New r410 condensing unit and new evaporator coil. gauges go…

Customer Question
New r410 condensing unit...

New r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

All things new except line set

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I dont think so

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
9/26/2017
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,908
Experience: Furnace, A/C and heat pump specialist.
Verified

Are bot service valves open and what is model on unit?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
service valves are open, dont have model number with me but its a goodmen
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Do you have blue on large valve and red on small? And does it do same in cool or heat mode if it is a heat pump?Are you an ac tech?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i am a tech and have installed several of these units. just havent run into this before. my first thought was blockage but everything is new but line set and i can blow nitrogen through it
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Thanks for this info. I work with experienced techs as well as folks who have no idea what a multi meter is,That is why I asked.Is this a single phase unit and are we working with single phase power supply?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
all single phase.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sounds like either a doa compressor or electrical issue.Are you in COOL mode and is it a heat pump or ac?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
cool mode and it is a heat pump. also i changed condenser and evaporator coil twice just in case and doing the same thing both times
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Same issue with two different condensing units?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Wow that is a weird one. If we had a restriction, high side would retard but suction would be at or near vaccuun

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Have you verified proper voltage on each phase of power?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
everything reads correct
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

I know it sounds next to impossible to be two compressors in a row, but if voltage is right, not much else I could think of.Like I say if it were a restriction both would not retard

Ask Your Own HVAC Question
Customer reply replied 4 months ago
im sorry i should have been more clear. Only the low side is going to retard. i am only showing around 150 on the high side on a 410 unit and also the last 8 compressors i got 5 were bad out of the box so not so crazy
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

If low side is retarding and you can blow through tubing with nitrogen , almost has the be an issue with the compressor.The reason I asked about single phase it it sounded to me like compressor was running backwards which can happen easily with a 3 phase unit

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i am license electrician so i know about the phasing. just wondering if the compressor could be bypassing but i dont hear the usual hissing sound
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Did you try heat mode just to see if it behaved differently?If not I would do that and verify not a bad reversing valve

Ask Your Own HVAC Question
Customer reply replied 4 months ago
that would suck. I did not try heat but i will. still 2 different units that would be weird to
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

I agree.No doubt whatever the issue is that something strange is going on.When can you go back ?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
tomorrow morning
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Let's try heat mode and see if we get a difference

Ask Your Own HVAC Question
Customer reply replied 4 months ago
i will try that and double check everything and see what i get.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sounds like a plan.We will go from there

Ask Your Own HVAC Question
Customer reply replied 4 months ago
thanks
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Thanks for letting work with you

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Buderus Wall Hung Modulating-Condensing Gas Boiler.
I have a Buderus Wall Hung Modulating-Condensing Gas Boiler. Two weeks ago an error message 6A appeared. The flame would not ignite and therefore we had no hot water. … read more
Bill
Bill
Service Mgr
15 satisfied customers
How much does an evaporator coil cost for Ruud Model
how much does an evaporator coil cost for Ruud Model UBHA-17J11SFGA cost? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
What do I need to do to replace condenser fan on my Kenmore
what do I need to do to replace condenser fan on my Kenmore refriger. … read more
Don T.
Don T.
President
Associate Degree
179 satisfied customers
I need to replace a condenser fan on a sub zero 736TC. 10
I need to replace a condenser fan on a sub zero 736TC … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Condenser contractor chattering is it bad? Just notice
We had very cold weather down to 10 degrees, fan not been running until today thouzght was running's. On heat strips. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a GSZ130421AE condensing unit and ARUF486016CA air
I have a GSZ130421AE condensing unit and ARUF486016CA air handler. The heat pump intermittently comes on and may operate a few minutes. When it stops operating, the air handler continues to run until … read more
airheatman
airheatman
HVAC Technician
8,908 satisfied customers
I'm installing a condensation pump for a friend, he has dual
I'm installing a condensation pump for a friend, he has dual zones and the condensation pump has a after switch. The thermostat has ABCD connections. I need the common and normally open connections an… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Does it make sense that the outside condenser unit for the
Does it make sense that the outside condenser unit for the second story of our split HVAC system is 3.5 ton but the evaporator unit in the attic is 4 ton?… read more
airheatman
airheatman
HVAC Technician
8,908 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need an evaporator motor for a mini split unit. Sn
I need an evaporator motor for a mini split unit. Sn 50120031-7056 What is the best way to get this? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
427 satisfied customers
Can I have a condensing furnace in a garage that's only
Can I have a condensing furnace in a garage that's only heated a couple days out of the week? I can install it inside the conditioned space but do I have to keep the garage heated all the time or can … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Gladiator Freezerator and the evaporator fan won
I have a Gladiator Freezerator and the evaporator fan won sorry won't turn off could it be the control board … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator
Hvac I am using a Goodman gsx 16 seer 2.5 ton the evaporator has 3/4 suction and the condenser has a 7/8 I'm going about 20 foot which size do I use for the copper tube… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
46 satisfied customers
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am installing an Evaporator Control Limit switch on the
I am installing an Evaporator Control Limit switch on the outside heat exchanger for the upstairs central heat & air unit in my house. I know that it is just supposed to splice into the low voltage co… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I am looking for a evaporator coil assy model number
I am looking for a evaporator coil assy model number G/HC030SA FOR CENTRAL ENVIRONMENTAL SYSTEMS … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
airheatman
airheatman
HVAC Technician
8,908 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x