold...
My furnace is throwing cold air.
Model m801p100cu60aaa. Flashing light blinks 3 times then pauses, blinks three times then pauses... pressure switch problem?
Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
9/29/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,806
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, do you hear the small inducer blower start as you set the thermostat to heat? if so, and if nothing else happens after that, it could be a bad pressure switch. Read the following and send me a photo of the wiring diagram, I will mark it up with trouble shooting instructions

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Hello, click here please. use a multi meter to measure the voltage between R and C terminals marked in yellow. Check that 5 amp fuse.

Then get me a photo of the actual wiring diagram (its a flat sheet of paper about 12" square, and it is glued to the inside of the blower access door, photo needs to be close up, taken straight on, in good light, and it must be *exceedingly well focused.

We can go from there

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, click here please, I have circled the pressure switch in blue, it should have Orange and Yellow wires attached, its about 4 inches round in most cases, mounted near the small inducer blower. and has one or two 1/4" black rubber tubes attached.

The verify a pressure switch problem fit a jumper wire between is two wire terminals, but do it AFTER the inducer fan has been running for 2 to 7 seconds.. not before, and not much later. If the burner fires we know its a pressure switch problem..

We can do without a multi meter for that test, to go further though you will need one.

.

We can go from there without a time limit, In depth with as much detail as needed , after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it. Over half of my customers forget to rate my work. That is something like yourself getting a 60% pay cut. Its not sustainable. I hope you understand.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,806
9,806 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,806 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a goodman furnace (gas). Pilot is out. How to light it?
have a goodman furnace (gas). Pilot is out. How to light it? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Furnace blinking red code and light is steady. I have 2
Furnace blinking red code and green light is steady … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My furnace is throwing out cold air. Settings are fine
My furnace is throwing out cold air. Settings are fine. I physically cleaned the filter but did not replace it. I do not know if my unit has a pilot light.… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
MY Trane XE80 gas furnace blower continues to run after reaching
MY Trane XE80 gas furnace blower continues to run after reaching thermostat temp and the gas shuts off then it's blowing cold air unless I raise the temp on thermostat… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane xb80 furnace throwing 'open high limit device ' code.
Trane xb80 furnace throwing 'open high limit device ' code. Need assistance due to cold weather this evening!… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hi, I have a Honeywell Tru-steam humidifier. It is wired
Hi, I have a Honeywell Tru-steam humidifier. It is wired to come on only when there is a heat signal. This required putting a pressure switch in the plenum. I am a retired HVAC engineer with 30 years … read more
Expert
Expert
I have a XL90 Trane furnace (2004). Burner won't light. ID
I have a XL90 Trane furnace (2004). Burner won't light. ID fan comes on, there is a fast blinking light. You can hear the gas valve click. Eventually the ID fan stops and the whole process starts over… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I have a ruud silhouette ii model ugph-12earjr led blinking
Hi, I have a ruud silhouette ii model ugph-12earjr led blinking 5 times. Won't fire up. Any suggestions?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Gibson, GL1RA, forced air furnace. It is about 7
I have a Gibson, GL1RA, forced air furnace. It is about 7 to 8 years old. For the last year, I had intermittent problem when it would not light up. When I turned off the power fully and turned on, it … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York TG9S100C16MP11A. It worked fine this morning
I have a York TG9S100C16MP11A. It worked fine this morning now it is 5 deg below the set value and will not come on. What it is doing is cycling some fan on (not the main blower) for about 1 to 2 minu… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a White-Rodgers 50a50-298 controller, gas heat furnace.
I have a White-Rodgers 50a50-298 controller, gas heat furnace. The unit is continuously blowing cold air. Upon start up, once every 60 seconds, I see flame for 30 seconds. This occurs 3 times, and on … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my goodman furnace seems to be blowing cold air temp set at
my goodman furnace seems to be blowing cold air temp set at 72 reading 67, furnace is running. through lower sight glass can see a red light blinking three times, then off and then repeats? Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Armstrong Air Ultra V Enhanced 80, approx 6 years
I have a Armstrong Air Ultra V Enhanced 80, approx 6 years old, and the Blower is running but it just stopped producing heat. The blower keeps running. Before I call a service repair what can I check … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have A Ruud Sil. II furnace that will cyle on normally; however,
I have A Ruud Sil. II furnace that will cyle on normally; however, when it is time for it to ignite, it does not. After that the fan will turn on normally but it is blowing only cold air.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My Lennox system will purge but not fire.. Problem has been
My Lennox system will purge but not fire.. Problem has been worked 6 times but is still occurring. Service Company is Ace Heating and Air Cond. in Fairfax VA. Model number is XXXXX 61MPZ36C090.. I'm c… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a coleman evcon G9T10014UPC13C model and ser. # is
I have a coleman evcon G9T10014UPC13C model and ser. # XXXXX XXXXX . It will not start tonight. I cannot fine my owner manual to trouble shot the system. When I try to restart the system after turning… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a lennox model G24M4 gas heater. Does it have a pilot
I have a lennox model G24M4 gas heater. Does it have a pilot light or is it electric ignite?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
my gas furnace just stopped working so the temp is 63, brrr.
my gas furnace just stopped working so the temp is 63, brrr. I have changed the batteries in the thermostat as it said I needed to replace them. Everything is back in place and furnace will not turn o… read more
Bill
Bill
High School or GED
318 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x