Model # is M7RL Series there is no hot air but the furnance…

Model # is M7RL...

Model # is M7RL Series there is no hot air but the furnance blows cold air the service light are all off except for the green and it flashes

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter is new and the thermostat setting is OK

Contractor's Assistant: Do you plan on doing the work yourself?

Not sure if is a limit switch on the outside then probably, If not the Furnace is less that a year old so I will probably have it fixed under warranty. I don" know who I can callt

Contractor's Assistant: Anything else we should know to help you best?

I don"t think so I do live in ST Charles ID

Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
9/23/2017
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,117
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

So the red and yellow are not lit...just the green continuous blink?

Ask Your Own HVAC Question

I see you mentioned limit switch so you already are on the right track...

Just above the burners on the front wall is the limit we want to check...do you know where this is? Or can you post a pic so I can draw part location for you?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
It looks like there are two a main limit switch above the burners and one above that on the Combustion air pipe.

correct..they are different circuits but could still code the same.

Now..the one on vent pipe..is there a tiny button in center? and the one on front wall is credit card sized?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
There is a bottom on the vent pipe a do not see any thing on the other

press button on vent switch...then tap the other limit above burner 3-4 times....tell me if light pattern changes

Ask Your Own HVAC Question
Customer reply replied 9 months ago
The furnace lite and all light are on. Does this mean I have one of the switch that are bad?

Either bad...or reacted to a problem.

Can you try a heat cycle now?

Ask Your Own HVAC Question

Is the furnace running now?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
It has cycled and it worked.i let do a complete cycle.

Excellent news....this could have been previous due to a dirty filter....obstruction in pipe now gone..anything that caused a bit more heat than normal.

I am glad all is well for you now...I would hold calling for service and only call if it were to trip again.

Just rate service (5 star rating system) to close for now and move off the active list.

Thank you!

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,117
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,117
23,117 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I too have a York Diamond 80. The heat does not come on. The
I too have a York Diamond 80. The heat does not come on. The thermostat seems to be doing its job. The blower comes on but the heat does not. I checked the pressure switch by blowing into the tube and… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I HAVE A TEMPSTAR FURNANCE, MOD# 5100BFC1. THE SYMTOMS ARE:
I HAVE A TEMPSTAR FURNANCE, MOD# ***** THE SYMTOMS ARE: COMES ON BLOWERS HOT AIR, THAN SHUTS OFF, FAN STAYS ON, CONTINUES BLOWING COLD AIR … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace seems to be stopping intermittently. The red
My furnace seems to be stopping intermittently. The red light is solid but green flashes … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,117 satisfied customers
My power went out and know my furnace is just blowing cold
My power went out and know my furnace is just blowing cold airon the inside it also has one red light blinking one flash which I believe means limit circuit open or external load on W?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
During operation the unit turns off. Diagnostic description
During operation the unit turns off. Diagnostic description refers to the Open Limit Switch Fault; Green LED - Flash, Red LED- Off.… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,117 satisfied customers
Hello, I have furnace model TG9S080B12MP11A. When i program
Hello, I have furnace model TG9S080B12MP11A. When i program my thermostat to drop the house temperature when i leave my house and raise it 1hr before i get home, the furnace blows hot air then cold ai… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Freedom 90 furnance and it cycles out and blows cold
I have a Freedom 90 furnance and it cycles out and blows cold air. This is the second winter we have lived in the house. If I push in the reset button the furnance will start back up and run anywhere … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a white-rodgers universal 50A55-843 with diagnostic
I have a white-rodgers universal 50A55-843 with diagnostic indicator flash code 4 open high temp limit switch flashing....the furnace only blows cold air.. I bypassed the limit switch and the burners … read more
V12Tech
V12Tech
252 satisfied customers
I have a Payne furnace model CU5830-C175. The blower is working,
I have a Payne furnace model CU5830-C175. The blower is working, but is blowing cold air. The LED indicator was flashing code ‘13'. I pulled the filter, and now have a solid indicator light. Should I … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
23,117 satisfied customers
I have a bryant 340aav furnance. We had heating service provider
I have a bryant 340aav furnance. We had heating service provider two weeks because no heat (no problems before that). Air filter needed to be be changed and also changed out power switch. This morning… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a programable thermostat XT300 and I have overridden
i have a programable thermostat XT300 and I have overridden all programs, set temp to 72 and it will only get to 67 and then blows out cool air after it reaches that temp. Currently says heat on- set … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My furnance keeps running but is blowing cold air. It is reading
My furnance keeps running but is blowing cold air. It is reading that the limit swithch is open. Once I turn off the furnance it lights and runs for awhile with hot air flashing one XXXXX XXXXXght the… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a lennox merit series furnace that will run and heat
I have a lennox merit series furnace that will run and heat my house well but when it shuts off it will stay off for a long time before kicking back on. It will let the temperature get well below the … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Lightning strike at our house, now an XC15 A/C unit gives error
Lightning strike at our house, now an XC15 A/C unit gives "error code 90" on a Honeywell iAQ thermostat (and isn't running). What can I do to troubleshoot and try to get this unit running again.… read more
Charles
Charles
State Licensed HVAC Contractor
Associate Degree
68 satisfied customers
Hi! I have a 9420 model thermostat. I live in Mt. Dora FL and
Hi! I have a 9420 model thermostat. I live in Mt. Dora FL and we are experiencing weather in the 30's (Daytime). My heat has run continuously for 3 days except that it blows cold air and then warm. I … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a trane xe 80 furnance that is giving me a 4 flash trouble
I have a trane xe 80 furnance that is giving me a 4 flash trouble code. Which indicates an open high limit switch. The filters were a couple months overdue for changing, so i put in two new ones. Any … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a nordyine furnace(manufactured home) and it is running
I have a nordyine furnace(manufactured home) and it is running in what seems to be short cycles.T-stat is set on 78 and house temp is only 71.The furnace will run for 7-8 mins then shut off come back … read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
We have a 2 year old frigidaire furnace. We have no heat blowing
We have a 2 year old frigidaire furnace. We have no heat blowing from vents. The furnace just keeps running with no heat. Please help Thanks… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question