I have a Burnham Series 2 Model Gas fired Boiler (205). The…

I have a Burnham Series...
I have a Burnham Series 2 Model B Gas fired Boiler (205). The Blocked vent switch has tripped twice per year over the last few years. Had switch replaced. Had chimney checked. I also have an indirect water heater attached, not sure if that matters. The vent is 6 inches but the Chimney liner is 5 inches. Chimney is about 30ft high, one 90 degree and 2 45 deg bends not that far. Chimney guy wants to replace liner with a 6 inch liner for $1600. Could it be due to lack of fresh air in the boiler room? I have a 4 inch fresh air vent near ceiling but it is always very hot in that room when I enter it. The room is about 10x10ft. I am wondering if I should put some vents in the bottom of the boiler room door and possibly the basement door as well. They are always closed. Any ideas other than spending the money on a larger liner which I read somewhere could make the back draft worse but allowing the hot air to cool sooner before leaving the chimney. Thanks
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
9/20/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

A 5" liner may be sized properly. I'd be skeptical of the chimney guy if he didn't size the liner according to the code requirements in NFPA 54 (national gas code). However you don't have enough air for combustion unless that 4" fresh air has a fan on it. That's one possible fix. Install a "fan in a can" fresh air intake fan which uses a 4" vent for intake. Vent in the bottom of the door may not give you enough combustion air.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Thanks. Can you recommend a specific can? Are these cans "always on"? There is an outlet near to the vent I can plug it in too. So, you don't think if I open up the fresh air vent from 4 to 6 inches and put an 18''x12'' open vent in the door won't work, since it may be the cheaper option to start? My brief look up of "fan in a can" show $300. Thanks

Fan only runs when boiler fires. I can't say if the door grill is adequate without knowing the size of the adjoining space (sq ft + height) that can't be closed off by another door.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Adjoining basement space is 20x20ft but closed off with another door to the first floor. Could I put a 18x12 open vent on the door leading to the basement as well as leading into the boiler room. These are things that I can do affordably. Otherwise, I need to get an HVAC guy into install the fan. Thanks

Do you want me to do the combustion air calcs? If so I need the height of the basment ceiling

Ask Your Own HVAC Question
Customer reply replied 10 months ago
ok, height of ceiling is approx 7 feet. thanks

Input for this boiler is 130k btu. With the grill in the door (no matter how big) and the 4" round outdoor vent you only have enough air for 80K. So you need another 40 sq inch of outdoor vent area or a fan in a can. This assumes the boiler is the only gas burning appliance in that room. if you have a gas water heater too add another 20 square inches to the outside vent.
I'd appreciate a favorable rating

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 10 months ago
I will look into having one installed. The burner is the only gas appliance in the room. The hot water is indirect heat from same boiler. Thank you for your time and expertise.

You're welcome

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
24,398 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rick, I have a 2 family house. we have two boilers. One
Hi Rick,I have a 2 family house. we have two boilers. One boiler has no problems. The 2nd boiler will not ignite when heat is called. On the boiler system board, the power light and the TSTAT/CIRC lig… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
A new 9 inch liner [55 ft 5 floors including the basement
a new 9 inch liner [55 ft 5 floors including the basement ]was installed in our chimney. the bldg. is 17 units apartments. and the liner came with 1 9 inch '' hole '' to connect the flue to the boiler… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
A boiler failed a draft test. -6. We need -15 for state program.
A boiler failed a draft test. -6. We need -15 for state program. Would a chimney liner and draft inducer do the trick? What is a ROUGH cost for install? thanks… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
OK...Heres the scoop. Im going to need your A game (just
OK...Here's the scoop. I'm going to need your A game (just playing...somewhat :-)! I have a 44 year old home which is a rancher that 2652 sq feet home and still has the original furnace. The furnace i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a gas Burnham boiler that is 15 years old (Model #P204BWNS)
I have a gas Burnham boiler that is 15 years old (Model #P204BWNS) that has been having intermittent spillage problems, filling my basement with humid air (and potentially bad gases--I have a CO detec… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
We have a burnham 2 stage gas boiler. The boiler must be manually
We have a burnham 2 stage gas boiler. The boiler must be manually reset with a small button attached to the vent hood often to get it to fire up and heat the water. What do I need to focus on to fix t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My parents have a burnham v7 oil fired boiler used for hot
My parents have a burnham v7 oil fired boiler used for hot water baseboard and for hot water generating. It is vented into a very decrepit brick chimney. The chimney runs straight up vertically within… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a three story building in Bronx NY. On the first floor,
I have a three story building in Bronx NY. On the first floor, there are two small stores and there are four apartments on the 2nd and 3rd floors. The apartments have two bedrooms each. Currently, I h… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a gas boiler at 175,000 input BTU and a gas water heater
I have a gas boiler at 175,000 input BTU and a gas water heater at 32,000 input BTU going into the same chimney. What is the actual calculation to figure the proper flue diameter for this? Please supp… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My gas fired boiler is taking a very long time to draft correctly.
My gas fired boiler is taking a very long time to draft correctly. As a result there is an excessive amount of fumes present in the building. Could lime buildup in the boiler be a factor or is this st… read more
MagiicAir
MagiicAir
HVAC Service Supervisor
Vocational, Technical or Trade Scho
110 satisfied customers
I have a condensation problem with my furnace vent pipe. I
I have a condensation problem with my furnace vent pipe. I have a masonary chimney aprox 30' rise ,a 5" flue liner aprox 15' of horizontal pipe {slight rise} inside an unconditioned basement,{about 50… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Burnham V74T in an old house with 2 zones operating
We have a Burnham V74T in an old house with 2 zones operating & 2 that aren't being used. I've installed a new L8124C triple aquastat, along with a Taco 007. The old aquastat was approx. 15 yrs old an… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Help! Heating emergency!! My gas boiler will not run because
Help! Heating emergency!! My gas boiler will not run because the temperature sensor in the flue hood keeps tripping. The reason for this is that there is a constant cold downdraft coming in through ch… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi, I have a Burnham gas fired steam boiler for my 2 story
Hi, I have a Burnham gas fired steam boiler for my 2 story home, a brick common chimney for boiler, gas hot water heater and fireplace. With the flu sensor connected, the boiler cycles off too soon fo… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
my boiler will shut down once in a while for some reason it
my boiler will shut down once in a while for some reason it is 6 years old and to restart it i have to click the sensor that is on the chimney hat the boiler is gas and model 205ncl-ge12 i have replac… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am considering a new Trane XR80, 111,000 btu, single stage
I am considering a new Trane XR80, 111,000 btu, single stage furnace with 4" media filter, General humidifier, 4 ton A coil and a bayvent 800B in lieu of a chimney liner. Can you provide any tips or r… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I just bought a house with a gas boiler and a gas fired heat
I just bought a house with a gas boiler and a gas fired heat pump in a confined boiler room. There seems to be either a supply or exhaust duct coming from the top of the heat pump (AO Smith Promax Plu… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
I have a hard-to-solve problem My 10-yr old gas-fired boiler
I have a hard-to-solve problem: My 10-yr old gas-fired boiler with electronic ignition has clean burners and 50% of the time ignites and burns cleanly with good chimney flue draft. The other 50% of th… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x