I have a bryant...

I have a bryant heater that will turn on for 5 minutes then shut down with a 31 code

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just today its the first cold day here

Contractor's Assistant: Do you plan on doing the work yourself?

If i can

Contractor's Assistant: Anything else we should know to help you best?

Not that i can think of

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
9/24/2017
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,614
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. This is a venting or vent sensor problem. Is your vent pipe metal or PVC?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I'm not sure which pipe is the vent, but looks like it's all pvc
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,804
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I need the full model number of the furnace, its on a tag inside the same compartment as the gas valve...just follow the 3/4" gas pipe to find that compartment.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
912SC36040S17A-A
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, click here for the manual that Bryant provides, they do not however include an internal furnace wiring diagram, what I usually do is mark those up with step by step trouble shooting instructions.

Take a close up, exceedingly well focused photo of the wiring diagram that is glued inside your blower access door and attach it here using the 'add files' link next to your send button.

I will mark it up with trouble shooting instructions. Meantime tell me if if the inducer blower is running or not,

Click here please

We can go from there

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, click here please, unplug the furnace, wait 2 minutes, plug it back in with the thermostat set to heat and up to 90F... then **after*** the inducer fan starts fit a jumper wire across the HPS switch 2 to 7 seconds after the inducer fan starts... if the rest of the furnace now operates properly, remove the jumper immediately. We will service the pressure switch and do a a few tests in that case.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

click here please, if the igniter module does not glow brightly 30 to 60 seconds after you have jumpered the HPS, then unplug the igniter module and measure the voltage between the two female sockets that power the igniter (red circle). If you get 120 volts, replace the ignitor module.

Let me know how much of this is within your skill set range so that I can tune my test procedures to you skill level. We can go from there without a time limit

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,804
9,804 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,804 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 2 stage with an evolution thermostat. Very cold
I have a Bryant 2 stage with an evolution thermostat. Very cold right now here in Chicago. I kep getting a system malfunction message to call techinician. The furnace shuts down but the fan is still o… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
Del 315AAV/JAV and the first cold day but heat is not coming
del 315AAV/JAV and the first cold day but heat is not coming on. the heat light on the unit is flashing. wondering if there is an easy fix? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
I have a furnace with no heat. The blower motor comes on
I have a Bryant furnace with no heat. The blower motor comes on before the inducer motor which is backwards from the way it is designed… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
I have just bought a second hand Rinnai 15. I'm told its
Hi I have just bought a second hand Rinnai 15. I'm told its a year old. But it only runs for 20 minutes before shutting down. Is there some setting that I've done wrong?… read more
canuck the pro
canuck the pro
281 satisfied customers
I have a Bryant Model 340AAV furnace that the limit switch
I have a Bryant Model 340AAV furnace that the limit switch tripped. After tripping several times over the course of this month I decided to pull the cover off the fire box and clean the surface of the… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello, I am having trouble with my furnace. It is a Payne
Hello, I am having trouble with my furnace. It is a Payne Model PGMAA. It's a forced hot air, but is blowing cold air. It is flashing error code 33, then after 5 minutes changes to 31. I have tried to… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I was just reading your prior conversation on the bryant
Hi, I was just reading your prior conversation on the bryant 350aav. I had a similar problem, code 31.. cleaned out the condensation trap and was working well for a few weeks. Today, got code 31 again… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my 10 yr old bryant furnace wouldnt kick on last night so
my 10 yr old bryant furnace wouldn't kick on last night so i turned on the fan and then it was blowing only cold. I checked it and at the time, it was blinking 31. I reset the air filter and then turn… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Carrier 58pav090-14 with trouble code 31. All of a sudden
I have Carrier 58pav090-14 with trouble code 31. All of a sudden it stopped working without any noise. I tried resetting it by turning off all the switches for one day. I changed the filter which was … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant GT-PX geothermal unit, it starts off blowing
I have a Bryant GT-PX geothermal unit, it starts off blowing cold then after a couple hours the air turns luke warm. If I shut down the unit then restart it, it will do the same(blow cold then turn wa… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Bryant gas furnace has stopped working in 15 degF temp.
My Bryant gas furnace has stopped working in 15 degF temp. Power is on, gas is working, filters are new, LED diagnostic light is blinking. Any suggestions to get it working again? Thanks.… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a Bryant plus 80 with an error code of 3 short blinks
I have a Bryant plus 80 with an error code of 3 short blinks and 1 long blink (31?) Blower comes on and does not ignite, blower runs about 10 minutes and then shuts off. What could be thee issue?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hello I have a Bryant gas heater, and woke up this morning
Hello I have a Bryant gas heater, and woke up this morning to it not blowing out heat. I shut it down for 5 mins, restarted it, and it's still not working. I checked the status code, and it's blinking… read more
Rick
Rick
HVAC Supervisor
24,614 satisfied customers
My Payne furnace wont ignite after being off for a week. I
My Payne furnace won't ignite after being off for a week. I get error 31 on the red blinking light. Any help appreciated. Optional Information: Make : Payne Model : Gas Already Tried: - turned down th… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Bryant heater model ck5exad60024aaa does not fire up. turned
Bryant heater model ck5exad60024aaa does not fire up. turned the unit back on because of latest cold but nothing. a week ago was working fine!… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
i have a bryant furnace... it is blowing cool air only... my
i have a bryant furnace... it is blowing cool air only... my temp in house is at 60 now and set at 73... I turned of electricity, gas and waited. Turned electricity back on then gas and it started up … read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a carrier furnace (5 years old) that gives an error
I have a carrier furnace (5 years old) that gives an error code 31. The High Heat/Low heat pressure relay was replaced and the problem continues... The issue is that it does not sustain High Heat... w… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Bryant CAV395024070 furnace thats taking a code 31.
I have a Bryant CAV395024070 furnace thats taking a code 31. When I run a component test, the inducer motor comes on, sometimes for only a second, sometimes for the proper amount of time, sometimes no… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.