I have an older Honeywell round thermostat (+/- 25 years…

Customer Question
I have an older...

I have an older Honeywell round thermostat (+/- 25 years old) that will only go on if I set the dial at least 5 to 8 degrees higher than the room temperature. If I set it at 70 F. before going to bed in the evening and the temperature of the room drops down to 64 -66F during the night, it does not go on. Could it be a problem with the thermostat or the valve that controls the radiant heat pump ?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Re settings, I can only control he temp I want the heat to go on. There are no filters in my radiant hear system.

Contractor's Assistant: Do you plan on doing the work yourself?

If it is simple , yes. However I had a plumber replace the valve to the radiant heat pump last Fall and it worked OK for the rest of the cool winter.....until this Fall .

Contractor's Assistant: Anything else we should know to help you best?

No, except that the valve in question opens up as I said initially only when I (testing it only) set it at least 4-6 degrees higher than room temp. So, do you think it could be a thermostat problem or ???

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
9/24/2017
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 10 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy. Can you tell me if you only have 2 wires hooked up in thermostat?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
After removing the cover of the thermostat I see a semicircular metal thin bar with grooves along it (below the dial ) and a metal pointer overlying it, pointing to a few line grooves from the beginning. So what is it and what does it control ? If you have a picture of this older round model you will see what I am trying to describe.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 10 months ago

That is what is called a heat anticipator. It used the low voltage to help warm the thermostat to anticpate when boiler should shut off.

Did you see what wires are attached and how many?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Ruud Furnance/Heat Pump system. Heat Pump is
I have a Ruud Furnance/Heat Pump system. Heat Pump is UPLA-031JAZ. Air Handler is UBHA-17J11NFAA. Original thermostat is Rheem part number 41-20804-15. The thermostat will consistently read 5-10 degre… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'd love to ask a question. I ave a ct87k in a heat only
I'd love to ask a question. I ave a ct87k in a heat only application. the system is a gas fired forced hot water system that is not one of the new high efficiency systems. What Cycle rate setting shou… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Weil McClain Series 2 gas fired water Boiler. How
I have a Weil McClain Series 2 gas fired water Boiler. How hig can I raise the water temp without doing damage. I'm set at 140. I think I can raise to 160. Would that be safe?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I recently moved to a house built in 1995 that has radiant
I recently moved to a house built in 1995 that has radiant in floor heating supplied by a Munchkin 140M boiler. Initially I noted the controls were not properly set up in accordance with the manual, s… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Trane xl624 in hold mode...set point 72....room temp 70.....takes
Trane xl624 in hold mode...set point 72....room temp 70.....takes forever to turn on furnace???… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,154 satisfied customers
I recently moved into a house that has radiant floor heating
I recently moved into a house that has radiant floor heating with a Burnham Revolution series gas boiler and a Honeywell T8775 thermostat. Everything was working well until we turned down the thermost… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
yesterday morning about 6 am, the heat pump fan was running
yesterday morning about 6 am, the heat pump fan was running blowing cool air and the indoor temp was 68 degrees and the thermostat was set at 71 and the outdoor temp was about 36 degrees. We cut the p… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,154 satisfied customers
My home has a Carrier air source heat pump (38YXA) as well
My home has a Carrier air source heat pump (38YXA) as well as high-mass (in slab) radiant fed by an electric boiler. Both system are on off-peak rates. My home is located in northern Minnesota. My que… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi there, I am in the process of buying a home that was built
Hi there, I am in the process of buying a home that was built in 2010. The house has radiant heat with a pretty big boiler. The problem that I have is that, in order for the hot water to come out, I h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My ptac unit must have a thermostat problem the fan will
My ptac unit must have a thermostat problem the fan will work but the ac will not cool. Last summer the desired temperature had to be set progressively lower to get the unit to cool now this year it w… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Amana PTAC air conditioner Model No PTH123E35AXXXAB has
My Amana PTAC air conditioner Model No PTH123E35AXXXAB has the following thermostat problems: in winter, in HEAT mode with the thermostat set at 58, the unit seldom cycles with room temperature in the… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
Have a Trane XL1200, DCY060F, when themostat calls for heat,
Have a Trane XL1200, DCY060F, when themostat calls for heat, heat pump kicks on runs a minute or two and then switches to aux heat, the heat pump kicks off and the gas furnace kicks on, outside temp i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
how do i set a honeywell sparcomix am series valve for a home
how do i set a honeywell sparcomix am series valve for a home 45000 btu radiant heat application currently i adjusted to setting number 6… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Now replacing Honeywell Chronotherm III digital thermostat
Now replacing Honeywell Chronotherm III digital thermostat from York ac/heat pump with the recommended Honeywell Touchscreen Vision Pro 8000 TH8320U1008. Old wiring attached to posts Red=R, Blue=C, Or… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a beach house that require heat now in October, breaker
I have a beach house that require heat now in October, breaker turned on to activate heat, Honeywell dial thermostat for base board heat in den, third one to replace, non-digital thermostat, dial 50-8… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox Elite Model CB29M Blower Coil, Heatpump Lennox
I have a Lennox Elite Model CB29M Blower Coil, Heatpump Lennox model HP29, TStat Lennox 21J7201. We noticed when we cut over to heat this fall that the blower began running almost non-stop, even thoug… read more
Bill
Bill
High School or GED
318 satisfied customers
I am a condo renter in which a new AC/heat unit was recently
I am a condo renter in which a new AC/heat unit was recently installed-to replace the prior 36-year old unit. I have had 2 days experience now with the new unit in which I set the digital thermostat t… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Lennox Elite series thermostat with a heat pump. The
I have a Lennox Elite series thermostat with a heat pump. The heat pump operates until the temp reads below 40 degrees. that is too low, when the outside temp is 40-43 degrees the house won't heat up … read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x