I have a boiler fired hot water heater, with Honeywell

I have a boiler...

I have a boiler fired hot water heater, with Honeywell V8043F1051 zone controls. The zone control for the hot water heater seems to be the problem. There is no resistance when I move the manual lever; but when I remove the entire unit, there is resistance, and I can see the female socket pivoting, not a big arc by the way. Put it all back together and ....no hot water.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

How do I check the thermostat? and where is it?? The zones for heat respond, boiler starts, room gets warm, its just the hot water side...

Contractor's Assistant: Do you plan on doing the work yourself?

If possible

Contractor's Assistant: Anything else we should know to help you best?

Don't think so

Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
9/23/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, is there 24 voltAC power to the valve in question, does it open and close when you apply 24vac power to it?

Use the 'add files' link next to your send button to attach a few photo's of the zone control panel with its cover off so I can see the wiring and a photo of the valve in question, We can go from there

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Sorry, can't really do the picture routine right now. However, on the top of the TACO box all three lights (red/yellow/green) are lit for the right zone....
Customer reply replied 9 months ago
You can call(###) ###-####
Customer reply replied 9 months ago
Never mind...the motor is shot. I ordered a replacement.

Good work!

Its time to select the 'finish and rate your expert link' near the top of your page and click on it. That is the only way the company pays me for my time, in exchange I will hold the question open to you for any follow up needed,

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,703
9,703 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,703 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Buderus GA124 boiler that supplies hot water for my
I have a Buderus GA124 boiler that supplies hot water for my radiant heating system and my hot water tank. The boiler will only start when causing one of the radiant heat thermostats to close. It won'… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an enerjet boiler and recently the relay on the
I have an enerjet boiler and recently the relay on the Honeywell L8148E relay stuck and I had a run away boiler would not shut down. I tapped the relay and it disengaged and shut the boiler down. I in… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am a general contractor and have 2 things I need answered.
I am a general contractor and have 2 things I need answered. First, I have a Teledyne Laars 85,000 btu mini therm II boiler that is supplying 5 radiant floor zones. I believe that this boiler was inst… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Living Room zone is set to 68 degrees, but room is at 75
Living Room zone is set to 68 degrees, but room is at 75 degrees and is not going down even when we lower it. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Buderus hot water heater/storage tank model #SM300/1,
I have a Buderus hot water heater/storage tank model #SM300/1, I have no hot water. Is there a re-set button? The radiant heat still works but no hot water to the rest of the house. What could be wron… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have Hunter 44260 thermostats in a house with hot water
I have Hunter 44260 thermostats in a house with hot water heat running 3 zones. I have this thermostat in all locations. The problem is the thermostat will engage the boiler at the low set point but w… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My house has 4 zones controlled by Aube thermostats. 1 of
My house has 4 zones controlled by Aube thermostats. 1 of the thermostats (TH147P)controls the master bedroom. Periodically, the room temperature on the thermostat will rise 10 to 15 degrees about the… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have two programmable Honeywell thermostats that have been
I have two programmable Honeywell thermostats that have been working without problems for 11 years. This am I hit hold temp and raised arrow to 71 degrees to warm up bedroom while I took shower tempor… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Taco ZVC406 zone valve control system, in conjunction
I have a Taco ZVC406 zone valve control system, in conjunction with a hot water/gas fired boiler system. The problem is with zone 2 (which goes to the main upstairs master bedroom,master bath, and off… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lochinvar Knight model WHN085. It is set up for 2
I have a Lochinvar Knight model WHN085. It is set up for 2 zones. Even with both thermostats set to 50 degrees F, the temp in the house is nearly 80. It appears that the boiler is not cycling off.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
have natural gas fired boiler for baseboard heat. I have 2
have natural gas fired boiler for baseboard heat. I have 2 zones still getting hot water flow, even after shutting off the thermostats. The boiler cycles on/off every 5-6 minutes, even with thermostat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hello. I have a lochinvar solution boiler which is about 1
Hello. I have a lochinvar solution boiler which is about 1 year old. It has worked great up until last night. I have three heating zones hooked up with different thermostats. Starting last night, two … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am replacing a Burnham LR1620 thermostat with a Honeywell
I am replacing a Burnham LR1620 thermostat with a Honeywell RTH2300B1012 model. Are they compatible?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have just replaced my old Honeywell round thermostats with
I have just replaced my old Honeywell round thermostats with the new T8775A round digital thermostats. I have Taco zone valves and have installed the resistors as instructed. The thermostats seem to b… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
How do I trouble shoot a Honeywell V8043F1051 zone valve.
How do I trouble shoot a Honeywell V8043F1051 zone valve. The thermostate is in the off position, yet the boiler is still sending heat to only that zone? Thanks, Todd… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
can you please tell me why my central heating comes on when
can you please tell me why my central heating comes on when my hot water comes on even though the heating is switched off?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
It is now the warm season and we have our furnace turned down
It is now the warm season and we have our furnace turned down but it still runs. The registers are hot and the house gets warm. We turn the emergency switch on off when we are not needing hot water. W… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why am I getting heat only downstairs but not upstairs?
I have a 2 zone (upstairs & downstairs) hot water base board heating system. The boiler is working and I am getting heat downstairs but no heat upstairs?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x