I have a Thermo Pride OL5-85 oil fired furnace with Riello F3 burner controlled by a 2 wire thermostat. Is there a switch or connection(s) I can make to turn the fan on for a short time, without the burner?
JA: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?
Customer: No problem, just want to turn the furnace fan on (only)
JA: Do you plan on doing the work yourself?
Customer: Only to throw a switch or connect a few wires together (with power off)
JA: Anything else we should know to help you best?
Customer: Only that I want to use the fan and air filter to filter air as I use a shop vac to blow air down the air intake register
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
9/22/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,310
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can

continue our conversation.

Do you have a G terminal on the furnace thermostat terminal strip?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
No, old Honeywell manual round thermostat with black and white terminals / wires only

At the furnace not the thermostat

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Thanks for the opportunity to call but let's continue chatting

call prompt is automatic. I have no control over it. We can continue here. You need to check where the thermostat leads connect to the furnace not the thermostat

Ask Your Own HVAC Question
Customer reply replied 1 month ago
The 2 wires from the thermostat connect to 2 wires (only) from the burner

The thermostat wires go directly to the burner control? If so I need a clearly focused picture wiring diagram of your unt. It's usually pasted to the back of the blower compartment panel.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

Ask Your Own HVAC Question

Ok, you need a new thermostat that has a G terminal (virtually all new ones do) then run a lead from G on the thermostat to G on the fan center relay. Refer to wiring diagram. When you want to run the fan only you switch the fan switch on the new thermostat from AUTO to ON

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Ok Rick, I can access all wiring from the thermostat to the furnace so it shouldn't be too difficult. I think that"s all I need for now. Thank you for your help. Damon.

You're welcome

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,310
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now

Thanks for using Just Answer

Ask Your Own HVAC Question
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,310
22,310 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,730 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I bought a home in april of 2017 and today I noticed the
I bought a home in april of 2017 and today I noticed the temp was at 66 deg.s, with down to the basement and my Tempstar (1996 yr I believe) wouldn't come on (gas/pilot light?0. I noticed it had a "sp… read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
My honeywell thermostat dose not have a rh inlet only an r.
my honeywell thermostat dose not have a rh inlet only an r … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
Got a rheem criterion 2 furnace that ignites and runs for 30
got a rheem criterion 2 furnace that ignites and runs for 30 secs then flames out and cycles… read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
I have a carrier comfort 92 furnace. The fan comes on but
I have a carrier comfort 92 furnace. The fan comes on but the heat will not come on. The thermostat needed to be replaced a few months ago and we have not had to use the A.C. or heat much since the th… read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
I have a Thermo Pride OL5-85 oil fired furnace with Riello
I have a Thermo Pride OL5-85 oil fired furnace with Riello F3 burner controlled by a 2 wire thermostat. Is there a switch or connection(s) I can make to turn the fan on for a short time, without the b… read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
I have a gmpn080-4 and it has been starting randomly but the
i have a gmpn080-4 and it has been starting randomly but the thermostat is not calling for heat. … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
My old thermostat had a jumper between rc and rh. My new
my old thermostat had a jumper between rc and rh. My new honeywell has only R RC and C. ??? … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
I have an older round manual thermostate with a red and blue
I have an older round manual thermostate with a red green white and blue wire. Will this be compatable with a nest thermostat? … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
My lawn guy cut my AC cables, but I reconnected them and the
Hello. My lawn guy cut my AC cables, but I reconnected them and the thermostat still will not turn on. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I need help. 2 days. Im certified in hvac, im just stuck
Hi i need help JA: I'll do all I can to help. How long have you been dealing with this? Customer: 2 days JA: Do you plan on doing the work yourself? Customer: Yes im certified in hvac, im just stuck r… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
198 satisfied customers
We have a Rheem unit and are trying to convert our
Hello we have a Rheem unit and are trying to convert our thermostat to a wifi only issue seems to be the common wire not there where would you add one … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
Furnace does not keep going until up to temperature - is
Furnace does not keep going until up to temperature - is this the thermostat of the furnace? Thermostat keeps reverting to 1:00 Mon which I assume is the set up code. Thermostat is the Focuspro wifi T… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a honeywell thermometer in our house. Is there a
We have a honeywell thermometer in our house. Is there a battery in them that needs to be changed? … read more
Rick
Rick
HVAC Supervisor
22,310 satisfied customers
Our add on cooling unit is to coming on. Fan is working but
Our add on cooling unit is to coming on. Fan is working but no cooling. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Need battery for - Rodgers 1970s furnace thermostat. Battery
Need battery for White - Rodgers 1970s furnace thermostat. Battery Replacement W.R Part no.(###) ###-#### 44-4868. Have tried Specialty Battery stores to no avail.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Forced air NG furnace...thermostat replaced (yesterday) and
Forced air NG furnace...thermostat replaced (yesterday) and now blower fan comes on BEFORE furnace burner ignites??? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
No power to flame rollout switch on gas furnace. Thermostat
no power to flame rollout switch on Bryant gas furnace … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am looking for Water Furnace Thermostat Model #TA32E12. I
I am looking for Water Furnace Thermostat Model #TA32E12. I need 2 of them to replace the ones I have because the read out display does not display. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,730 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x