I ave ramsond ductless mini split air condition system E6 error

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
9/20/2017
HVAC Technician: David Bowden, General Contractor replied 10 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,309
Experience: Owner at Floridaco
Verified

T​he E6 error code is for a malfunction of the indoor fan motor. Attached is a link to the manual for reference, see page 27. Scroll down a little bit to the Manual tab, click on that and the owners manual will be listed.

http://www.ramsond.com/r37gwx/

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 10 months ago

Hello… Thank you for using Just Answer, my name is ***** ***** I will be assisting you today.

From the information you’ve provided, I will try to find a quick and simple solution to your specific question. All my responses are designed to be helpful, insightful, and any guidance or suggestions are based from the information you have provided on your post above, with the intent of trying to save you time, money, and headaches.

I have found in many cases it has always been better if we can establish an effective way to communicate, since either of us may have additional information or questions, that may be necessary in resolving the problem your experiencing, and uploading clear photos will greatly help us both.

After I have completed my research and provided my response to your question, all I ask in return is that you quickly and favorably complete the 5 Star Rating when it appears, so I may receive full credit for my answer, advice and recommendations. I appreciate your understanding and cooperation of this request.

Please note that I may not be able to resolve this problem, especially if it becomes necessary for a qualified service provider to be contacted to perform additional testing, diagnosing, or troubleshooting.

Is there any additional information you would like to add that was not mentioned before?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 1,309
1,309 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
After topping off the refrigerant, i ran my Ramsond mini-
After topping off the refrigerant, i ran my Ramsond mini-spit with the line shut. Now the compressor doesn't seem to run. Would that be because the condensor overheated, or is it likely that the entir… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How can I get technical support on a Shinco ductless mini
how can I get technical support on a Shinco ductless mini split heat pump air conditioning system. I am a licensed contractor. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
My 5yrold Ramsond 1200 BTU unit failed to switch from heat
My 5yrold Ramsond 1200 BTU unit failed to switch from heat to AC. Now it does nothing. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
On a Mitts ductless split, what is the E6 error code. Less
on a Mitts ductless split, what is the E6 error code … read more
Mark Trimble
Mark Trimble
Hvac trade school 1994
Morning Phil, just installed a Ramsond multi-split a/c unit
Morning Phil, I'm John We just installed a Ramsond multi-split a/c unit in the computer room. It's running but we're not getting ANY COOL AIR OUT OF IT… read more
Steve
Steve
Chief Engineer
9 satisfied customers
I'm checking out a comfortstar mini split system 4 indoor
Hi, I'm checking out a comfortstar mini split system 4 indoor air handler and one outdoor condenser . The indoor unit display E6 on two of them and the other two is working fine. Check to see what is … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Celiera 12000 BTU (1 Ton) Ductless Mini Split Air Conditioner
Celiera 12000 BTU (1 Ton) Ductless Mini Split Air Conditioner Model # ***** Runs fine for a while and then stops cooling and displays Error code E4… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 12,500 btu mini split Ramsond ductless heat pump.
I have a 12,500 btu mini split Ramsond ductless heat pump. It has an error code E2 " fault of indoor pipe temperature sensor". Is the sensor available, and if so where can I order one?… read more
Tech Justin
Tech Justin
Master HVAC Technician
66 satisfied customers
How to troubleshoot E6 error code on Gree GWH24AC-D3DNA2D?
I have a Gree GWH24AC-D3DNA2D mini-split. It is not heating or cooling. The indoor unit has power and is displaying E6 on the display. I have already disconnected the power for 10+ minutes, however, i… read more
R G
R G
44 satisfied customers
Do you ecommend a mini split ventless air conditioner for
Do you ecommend a mini split ventless air conditioner for a home 1200 square feet in Nova scotia- Is the mini split a better product ,as we now have hot air and interested in a ventless system- We now… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hey. I live on the top floor of a historical building. 1200sqf
Hey. I live on the top floor of a historical building. 1200sqf (one bedroom). They installed fan coils in each unit and in th e 7 years i have been living there it has had nothing but problems. It doe… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
ComfortAire air conditioner fan does not work at high speed
I have a Comfort Aire Mini-Split 18000 BTU Air Conditioner/Heat Pump. It is about five years old. It is blowing cold air, but even though the remote shows the fan on high, it is really on low (I guess… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Trane High Efficiency B1000 unit for one small building
I have a Trane High Efficiency B1000 unit for one small building (1200 sq. feet) that is adjacent to a log cabin. I'd like to expand its use to the cabin. Is this possible?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Are there any favored brands of ductless heat pump heating
Are there any favored brands of ductless heat pump heating systems for the Puget Sound region (Tacoma-Seattle area) at sea level? We have only a few days in need of air conditioning.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have LG 13 seer mini split ductless system. model is lsu246hv. The
I have LG 13 seer mini split ductless system. model is lsu246hv. The system is not working and error message is CH02. could you help to me, this system is still warrenty.......contact XXX-XXX-XXXX… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
is this hierarchy of a/c terms correct I. Ductless ac units
is this hierarchy of a/c terms correct? I. Ductless ac units 1. room ac a. portable ac units b. window ac units c. wall ac units d. ptacs 2. Split ac units (ductless) 1. mini split ac II. Ducted syste… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
My ramsond mini ductless HVAC, while in the heat mode, acts
My ramsond mini ductless HVAC, while in the heat mode, acts like the DIFFERENTIAL set point is zero, it seems to reach the desired room temp then shuts off, then comes back on very shortly, as if the … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
We are looking at a remodel of a 70 year old California Beach
We are looking at a remodel of a 70 year old California Beach house. The main house will be about 1800-2000 sq ft two bedroom house on two floors. It has an 8 foot ceiling. The unit MUST be placed in … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x