Replaced capacitor on my ac unit now it runs for about 30min…

Customer Question
Replaced capacitor on my...

Replaced capacitor on my ac unit now it runs for about 30min and stops. After a about 30 more min it starts back on its own. Repeating that sequence...

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

The filters in the inside is fine

Contractor's Assistant: Do you plan on doing the work yourself?

Maybe...if I could narrow down the problem

Contractor's Assistant: Anything else we should know to help you best?

No...thats about it. I changed the capicor because the fan was not running and humming. after that the fan came on but soon began the cycle I stated above

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
9/28/2017
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to Just Answer. My name is ***** ***** I'll be happy to assist you today. Does the indoor unit continue to run when the outdoor unit shuts off?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
its an all outdoor 3 tun package i can hear another fan running and a little air coming thru the vents so I can here it running but the fan is turning on initially and turning off in about 30 min and repeating that but I can hear the unit on and hear it shuting down when I control the thermostat
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, so it sounds like the indoor blower is running. Was the capacitor you replaced for the outdoor fan? Was it a dual capacitor that runs the compressor as well? If you would like you can take photos and post them to this chat.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Okay, thank you. Do you hear the compressor running when the fan shuts off? Or do you know if the contactor loses 24v and opens contacts to shut both fan and compressor off? Sorry for so many questions - I'm just trying to get a good idea of whats happening there so I know where to look.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I dont know if the contactor loses 24v but I dont hear the compressor when the fan stops
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Could you do me a favor and check the contactor next time the fan shuts off and see if it's pulled in or if it opened? If it stays pulled in when the fan shuts off then we likely have something going on on with the motor/compressor on the high voltage side of things. If it loses 24v and opens up then we have something on the low voltage side of things (could be a freeze stat, low pressure switch, etc). Is the compressor definitely running and system cooling when the fan is running? Could you also let me know the make and full model # of the unit?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
The model is a TRANE ycc036f1m0bd... older unit and I'll get back with you on the contactor. How long do i have to respond
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

This question will stay open for 30 days, so no hurry lol. I'll look up that unit and see if there's anything I notice from the wiring diagram.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Any luck checking the contactor?

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Just checking in again. Let me know if you still need assistance.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Intertherm unit is heating but the fan is not blowing.
my Intertherm unit is heating but the fan is not blowing. Can feel the heat above the A coil. Fan runs fine in "on" position. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
AC was blowing fine earlier saturday. Woke up about 30 min
AC was blowing fine earlier saturday. Woke up about 30 min ago with my wife telling me the house is getting hotter. I check both the upstairs and downstairs and the temps show 83 and 81 respectively. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I had been in contact over the weekend. I replaced the
I had been in contact over the weekend. I replaced the capacitor and it began working. The issue now is that the air is not blowing very cold. I had someone over and they said it was the coils at issu… read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
Unit not working XL14i. We just replaced the fuses in the
Unit not working XL14i. We just replaced the fuses in the outside unit on the wall.It started to hum but stopped. Fan in garage is running, no AC … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
L have a Heil Model N2H318AKA100 outdoor A/C unit. Was
l have a Heil Model N2H318AKA100 outdoor A/C unit. Was working fine then stopped. The compressor buzzes for a few seconds and repeats every 30 seconds or so. Also the fan does not start on its own. Co… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I hand a Lennox 10 acc 060-230-02 AC unit and the fan was
I hand a Lennox 10 acc 060-230-02 AC unit and the fan was not turning. I replaced the capacitor and it started up but stops after around 30 minutes. Is my motor/condenser bad or could I have not prope… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a Coleman EB15B electric furnace in a 2000 model mobile
I have a Coleman EB15B electric furnace in a 2000 model mobile home. Fan began to kick off before set temp was reached and coils still heating!! Blower fan relay was making a humming buzzing noise at … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 7 year old Bryant model 310AAV. The blower motor is
I have a 7 year old Bryant model 310AAV. The blower motor is part number HC41TE113 with a 10 micro farad capacitor. I have a bryant air purifier with the HEPA filter that I change annually. The blower… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Bryant NG Model 330AAV. I run the fan continuously
I have a Bryant NG Model 330AAV. I run the fan continuously for circulation. It stopped working. The LED light is on...no flashes. I bought and replaced the motor and it does not come on. Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox 10acc-024-230-04Eveything has power, inside unit
Lennox 10acc-024-230-04 Eveything has power, inside unit running fine. When outside unit tries to kick on it just buzzes, fan doesn't spin.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman CLJ 30-1 ac unit. Inside, it is still blowing
I have a Goodman CLJ 30-1 ac unit. Inside, it is still blowing non-cool air, but the fan on the outside unit has stopped working. The fan motor is very hot. It is making a small humming sound. The bla… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My ac/heat unit began making a high pitched squeel at random
My ac/heat unit began making a high pitched squeel at random a few weeks ago that seems louder near the duct return register. Then the last 2 days the outside unit comes on for about 1 min turns off a… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The blower motor on my 40 year old GE furnace is not working.
The blower motor on my 40 year old GE furnace is not working. When I turn on the switch I get a humming noise, and no indication that the motor is trying to run. The squirrel cage fan seems to turn fr… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
after 39 min ac stops blowing cold conderser motor stops and
after 39 min ac stops blowing cold conderser motor stops and gets very hot ac blowing hot air leave off for an hour and it might work for a few minutes and then repeat malfuction have changed blower m… read more
Regan Land
Regan Land
HVAC Technician
768 satisfied customers
Sir, I have a Westinghouse ft3bc AC unit at my house. Its
Sir, I have a Westinghouse ft3bc AC unit at my house. It's not running and is making a low pitch humming sound every 1-2 mins. I had a problem similar to this in my last house (different AC unit brand… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
I have a lennox ac 3 ton central air and heat. model no. 80uhg3-60a-1.
I have a lennox ac 3 ton central air and heat. model no. 80uhg3-60a-1. during ac operation the fan will stop pematurely and the try to restart within seconds. it will click on the circuit board then m… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Trane EX1000 unit. I am in San Antonio, TX and its
I have a Trane EX1000 unit. I am in San Antonio, TX and it's really hot. Recently, the condensor fan motor has started shutting down. The fan motor has been replaced and it still does the same thing. … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, Outside compresser unit comes on when ac is turned on but
Hi, Outside compresser unit comes on when ac is turned on but the fan stops turning after about 10 min. and fan motor still running and gets hot. Is this bad fan motor. Thanks Mike… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x