HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

New r410 condensing unit and new evaporator coil. gauges go…

Customer Question
New r410 condensing unit...

New r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

All things new except line set

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I dont think so

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
9/26/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,030
Experience: Furnace, A/C and heat pump specialist.
Verified

Are bot service valves open and what is model on unit?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
service valves are open, dont have model number with me but its a goodmen
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Do you have blue on large valve and red on small? And does it do same in cool or heat mode if it is a heat pump?Are you an ac tech?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
i am a tech and have installed several of these units. just havent run into this before. my first thought was blockage but everything is new but line set and i can blow nitrogen through it
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Thanks for this info. I work with experienced techs as well as folks who have no idea what a multi meter is,That is why I asked.Is this a single phase unit and are we working with single phase power supply?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
all single phase.
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Sounds like either a doa compressor or electrical issue.Are you in COOL mode and is it a heat pump or ac?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
cool mode and it is a heat pump. also i changed condenser and evaporator coil twice just in case and doing the same thing both times
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Same issue with two different condensing units?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Wow that is a weird one. If we had a restriction, high side would retard but suction would be at or near vaccuun

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Have you verified proper voltage on each phase of power?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
everything reads correct
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

I know it sounds next to impossible to be two compressors in a row, but if voltage is right, not much else I could think of.Like I say if it were a restriction both would not retard

Ask Your Own HVAC Question
Customer reply replied 8 months ago
im sorry i should have been more clear. Only the low side is going to retard. i am only showing around 150 on the high side on a 410 unit and also the last 8 compressors i got 5 were bad out of the box so not so crazy
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

If low side is retarding and you can blow through tubing with nitrogen , almost has the be an issue with the compressor.The reason I asked about single phase it it sounded to me like compressor was running backwards which can happen easily with a 3 phase unit

Ask Your Own HVAC Question
Customer reply replied 8 months ago
i am license electrician so i know about the phasing. just wondering if the compressor could be bypassing but i dont hear the usual hissing sound
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Did you try heat mode just to see if it behaved differently?If not I would do that and verify not a bad reversing valve

Ask Your Own HVAC Question
Customer reply replied 8 months ago
that would suck. I did not try heat but i will. still 2 different units that would be weird to
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

I agree.No doubt whatever the issue is that something strange is going on.When can you go back ?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
tomorrow morning
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Let's try heat mode and see if we get a difference

Ask Your Own HVAC Question
Customer reply replied 8 months ago
i will try that and double check everything and see what i get.
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Sounds like a plan.We will go from there

Ask Your Own HVAC Question
Customer reply replied 8 months ago
thanks
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Thanks for letting work with you

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trane XR90 is leaking water out of the bottom of the unit.
Trane XR90 is leaking water out of the bottom of the unit. I pulled off the condenser trap on the right side, cleaned and tested - works fine. There are two pvc drains going to it - one from the upper… read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
I have a Trane XE 1100 heat pump that is 15 years old and used
I have a Trane XE 1100 heat pump that is 15 years old and used year round. It just started tripping the breaker in the breaker box as soon as it turns on. The technician says the compressor has a dead… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
What is the cost of a Goodman evaporator coil replacement?
What is the cost of a Goodman evaporator, for the part and for the part installed with the usual amount of freon (R22) in a two-section (upstairs) Trane XL 1500? The unit is leaking badly and the tech… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
My upstairs HVAC has the evaporator located in the attic.
My upstairs HVAC has the evaporator located in the attic. There are two drain lines running inside the wall to ground, one on the evaporator and one on the drip pan under the evaporator, the drip pan … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
61 satisfied customers
What would make evaporator fan motor stop and the unit to
what would make evaporator fan motor stop and the unit to freeze up … read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need the BTU rating for a Heatcraft Evaporator Model
I need the BTU rating for a Heatcraft Evaporator Model ADT56AWGJ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Today, evaporator coil froze over and i heard the outside
Today, evaporator coil froze over and i heard the outside condensor area making a louder noise. i shut the ac off when noticing this and the coil melted and the fan blows air now. i looked at the evap… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,808 satisfied customers
I replaced a jazz bored today along with evaporator fan
I replaced a jazz bored today along with evaporator fan motor and I can only get the motor running if I use the ground wire to one terminal on the motor and one of the wires that has 120 V I replaced … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
Why is my suction line freezing up?
Why is my suction line freezing up?… read more
R.G.
R.G.
318 satisfied customers
my cooling fins need to be replaced......is this possible
my cooling fins need to be replaced......is this possible???… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Is it possible to charge a heat pump system while in heat
Is it possible to charge a heat pump system while in heat mode?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I want to install a new 3 ton 16 seer AC condenser. The lineset
I want to install a new 3 ton 16 seer AC condenser. The lineset install already is 3/8" OD liquid and 7/8" OD suction. The run is 90 feet from the unit and there needs to be 6 90 degree elbows to make… read more
airheatman
airheatman
HVAC Technician
9,030 satisfied customers
Hello Phil i have an ice machine . It leaks water at the bottom
Hello Phil i have an ice machine . It leaks water at the bottom From center to back . Can you help me?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.