I installed a carrier 38MGQF-36-6 mini split system for one of my customers and he had all of the wiring done by an electrician who used solid romex wire, I know that's good for the feed but not between the evaps and the condensing unit. A good deep vacuum was pulled after nitrogen testing the line sets, I powered up the unit and a ^P6 code showed up on the evap sections of the system. I'm believe that the wires from condensing unit and the evaporators is what's keeping it off line.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Remote stats and brand new evap units

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
9/21/2017
HVAC Technician: David Bowden, General Contractor replied 8 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 856
Experience: Owner at Floridaco
Verified

The P6 Error Code Definition: (Unit Size 36K – 42K) = Communication error between the inverter drive and main board. What size Romex wire was used?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
12
HVAC Technician: David Bowden, General Contractor replied 8 months ago

Do you know the amp rating of the units? #12 will support up to 20amps.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
The wire feeding the condenser is #10 romex and the wire feeding the evap sections is #14 3 romex the amp rating of the unit is 27 amp min circuit
HVAC Technician: David Bowden, General Contractor replied 8 months ago
10 handles 30 amp if copper wire and 14 handles 15 amp
Ask Your Own HVAC Question
Customer reply replied 8 months ago
Could the type of wire be the issue, being that it is solid unshielded wire that travels from the condensing unit to the evap sections. The condenser is located near the electric meter and incoming power.
HVAC Technician: David Bowden, General Contractor replied 8 months ago
Wire is wire regardless of how it is encased even romex has wires that are wrapped similar to off the reel
Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 8 months ago
Romex is usually installed inside walls and ceiling not on the surface
Ask Your Own HVAC Question
Was this answer helpful?
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 856
856 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
mini split does not respond to remote, unit will operate by
mini split does not respond to remote, unit will operate by manual switch on inside unit. Tried another remote from similar unit, no results.… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
Is it common for a limit switch to trip on extremely windy
Is it common for a limit switch to trip on extremely windy days? Last time this happened, I changed the filter and everything was OK. That was 1 month ago. Now it's happening again, on a very windy da… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I had my condenser switched from a carrier using R22 to a R410
I had my condenser switched from a carrier using R22 to a R410 puron. However, my air handler is still the old R22. My contractor ran the unit for 15 mins before I realized he did not flush the lines … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I am replacing a evaporator on a refrigerator and I have a
I am replacing a evaporator on a refrigerator and I have a FB12 flame barrier. It has two sides and aluminum and fiberglass. There's a little sticker on the aluminum side saying do not use the side to… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier vs Rheem brand? Which one better? For carrier we got
Carrier vs Rheem brand? Which one better? For carrier we got 10 year warranty, 3 years labor and 5 year maintenance plan For rheem we got 10 year warranty, 2 year labor and 2 year maintennacr plan Any… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
What Carrier thermostat will replace a Carrier Thermidistat
What Carrier thermostat will replace a Carrier Thermidistat installed in 2000? I want an exact functional replacement. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My upstairs HVAC has the evaporator located in the attic.
My upstairs HVAC has the evaporator located in the attic. There are two drain lines running inside the wall to ground, one on the evaporator and one on the drip pan under the evaporator, the drip pan … read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
61 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a carrier heat pump and my condenser unit continually
I have a carrier heat pump and my condenser unit continually runs even when the thermostat is turned off. can you help … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
New r410 condensing unit and new evaporator coil. gauges go
new r410 condensing unit and new evaporator coil. gauges go straight to retard when unit starts … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
What is the pressure drop across the condenser for a Carrier
What is the pressure drop across the condenser for a Carrier 19XL5151463 ser# XXXXX?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
How much does a 4/3 ton Lennox Elite XC16 AC cost?
I live in San Diego California and planning to replace my old AC and Furnace. So want to know how much would the following Lennox system cost ? 1) 4 ton Lennox Elite XC16 air + SL280V 2 Stage 70000 BT… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Night sir,here i have problem wit carrier 19 xr chiller 350
Night sir,here i have problem wit carrier 19 xr chiller 350 ton.the chiller can run55% after load to55% to 60%..the chiller evaporator refrigeration temp going very low approach 10 different..we all r… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
What is a good replacement for a Lennox 10acb30-7P
What is a good replacement for a Lennox 10acb30-7P… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a 9 year old Carrier Weathermaster 50HJ that is not
I have a 9 year old Carrier Weathermaster 50HJ that is not cooling properly. After much effort including; coil cleaning, filter replacement, condenser pressure testing, and condenser fan replacement i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier walk in condenser unit mod#pwh215L44d contactor not
carrier walk in condenser unit mod#pwh215L44d contactor not pulling in.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x