The air handler for our hp will not come on, sometimes. When…

Customer Question
The air handler for...

The air handler for our hp will not come on, sometimes. When it doesn't, I can pull out the breaker and replace it and then it will start. What is wrong?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes! HP comes on but fan does not.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

Can't think of anything.

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 53 minutes by:
9/22/2017
HVAC Technician: airheatman, HVAC Technician replied 11 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,379
Experience: Furnace, A/C and heat pump specialist.
Verified

Could be a relay sticking.Does the outdoor always come on when you call for cool?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 11 months ago

OK if outdoor stays running, we still have power to air handler as outdoor would not be getting signal if no power to air handler.It may be that when flipping breaker, you are touching a wire or vibrating something or perhaps resetting control board.

What is model on air handler ? Do you have a meter for troubleshooting?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
FK4CNF005000AEAA, have a multimeter
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Is it acting up at present?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

The FK4CNF005000AEAA has what is called an ECM motor. An ICM2 is fed high voltage AC power through the 5-pin connector. The AC power is then rectified to DC by a diode module. After rectification, DC signal is electronically communicated and fed in sequential order to 3 stator windings. The frequency of these commutation pulses determines motor speed. The rotor is permanently magnetized. An ICM2 is powered with high voltage at all times. The motor will not run with high voltage alone. Low voltage must be applied to control plug to run motor.

Your issue can be either the bell controller or the board which signals bell controller.

The issue is most likley a bad bell controller.

These motors have a 10 year warranty so if less than 10 yeas old will be to your advantage to call dealer rather than go much further and risk voiding warranty.

Below are links to the procedures for testing windings and phase as well as a link to the required tester

I am happy to guide you if this is something you want to do yourself and can acquire the tester.Just let me know how you want to proceed.

https://www.gamut.com/p/motor-diagnostic-tool-ecm-motor-diagnostic-tool-for-ecm-motors-MzQ0MjY3?gclid=CjwKEAjw4IjKBRDr6p752cCUm3kSJAC-eqRtpV1jqI08Bg4ru9VOCuXDVQxYqlwQK7tBjC5MuqMmihoC1yvw_wcB&gclsrc=aw.ds&dclid=CLiYmJLAwdQCFQ5mwQodY6UN7A

Ask Your Own HVAC Question
Customer reply replied 10 months ago
It is doing it more often, now. The unit is 20 yrs old. Hate to spend a lot of money on it, but don't want to install new one, either. Haven't worked on HVAC much, but dedicated DIYer.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

You would be better off to replace the air handler than pay for parts for this thing if it is 20 years old.THat FK4C was a high end air handler 20 years ago. Blower and module run about 600 bucks, just module on motor about 500 and control board around 450 all wholesale so expect to pay a contractor doubl;e those prices.

Without being able to test with the ecm tester, you can throw a lot of money at this thing.

I don't mind telling people to guess and take a chance on which part it is when we are talking 12 dollar relays but hate telling ou to try board without knowing.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Aren't there any cheap relays on this one?
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Unfortunately this one uses a high tech control nodule rather than the standard relays.All relyas are built into a solid state board

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Is it possible to bypass the control module?
Customer reply replied 10 months ago
Can I bypass the control module?
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Unfortunately not as the motor does not get just a standard 24 volt signal like it would from a relay.The board sends signals in various volts of ac or dc to determine speed

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,379
9,379 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Thank you. My ac blower doesn't stop this is been going on
my ac blower doesn't stop this is been going on for a week … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a RHLLHM2417JA F/C and a RPNL024JAZ H/P. The F/C
I have a RHLLHM2417JA F/C and a RPNL024JAZ H/P. The F/C blower is turning off and on (short cycling) whether the thermostat is calling or not. When I turn up stat the H/P won't even start/run. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
If I lift the top of my home thermostat the #starts with
If I lift the top of my home thermostat the #starts with 960. It has H/C on top left, fan on left. Up/down arrows on right. The bottom 4 buttons from left to right are Prog. - TimeTemp- Day- HoldEnd. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem 41-20804-15 thermostat, I bought a Honeywell
I have a Rheem 41-20804-15 thermostat, I bought a Honeywell RTH2300 to replace it. Match what was being used and set the programming but I am not getting anything. Rheem B-BLUE R-RED G-GREEN Y-YELLOW … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Goodman Heat Pump - three years old. cools but does not heat.
Goodman Heat Pump - three years old. cools but does not heat. Condenser fan does not come on at 60 degrees outside air temp and unit blows no warm air.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Goodman CPKJ36-1AB split system heat pump. Every 2
I have a Goodman CPKJ36-1AB split system heat pump. Every 2 to 3 weeks, my air handler will not come on. The condenser unit will come on and run. If I go to my panel box, shut off my breaker and turn … read more
airheatman
airheatman
HVAC Technician
6 years college
9,379 satisfied customers
Our Braeburn 3200 will not kick on and - heat - just flashes
Our Braeburn 3200 will not kick on and "heat" just flashes and can't get off "aux". We've tried everything in the manual....nothing works. Please help. Will be cold tonight and support center is close… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My ac went out yesterday in 108 degree weather. My ac guy
My ac went out yesterday in 108 degree weather. My ac guy is here and having a tough time figuring it out. Is there a reset switch?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Our air handler is not coming on-line with the compressor.
Our air handler is not coming on-line with the compressor. It started yesterday evening. The thermostat kicks on the compressor but the internal air handler was not running at all. After trying to pow… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an 80k propane fired furnace, which has a DC variable
I have an 80k propane fired furnace, which has a DC variable speed air handler motor, recently replaced. several days ago we ran out of propane. I don't know if this had an effect on our problem. When… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My carrier cac system stopped working and the repair guy cant
My carrier cac system stopped working and the repair guy can't come for a week! The thermostat works and is trying, but the fan and units inside and out aren't on. No breaker is tripped and I can't fi… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
On my home heat / ac air handler unit, the fan doesnt come
On my home heat / ac air handler unit, the fan doesn't come on. I hear clicking, almost a solenoid noise, and the gas burner comes on, but not the fan part of the system. Any idea of the problem / sol… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I had a contractor doing some work at my house while I was
I had a contractor doing some work at my house while I was at work the other day. He worked on my new electric stove outlet. Since then, my furnace will not come on - of course, he knows nothing about… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Rheem heat pump (2 mo. old) with a Honeywell t-stat
I have a Rheem heat pump (2 mo. old) with a Honeywell t-stat (brand new)... the air handler fan will not shut off, even when the t-stat says the system is off. Any thoughts as to how to fix the proble… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a GOODMAN Air Handler Model # AR 36-1 I didnt get
I have a GOODMAN Air Handler Model # XXXXX 36-1 I didn't get the Heat Pump model #..I'm at work now..The problem I'm having is the Heat Pump will not come on (GOODMAN also) in the Heat Mode..But It wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My rheem air handler fan will not shut off even when I adjust
My rheem air handler fan will not shut off even when I adjust the thermostat setting to 'off' for both fan and unit. I disconnected entire thermostat and also replaced with a new thermost but the prob… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I replaced my weathertron thermostat with a programable Ritetemp
I replaced my weathertron thermostat with a programable Ritetemp model 6030. I have a Trane XE 800 heat pump. The fan came on initially but the heat & cool would not. I corrected the wiring with the t… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
breaker flipped insider air handler. Reset breaker, outside
breaker flipped insider air handler. Reset breaker, outside heat pump and fan will not start. happened one year ago. then when I flipped breaker unit started… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.