Customer Question
My Coleman 80% updraft...

My Coleman 80% updraft gas furnace is showing a red steady indicator light on the control board, (control failure). It has thermostat low voltage, and 110 volt current to furnace. Is it the control board itself?

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

Yes to thermostat, HSI tested for continuity.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

No rollout switches were tripped, cleaned flame sensor, high limit ok, door switch ok, induction blower motor free, as is fan blower motor.

Submitted: 12 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
9/22/2017
HVAC Technician: Regan Land, HVAC Technician replied 12 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to Just Answer. My name is ***** ***** I'll be happy to assist you today. Unfortunately the solid red light means bad control board. I can look up a replacement if you could get them the full model # of the furnace.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a G61MPV-36B-071-10 furnace, Code 1-2 is on. I have
I have a G61MPV-36B-071-10 furnace, Code 1-2 is on. I have replaced the igniter and the flame sensor. The igniter never glows and no gas enters burner. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Having a problem with my unit not blowing hot air. All
Having a problem with my unit not blowing hot air JA: Did you double-check the thermostat's settings? And what about the filters? Customer: all checked JA: Do you plan on doing the work yourself? Cust… read more
Regan Land
Regan Land
HVAC Technician
Vocational, Technical or Trade Scho
768 satisfied customers
Nordyne model #g6rco80c12b continuse red light -false flame
nordyne model #g6rco80c12b continuse red light -false flame or gas valve relay shorted code . main blower comes on no power to gas blower does not start the cycle to turn on the ignition … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rick, I have a 140k btu 80% efficient ICP/Arcoaire/Comfortmaker
Hi Rick, I have a 140k btu 80% efficient ICP/Arcoaire/Comfortmaker furnace with 50A50-110 White Rodgers integrated control module. Towards the end of the cycle the unit shuts down, pauses for a moment… read more
Rick Warner
Rick Warner
Zone Manager
Tech 1
12 satisfied customers
regan. I have a problem with my xr90 trane furnace. I am
Hi regan. I have a problem with my xr90 trane furnace. I am getting the four flash open limit device code. The filter is new. The furnace will kick on and fire for about 20 seconds but then shuts off.… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Inducer motor runs, HSI glows for several seconds, then no
Inducer motor runs, HSI glows for several seconds, then no gas (gas valve doesn't open). Pressure and switch checkout, roll out switches check out for continuity. Already replaced the control board. I… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
I have a Rheem 80 furnace in a rental unit. Renter called
I have a Rheem 80 furnace in a rental unit. Renter called today because furnace fan was only blowing cold air. When I arrived, I cycled the furnace at which point the induction motor and main blower m… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Gibson KG6RC080C-16B furnace that is not heating... It
I have a Gibson KG6RC080C-16B furnace that is not heating... It uses Nordyne 624631-a control board and a 904081 gas valve. I am getting a constant flash from the red led on the control board. After r… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I got an Armstrong G1N80AU natural gas furnace and got a 4
I got an Armstrong G1N80AU natural gas furnace and got a 4 flashes failure code which as per the O&M manual indicates an open limit switch or limit switch circuit fault. I checked the rollout switch, … read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a Carrier 8000TS. It is not staying on to warm house
I have a Carrier 8000TS. It is not staying on to warm house up. I did some research, cleaned the sensor, and the error code changed from 14 to 33. I read what it said to do, but cant find the flame ro… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a williamson 2 stage gas furnace.It starts its cycle...induction
I have a williamson 2 stage gas furnace.It starts it's cycle...induction motor...igniter glows...gas ignites but when fan comes on, moter and gas shut off. Fan runs about 20 seconds then the cycle sta… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
i need a detailed step by step sequence of operation of 80+
i need a detailed step by step sequence of operation of 80+ and 90+ furnace i need voltages pre-purge and post purge details i really need step by step details also i need a trouble shooting ladder di… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I saw you helped someone with a similiar problem. I have a
I saw you helped someone with a similiar problem. I have a Bryant furnace that is indicating a code 33 error. The inducer is not spinning and the iginitor is not getting hot when I ran the test (jumpe… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My Coleman Evcon comes on for about 3-5 minutes and then goes
My Coleman Evcon comes on for about 3-5 minutes and then goes right back off, can trip thermostat and comes back on and does same, am freezing… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Diagnostic flash code for Coleman Evcon Furnace model #BGM12520B
I need the Diagnostic flash code for Coleman Evcon Furnace model #BGM12520B Optional Information: Make : Coleman Evcon Model : BGM12520B Already Tried: Need diagnostic Flash Code… read more
Bill
Bill
High School or GED
318 satisfied customers
hello, i have a rheem 80 plus imperial furnace which appears
hello, i have a rheem 80 plus imperial furnace which appears to operate normally for a couple of days at a time then just recently it started to have issues with the automatic ignition system... i rem… read more
Robert
Robert
Associate Degree
161 satisfied customers
I have a Gibson furnace. On start-up this heating season it
I have a Gibson furnace. On start-up this heating season it blows out cold air right from being turned on, and then the fan won't go off - I have to cut the power to get it to stop. The furnace is abo… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an Air Ease Ultra SX 80 furnace that is 12 years old.
I have an Air Ease Ultra SX 80 furnace that is 12 years old. The T-stat calls for heat, the HSI(hot start igniter) gets yellow hot, the pilot light starts burning, the FS(flame sensor) gets red hot, a… read more
Ronald
Ronald
Consultant
Bachelor's Degree
4 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less