I have a Thermo Pride OL5-85 oil fired furnace with Riello F3 burner controlled by a 2 wire thermostat. Is there a switch or connection(s) I can make to turn the fan on for a short time, without the burner?

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

No problem, just want to turn the furnace fan on (only)

Contractor's Assistant: Do you plan on doing the work yourself?

Only to throw a switch or connect a few wires together (with power off)

Contractor's Assistant: Anything else we should know to help you best?

Only that I want to use the fan and air filter to filter air as I use a shop vac to blow air down the air intake register

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
9/22/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,621
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can

continue our conversation.

Do you have a G terminal on the furnace thermostat terminal strip?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
No, old Honeywell manual round thermostat with black and white terminals / wires only

At the furnace not the thermostat

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Thanks for the opportunity to call but let's continue chatting

call prompt is automatic. I have no control over it. We can continue here. You need to check where the thermostat leads connect to the furnace not the thermostat

Ask Your Own HVAC Question
Customer reply replied 11 months ago
The 2 wires from the thermostat connect to 2 wires (only) from the burner

The thermostat wires go directly to the burner control? If so I need a clearly focused picture wiring diagram of your unt. It's usually pasted to the back of the blower compartment panel.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

Ask Your Own HVAC Question

Ok, you need a new thermostat that has a G terminal (virtually all new ones do) then run a lead from G on the thermostat to G on the fan center relay. Refer to wiring diagram. When you want to run the fan only you switch the fan switch on the new thermostat from AUTO to ON

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Ok Rick, I can access all wiring from the thermostat to the furnace so it shouldn't be too difficult. I think that"s all I need for now. Thank you for your help. Damon.

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,621
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now

Thanks for using Just Answer

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,621
24,621 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an oil furnace... after running out of oil, then oil
I have an oil furnace... after running out of oil, then oil delivery today, I need to restart it. I have a Riello 40 burner. I've hit reset twice... sounds like it fires up but still blowing cold air.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Goodman GMh 9 50 703BXac Won't fire up. LED readout is
Goodman GMh 9 50 703BXacWon't fire up. LED readout is pressure switch stuck open three flashes I took the tubes off the pressure switch Bloom out tap the pressure switches what do I do next… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My blower is working but only cool air is coming out. Help!
My blower is working but cool air is coming out. Double checked the thermostat's settings and checked the filters too. Even cranked up the thermostat. The unit is only 3 years old.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Dunkirk oil fired boiler model3E.75 92,000 btu with
I have a Dunkirk oil fired boiler model3E.75 92,000 btu with Riello 40 F3 type 261T gun firing rate 0.5-0.95 GPH. My question is, can I convert the boiler to fire on natural gas by changing the gun?… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
Last night we awoke to our heater running and running.
Last night we awoke to our heater running and running. Noticed the screen on our Honeywell focus pro 6000 was blank. Changed the batteries and it remained blank. Shut off the furnace, and today will p… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
Hi. I have a Bryant 383KAV. I noticed its only blowing out
Hi. I have a Bryant 383KAV. I noticed its only blowing out cold air. I replaced the filter just a couple weeks ago. Vents are clean, no blockage and the limit switch has an auto reset. When I power cy… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just replaced the exhaust blower on my gas furnace (bearings
I just replaced the exhaust blower on my gas furnace (bearings shot). Now it is running, but after it turns on, the pilot won't light. If I take the cover off of the burn chambr and allow air in, the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi- I am trying to start my furnace for the winter Bryant
Hi- I am trying to start my furnace for the winter Bryant upflow model #398AAV and the furnace blower wont come on. It seems like the inducer motor is working and the thermostat says heater on, but th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am going to install a new furnace in my home. My old one
I am going to install a new furnace in my home. My old one is 15 years old. It is a Ford 180,00 btu.Oil with continuos fan running all the time. House is approximately 3000 sq feet with 5 ton air cond… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Thermo Pride furnace. When the thermostate calls for
I have a Thermo Pride furnace. When the thermostate calls for heat, only the exhaust fan goes on. Once in a while the furnace works okay. Woke up to 55 degrees in house. when I press the Roll out swit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Thermo pride oil furnace -- no heat, but fan is on. red button
Thermo pride oil furnace -- no heat, but fan is on (when I put to "on", not when I put to "auto"). red button pushed to reset burner. comes on for 10sec and then shuts off. The fan works -- but no hea… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I am installing a outdoor wood stove and in the process of
I am installing a outdoor wood stove and in the process of wiring a 2nd thermostat to run the blower on the current oil furnice - it is a Thermo pride oil fired furnace OL11-105. The thermostat that i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My thermo pride oil furnace reset button is flashing and it
My thermo pride oil furnace reset button is flashing and it wont reset. What can I do. There is plent of oil. It was working this morning and I have reset it before with no problem.… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
Hi; Got a Thermo Pride oil fired OL5-85 RDA low boy hot air
Hi; Got a Thermo Pride oil fired OL5-85 RDA low boy hot air furnace with direct drive multispeed fan motor and hooked up for AC, came home from work Fri. and found blower motor running on high spd. an… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Herrmidifier # 447 connected to a Thermo Pride oil
I have a Herrmidifier # XXXXX connected to a Thermo Pride oil hot air system. The #447 was installed on the cold air inlet- correct installation should be on warm air outlet?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have a thermo pride furnace with a beckett by honneywell
i have a thermo pride furnace with a beckett by honneywell r7184b its stuck in lockout mode and the oil pump wont turn on it ran out of oil i did put 50 gal in the tank before trying to restart the fu… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I have a rental apt with a Thermo Pride oil fired furnace...It
I have a rental apt with a Thermo Pride oil fired furnace...It is so loud, I have to block the vents in the bedroom just to be able to sleep...It sounds like there are 2 different blowers, one as loud… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Furnace fires in the morning, heats everything up, blower comes
Furnace fires in the morning, heats everything up, blower comes on later but won't light. Worked with two different Techs, changed smart valve, changed pressure switch and circuit board. Filter is cle… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x