40qca060791-103 indoor 38dxa165913 outdoor blowing 2 amp…

Customer Question
40qca060791-103 indoor 38dxa165913 outdoor...

40qca060791-103 indoor 38dxa165913 outdoor blowing 2 amp fuses indoor board

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Look just went to service unit and clean drain and look at the indoor board and thats it turn unit on and had a qiuck fault code could be e2 not sure and then all the power of the thermostat when off cheeck indoor and found 10 amp fuse blown and cicuit braker trip replace fuse and reset fuse and turn on and it run indoor fan ok after checking found that inddor fan is running with the unit turn off

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Not sure it very strange i did nothing to it thinking that the indoor board is faulty i replace board and then turn on and when the power is on now blow a 2amp fuse on the indoor board thing that the trasformer is faulty as well replace it as well and now still blowing a 2amp fuse so confused now

Contractor's Assistant: Do you plan on doing the work yourself?

Im hoping to do

Contractor's Assistant: Anything else we should know to help you best?

Not sure what else i can tell you be greatfull if you can help

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
9/22/2017
HVAC Technician: airheatman, HVAC Technician replied 11 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
Experience: Furnace, A/C and heat pump specialist.
Verified

Finding a short can be difficult. Easiest way to find is by process of elimination.If you can get several fuses, we can try different things until we no longer blow fuse to locate the short.

1.Disconnect all thermostat and outdoor unit control wires from the terminals on indoor unit control board.Turn power on to furnace and see if fuse blows.If it blows, the control board in unit is shorted and will need to be replaced.If not move to step 2.

2.Next I want you to connect those wires back one wire at a time turning power off and on to furnace after each one to see when fuse blows. Reconnect in this order

R G W Y and then C If you have C.(door switch has to be held in each time in order to have power to furnace.)

3. Go to outdoor unit. Disconnect the 2 control wires going to Y and C where they first enter the unit. Turn thermostat to call for ac. If fuse still blows we have a short in those wires between indoor and outdoor units.Could be chewed or skinned, possibly nicked by weed eater, etc. allowing wires to touch and create short.If it does not blow,we know short is inside of the outdoor unit.Move to next step.

4. Reconnect those 2 wires .Then locate the contactor relay in outdoor unit. Remove the small control wires on the contactor coil.Turn on AC.If fuse does not blow, the contactor coil is shorted and contactor will need to be replaced.If fuse still blows we know short is between where wires enter unit and the contactor.Move to next step.

5.Reconnect the contactor wires.Follow the control wires from where they enter unit and see what component may be in that circuit .(Pressure switches, time delay, defrost control board, etc).Follow same procedure of disconnecting wires to each of those controls and see if we find one that seems to cause fuse to blow when in circuit.Also look for any place the small control wires may be touch a hot gas copper line in unit that may have melted sheathing on wire and be allowing copper to ground to pipe.

Let me know what you find and we wlll go from here.

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Ok txs for your response
Customer reply replied 11 months ago
Can you cal me
HVAC Technician: airheatman, HVAC Technician replied 11 months ago

The website charges an extra fee for live phone calls as the tech is dedicating his time solely to your issue while on phone. Experts may be working on several questions at a time in chat.I am currently unable to accept phone call, but you can request phone call under the additional service and if a tech who can call is available, they will accept call.

Can you start by taking outdoor unit out of the picture by disconnecting control wires to it?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Ok will try that first
HVAC Technician: airheatman, HVAC Technician replied 11 months ago

Let me know

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Hi there buddy this indoor board has the letters R B E Y G L W2 C and wires are connected to this board
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Disconnect the Y and C and see if fuse still blows

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a Trane XR13 Heat Pump at our cafe, with what seems
Hi, We have a Trane XR13 Heat Pump at our cafe, with what seems like no power running to it, nor the thermostat. I first noticed this when it was warmer than usual, and when I went to check the thermo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Klimaire kmir series unit with power to the outdoor
I have a Klimaire kmir series unit with power to the outdoor unit but none of the three indoor units react to the remote or manual button on the indoor unit… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
How do I wire my 5 wire motor to 3 wires, Just started, Yes,
How do I wire my 5 wire motor to 3 wires JA: I'll do all I can to help. How long have you been dealing with this? Customer: Just started JA: Do you plan on doing the work yourself? Customer: Yes JA: A… read more
airheatman
airheatman
HVAC Technician
9,367 satisfied customers
While fitting my new thermostat, my ac went off and never
While fitting my new thermostat, my ac went off and never starting. I troubleshoot and found that my HN51KC024 output was 0 and input 247v, I changed the contactor and getting same results… read more
airheatman
airheatman
HVAC Technician
9,367 satisfied customers
My 3 amp fuse in control board keeps blowing, just today so
just today so i replaced the thermostat and the fuse things were working for about ten minutes then the 3 amp fuse blew again … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
AC does not turn on fan on manual does not turn on either Luxpro
Hi, AC does not turn on fan on manual does not turn on either Luxpro thermostat displays T then OL I replaced the batteries - no joy I reseted it by pressing the middle button with pen - no joy I remo… read more
airheatman
airheatman
HVAC Technician
9,367 satisfied customers
I have an LG S24AHP SPlit system Airconditioner The unit
I have an LG S24AHP SPlit system Airconditioner The unit stopped working There were no lights or anything working on the unit The Control fuse on the Indoor unit control board had blow I replaced the … read more
airheatman
airheatman
HVAC Technician
9,367 satisfied customers
When my ac stopped I went into the attic & in the handler I
When my ac stopped I went into the attic & in the handler I found a blown 3 amp fuse on the Furnace control board, & I replaced it with only fuse I had (a 7 amp fuse), I later found the 24v transforme… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
what activates the indoor fan? The thermostat is working and
what activates the indoor fan? The thermostat is working and the compressor turns on. the indoor fan works if it is energized seperately. I hear a click but fan will not blow.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a 20 year old high efficiency carrier central air unit
i have a 20 year old high efficiency carrier central air unit which was working until today. The indoor fan works fine when switched to cool and auto fan; T inside 80 and setting 70, the outside compr… read more
MagiicAir
MagiicAir
HVAC Service Supervisor
Vocational, Technical or Trade Scho
110 satisfied customers
I have a carrier 40QCA060791--03/38DXA165913 model. It was
I have a carrier 40QCA060791--03/38DXA165913 model. It was working perfectly just 2 days ago and I had to turn it down because it's freezing. Then it stopped working yesterday. I took off the filter &… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Payne PH10JA036-E Heat Pump, PF1MNA Fan Coil, and
I have a Payne PH10JA036-E Heat Pump, PF1MNA Fan Coil, and Bryant TSATBBPHP01-B Programmable Thermostat. Found house cool, no power to thermostat. Found 5 amp fuse on control board in fan coil blown. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi my vizo combi condensing boiler keeps blowing one of the
hi my vizo combi condensing boiler keeps blowing one of the 2amp fuses on the circut board left as you look at it… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Im trying to help a friend of mine with his a/c.He has a mod
I'm trying to help a friend of mine with his a/c.He has a mod twg30a140b a/h with a twr030c100a5 heat pump & a weathertron baystat 240a t-stat.He had a problem with the unit & tried to repair it himse… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My AC just stop working. My White Roger thermostat 1f79 was
My AC just stop working. My White Roger thermostat 1f79 was low on batties. I change the battiers. Now I'm trying to start my Cooling system, but it keep on blowing a 5 amp fuse on the control board? … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
our heat pump (18 months old) stopped working yesterday. The
our heat pump (18 months old) stopped working yesterday. The thermostat (batteries replaced this morning) says "cooling on". Interior temperature is 79, cooling is set to come on at 75. But the heat p… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
my GMH95 has 6 flashes on LED. There are no obstructions. This
my GMH95 has 6 flashes on LED. There are no obstructions. This unit in less than 3 years old and has operated fine till now… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 85sta/stx. Thermostat acted eratically, no known
I have a 85sta/stx. Thermostat acted eratically, no known reason. Heat pump appeared to have a faulty contactor which was replaced. Now the entire board on the furnace is dead. No LED, no power to any… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x