I have a Carrier Infinity. How can I determine if the low…

Customer Question
I have a Carrier...

I have a Carrier Infinity. How can I determine if the low stage is working on the unit. When newer, often the fan would be at a very low rate of speed, and I don't think it is anymore, which I understand is the low stage of the compressor. Cooling fine, but at "full speed".

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Filters are always clean -- I change ahead of schedule normally. How can I check this at the thermostat?

Contractor's Assistant: Do you plan on doing the work yourself?

I need to determine if I have an issue. I have had a tech look at, and he indicated fresh capacitors are in order -- the unit now has all new fresh heart start and run capacitors, and I still don;t think the low stage is operating. If I can fix myself, I will.

Contractor's Assistant: Anything else we should know to help you best?

I don't think so.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 28 minutes by:
9/27/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,819
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, you need a clamp around amp meter, $50 at a big box electrical dept, or $28 at Harbor freight.

Then I can coach you on how to measure the systems amperage draw in both high and low speeds, we will then set the thermostat for cooling and down to 65F with the house at 75F that will put it into high speed, then measure the amperage draw of the blower, and the outside unit.

Then repeat with the cooling set to 73 or 74F and measure the amp draw at low speeds, that will tell us if the system is actually going into low speed mode effectively or not.

.

Regarding your mention of fan at high speed when outdoor unit is in low speed, that happens when the humidity is lower than the humidistat setting, and dehumidification is not required... when the humidity goes above the set point the system will put the blower in to a lower speed, this causes the cooling coil to run cooler, and draw more moisture from the air,

click here for pictures

.

We can go from there without a time limit, In depth with as much detail as needed , after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,819
9,819 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,819 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My ac unit has a two speed compressor but wil not go into
my ac unit has a two speed compressor but wil not go into high speed and stay … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
My infinity system is showing malfunction code 81 low
My infinity system is showing malfunction code 81 low thermal lockout. System is still heating. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I just had a new Infinity Carrier System installed, 19VS
I just had a new Infinity Carrier System installed, 19VS outdoor unit and the 59MN7 furnace. The WiFi Touch thermostat. DUMBED DOWN QUESTION....How do I manually make the fan run, without overriding m… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I'm considering buying a Carrier Infinity Coastal 3-ton heat
I'm considering buying a Carrier Infinity Coastal 3-ton heat pump, 2-stage condenser with variable speed air handling unit. Is it worth the money to get the Thermidistat control or is the standard Car… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
With the Carrier Infinity SYSTXXCITN01-A control, does this
With the Carrier Infinity SYSTXXCITN01-A control, does this control avoid the need to set the dip switches in the unit. In particular for continuous fan operation. It appears that some features can be… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
The high stage contacter on my Carrier HNA25A HEAT PUMP stays
The high stage contacter on my Carrier HNA25A HEAT PUMP stays open during startup after being off for more than 12 HRS. WHAT IS THE PROBLEM?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I have a 6-year-old Carrier system (2 stage heat/2 stage
Hi, I have a 6-year-old Carrier system (2 stage heat/2 stage cool) with an Infinity Control thermostat (older model, not the newer touch display). I would like to replace the thermostat with a Lyric o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am deciding between Carrier Infinity 98 and Lennox SLP28.
I am deciding between Carrier Infinity 98 and Lennox SLP28. The Carrier Distributor said go with the Performance 24ACCC in that it would not break down. He said the Infinity is highly technical and co… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Carrier 38TDB condenser fan seems to be running at high
My Carrier 38TDB condenser fan seems to be running at high speed while the compressor is running on low speed. It seems that it used to run much slower and consequently much quieter.… read more
lordofbtus
lordofbtus
pres
Vocational, Technical or Trade Scho
1 satisfied customers
Actually I have been working on Infinity model#25HNA660A300
Actually I have been working on Infinity model#25HNA660A300 and Have already changed compressor, capacitor, board. I did this because technical consultant for Carrier had told me to do this according … read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
Need to make a quick decision to get the tax rebate. I have
Need to make a quick decision to get the tax rebate. I have been quoted prices for the Carrier Comfort 25HCC560 (5 ton, variable speed AH with single speed compressor), Carrier Comfort 25HCB660 (5 ton… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Our contractor just installed a Carrier 5-ton Performance Series
Our contractor just installed a Carrier 5-ton Performance Series 24APA7 and a Boost 80 58PHX110-20 furnance. I thought I was getting an Infinity 80 58CVX110120 furnace with a variable speed motor. The… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a 4 ton unit. Dual stage a/c cooling compressor (carrier
I have a 4 ton unit. Dual stage a/c cooling compressor (carrier infinity 38TDB) with an (FE4AN) fan coil and an infinity electronic thermostat (systxcc). I look at the program this evening and at low … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,819 satisfied customers
Hi, I have a Carrier 38TDA 2 speed 4 ton condensor. It
Hi, I have a Carrier 38TDA 2 speed 4 ton condensor. It works fine in the first stage, but it has a problem where it starts the compressor in the second stage and runs for a short time. Then the compre… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Today I had an error code of 71 followed shortly by a code
Today I had an error code of 71 followed shortly by a code of 81. The system is a Carrier Infinity two stage heat pump about four yaers old. Any ideas??? Model 25HNA636A… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
there is a error code -72 thermal cutout in high stage on the
there is a error code -72 thermal cutout in high stage on the infinity thermostat. The Outdoor compressor comes on for a few minutes but the air never gets cool. Also error code 71- thermal cutout on … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a 4 year old 5 ton Carrier Infinity HP and have had
I have a 4 year old 5 ton Carrier Infinity HP and have had minor issues since day one. In April 2009 board had to be replaced. November 19th 2009 I had a System Malfunction notice on control panel. Te… read more
John
John
High School or GED
27 satisfied customers
I have an Infinity 96 Model 58MVB with an SYSTXCCUID01--B
I have an Infinity™ 96 Model 58MVB with an SYSTXCCUID01--B Infinity Control, The instructions don't explain how to wire it to a Ruud UARL-JEZ Series AC to the thermostat.… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x