What is a symptom of an Aquastat not sensing water level?

Customer Question
What is a symptom...

What is a symptom of an Aquastat not sensing water level? Could the switch be bad?

Contractor's Assistant: How long has this been going on? And how severe is the problem?

Never had any trouble. Had furnace cleaned and tech said could not get electricity to run the boiler again, because Aquastat was bad. Boiler i=was installed in 2014 and had never had trouble starting before this.

Contractor's Assistant: Do you plan on doing the work yourself?

No.

Contractor's Assistant: Anything else we should know to help you best?

My question is -did the Tech damage something? There have been no problems since the boiler was installed in 2014.

Submitted: 12 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
9/22/2017
HVAC Technician: Rick, HVAC Supervisor replied 12 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,850
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Aquastats sense water temp not water level (with the exception of new aquastat/relays with built in low water sensing). Possible but unlikely to have a bad 3 year old aquastat. Cleaning the boiler shouldn't damage the aquastat but if the tech had to remove it to get the jacket off to clean it then reinserted the aquastat bulb incorrectly that could keep it from firing.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Triangle Tube Excellence that I had installed about
Hello, I have a Triangle Tube Excellence that I had installed about 6 years ago and it has been running pretty good after having to have a few small adjustments made to it right after it was installed… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My name is ***** *****, and I am curious about whether it is
Customer: My name is ***** *****, and I am curious about whether it is reasonable for a novice do-it-yourselfer to attempt to replace the aquastat on a 27 year old utica boiler? Also, with a boiler th… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Good morning. I have a Thermo Dynamics Boiler S-Series Model
Good morning. I have a Thermo Dynamics Boiler S-Series Model S-100. Installed in 1991. The last two days the furnace did not kick in and we had no hot water. 3rd time in about two weeks. The red light… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Burnham P809HNEI-L2 gas boiler, Aqua stat with -limit reset
Burnham P809HNEI-L2 gas boiler, Aqua stat with hi-limit reset keeps tripping even after it ran for a week no problem. Went back changed both aqua stats set temp on boiler to 180 and set hi-limit with … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
My furnace runs and shuts off repeatedly, as in I counted 8
My furnace runs and shuts off repeatedly, as in I counted 8 starts in a minute last night. the house is warm but its going thru fuel like crazy. the oil tank is in the basement so not freezing line. I… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I was trying to install a Honeywell Wifi Thermostat, but there
I was trying to install a Honeywell Wifi Thermostat, but there was no C wire. I looked at the Honeywell Aquastat attached to the gas furnace, and there were two terminals labeled "Thermostat". The 2 w… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a jvs125 125000btu mini therm which services three zone
i have a jvs125 125000btu mini therm which services three zone values. the high limit is 180degrees. when one of the zones calls for heat the furnace hums and or starts to vibrate .never had this prob… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
1993 weil mcclain oil furnace honeywell r4184d ignition oil
1993 weil mcclain oil furnace honeywell r4184d ignition oil primary control with honeywell aquastat r8182d . continued cycling of burner even when boiler is up to temp and not calling for heat or hot … read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Recently the circuit board burnt out. Had a HVAC guy come in
Recently the circuit board burnt out. Had a HVAC guy come in and rig the transformer to give heat. He told me I had to swap the motor, circuit board, etc for $2500. Does that seem accurate?? I could h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My forced hot water system is heated by a utica MGB150HD natural
My forced hot water system is heated by a utica MGB150HD natural gas fired boiler. When it stopped working, I called in a plumber, who tested it and said that the only problem was that the Honeywell L… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My Honeywell Aquastat Relay L8148E is not working. Why?
I have a Honeywell Aquastat Relay L8148E. When I turn the thermostat to call for heat nothing happens. If I lift the Switching Relay (close the circuit), it works. When I let go, the circuit opens and… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I installed L8148E aquastat relay on a gas boiler twice in
I installed L8148E aquastat relay on a gas boiler twice in the last 2 days.It has the 5 pin plug for the electric damper.The damper is also new.When the damper is closed the (circulator pump is runnin… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
L4081 aquastat. Appears that the unit is not switching the
L4081 aquastat. Appears that the unit is not switching the boiler on when low limit reached. Have to hit reset to turn on boiler (WM Oil ) Is there a service action that can be taken? Are there manual… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a RAB140 Reznor waste oil boiler about 8 yrs old. It
I have a RAB140 Reznor waste oil boiler about 8 yrs old. It will go into lockout about every 2-4 days. I push reset and it starts up again with no problems. always goes into lockout when i am not arou… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Tekmar 260 control that controls my boiler which heats
I have a Tekmar 260 control that controls my boiler which heats the house and also supplies hot water through a heating coil and holding tank. Two days ago we awoke to find we had no hot water althoug… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am installing a Heatmor wood fired boiler in my home. The
I am installing a Heatmor wood fired boiler in my home. The heat exchanger will be installed in an older Ruud gas fired hot air furnace, immediately above the A-coil. Is there a simple way to have the… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
I have a Burnham oil-fired boiler, which wasnt running right,
I have a Burnham oil-fired boiler, which wasn't running right, the tech put a tester on all the electrical & said everything was OK & did a seasonal cleaning with filter replacing & when he started it… read more
Rick
Rick
HVAC Supervisor
24,850 satisfied customers
Have a old utica boiler about 38 years old . just had it serviced
Have a old utica boiler about 38 years old . just had it serviced and service man said it needs a aquastat l3148e because it is getting to hot. it is operating 180 to 212 then back down. he said it wa… read more
buck3371
buck3371
Vocational, Technical or Trade Scho
22 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x