I have a Trane XR80 that is an air conditioner and heater…

Customer Question
I have a Trane...

I have a Trane XR80 that is an air conditioner and heater unit. The trouble I am having is the unit will run in air conditioning mode or fan only mode and then shut off. It then will not start. After a day or so it will start again and run. It will run for a while and then shut off before reaching the temperature it was set to reach. It seems like it will run longer on cool days. I am wondering if a thermal overload switch is shutting it off. I can not heat the house, cool the house, or just run the fan. I am guessing a thermal switch is sensing it is getting to hot, shutting itself off, sensing its cooled down, and allowing it to run again until it gets hot again. I hear a bubbling sound when it shuts off. What noise is that? And is it normal?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Two filters located in different rooms are clean. But lots of dust is along the inside of the duct. Either previous owners ran the unit with no filter or dust is entering the unit from an unfiltered source. Thermostat will send a signal to the unit to start but nothing happens.

Contractor's Assistant: Do you plan on doing the work yourself?

I hired a HVAC expert to look at it a year ago but it ran fine d

Contractor's Assistant: Anything else we should know to help you best?

It ran fine while he was here. I have been shutting the unit off and the turning it on when I need to cool that part of the house. This last time the unit ran for 20 minutes and then shut off and wouldn't run again even though I lowered the temperature settings to 65.

Submitted: 12 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
9/22/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 12 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,362
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. Check drain line and see if there is a float switch that may be tripping. It is located in drain line and has two wires attached. Also check to see if the furnace is blinking and error code. The light is located on the furnace board and you will be able to see it thru the small in fan housing bottom of furnace. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XR80 furnace. the error code is flashing 4
I have a Trane XR80 furnace. the error code is flashing 4 times, which the manual says, its a temperature switch is open. my blower fan goes on and blows hot air for about 2 minutes, but then the fan … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
4 blinks from the furnace red light after it runs and then
4 blinks from the furnace red light after it runs and then shuts down the flame ignites but then shuts off after a cycle … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a new central A/C unit that came with the Honeywell
I have a new central A/C unit that came with the Honeywell PRO 4000 digital thermostat. Once the inside temperature reaches the set A/C temperature it will sometimes turn off. Yesterday with these hot… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a 4 ron Nutone ac/heat pump. It is 4 years old.
We have a 4 ron Nutone ac/heat pump. It is 4 years old. Recently we have had a problem with both the heat pump and the air conditioner stopping for no apoarent reason. Our house gets too cold on chill… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,978 satisfied customers
I have a 2009 Luxaire Acclimate Modulating gas furnace...it
I have a 2009 Luxaire Acclimate Modulating gas furnace...it is turning on at correct programmed time, but not to desired temperature. Thermostat has been replaced. It is supposed to come on at 6am and… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a nordyne heat pump that has been cooling without issue
I have a nordyne heat pump that has been cooling without issue all summer. Today is the second time I've had to kick over to heating mode. When I switched it on today it ran a short cycle the exterior… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
This is a follow up to an earlier question about auto changeover
This is a follow up to an earlier question about auto changeover on the Honeywell RTH7600 thermostat. The Wake, Leave and Return cycles for heat is set to 72 and the cool temperature for those cycles … read more
caleb
caleb
63 satisfied customers
It has been really warm outside and my AC seems to be blowing
It has been really warm outside and my AC seems to be blowing not so cool air inside. I checked the condensor unit this morning and saw that the fan was not blowing. Also it appeared there was a great… read more
Appliance Tech Larry
Appliance Tech Larry
Outside inhome service tech
High School or GED
19,156 satisfied customers
Hi Honeywell, A thermostat question. Staying at a friends
Hi Honeywell, A thermostat question. Staying at a friend's place. The temp was set at 70 degrees, but the place was cool. I pushed the Up arrow up a couple of times, then mistakenly turned the system … read more
drcool299
drcool299
shop owner
Bachelor's Degree
22 satisfied customers
We have a Lennox 10HPB36-10P air conditioner that has just
We have a Lennox 10HPB36-10P air conditioner that has just stopped cooling. I went and checked what I could. The contacts are operating properly, the only thing I can tell from just looking, is the st… read more
drcool299
drcool299
shop owner
Bachelor's Degree
22 satisfied customers
why would my compressor shut off before it reaches the thermostat
why would my compressor shut off before it reaches the thermostat temp? my freon levels is full… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a three year old home and having trouble with the furnace
I have a three year old home and having trouble with the furnace operation. The furnace is a Luxaire GY9S UP, besides having two new fan motors installed since taking ownership of the home another pro… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
When Heat pump (HP) in my house starts, the temperature of
When Heat pump (HP) in my house starts, the temperature of the big copper line close to the air handler rises to about 65-70 C (I've attached a thermocouple with a an OMEGA readout unit that displays … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,362 satisfied customers
My Soleus dehumidifier suddenly stopped working - the fan stays
My Soleus dehumidifier suddenly stopped working - the fan stays on, lights are on, but no water in reservoir after a few days (normally had to empty tray 1 - 2x a day. Already cleaned the slightly dir… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 12 year Lennox air conditioning system and heat pup
We have a 12 year Lennox air conditioning system and heat pup which has been working great up until yesterday. The fan stopped and the unit was making a strange humming noise. We shut the system off a… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I came home from a 3-day vacation and my house smelled like
I came home from a 3-day vacation and my house smelled like something had overheated. I think I've traced it to my electric furnace. Turns out the filter should have been replaced long ago :-( I felt … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem RGPH-10EAMER furnace shuts down while the thermostat
My Rheem RGPH-10EAMER furnace shuts down while the thermostat is still calling for heat. It starts again right after it shuts down and finishes heating to the called for temperature. I thought it migh… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have two trane xe 90s in my house. The one in the attic
I have two trane xe 90s in my house. The one in the attic just stopped cooling. The Fan outside the house is running and the thermostat is set to cool but the blower does not start. I looked in the at… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.