Combustion and Flue Product Safety in Non-Standard Residential HVAC InstallDave (or another HVAC person if I'm not able to choose Dave after clicking "Get an Answer),The old furnace my mother is replacing was in a space too small to position the return and filter next to the furnace and also allow the recommended 25" of service area in front of the furnace. Placing the return and filter under the furnace needs to be explored given the very limited horizontal space available in the HVAC closet. The manual for the Lennox filter housing she's looking at shows vertical is an accepted configuration for the filter housing (and presumably Lennox furnaces (she'll probably get the EL296V)). At first read it seems like there might be a safety issue if the installers don't seal the return to the furnace (and presumably filter housing) perfectly...From the Lennox EL296V manual (I'll attach this if given the chance after clicking "Get an Answer"), p. 6... (In a section discussing placing the furnace in a small closet...) "When the furnace is installed so that supply ducts carry air circulated by the furnace to areas outside the space containing the furnace, the return air must be handled by ducts which are sealed to the furnace casing and which terminate outside the space containing the furnace. This is especially important when the furnace is mounted on a platform in a confined space such as a closet or small equipment room. Even a small leak around the base of the unit at the platform or at the return air duct connection can cause a potentially dangerous negative pressure condition."
From p. 10... "Improper installation of the furnace can result in personal injury or death. Combustion and flue products must never be allowed to enter the return air system or air in the living space. Use sheet metal screws and joint tape to seal return air system to furnace. In platform installations with furnace return, the furnace should be sealed airtight to the return air plenum. A door must never be used as a portion of the return air duct system. The base must provide a stable support and an airtight seal to the furnace. Allow absolutely no sagging, cracks, gaps, etc. (Later they sort of repeat this...) Return air can be brought in through the bottom or either side of the furnace installed in an upflow application. If the furnace is installed on a platform with bottom return, make an airtight seal between the bottom of the furnace and the platform to ensure that the furnace operates properly and safely."So it seems like combustion gas and negative pressure are always a safety issue BUT ARE EVEN MORE SO IF THE FURNACE IS MOUNTED ON A PLATFORM AND THE RETURN IS TO THE BASE, NOT A SIDE. What I can't figure from reading the directions is if this applies when combustion air is brought in from the outside (above the roof) and exhaust is expelled outside (above the roof). I think the term for this is "sealed combustion."So my question is... Are the warnings above to super-perfectly seal a return entering the underside of the furnace to the furnace applicable in what I am (maybe incorrectly) calling a "sealed combustion" installation? Or are combustion gasses and negative pressure more of a concern when there is not a PVC pipe bringing combustion air from outside the home AND a pipe exhausting exhaust to the outside of the house? If combustion air/combustion chamber/exhaust are separate from supply and return air I don't see what the need is for all these warnings?Thank you.Bruce
Show More
Show Less
Ask Your Own HVAC Question
Answered in 25 minutes by:
9/20/2017
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello Bruce, and welcome to Just Answer. My name is ***** ***** I'll be happy to assist you today. You are correct in calling the EL296V a sealed combustion unit. Improperly sealed return air is an issue with 80% furnaces that are not sealed combustion units. There have been deaths that have occurred from this, so Lennox (and other manufacturers) put this warning in all gas furnace manuals as a release of liability statement. The sealed combustion units will not be effected by improperly sealed return air as long as all seals on the furnace are intact and good. There could be the potential of a problem if one of the seals breaks down, tears, etc. From an Indoor air quality (IAQ) standpoint you would definitely want the return sealed regardless. The filter housing will also have a seal that will prevent leakage, so installing the filter in the closet is an accepted practice.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
Regan,Thanks for the response. The owner of the HVAC company my mother is working with and his right-hand man are good guys but are new to HVAC. Some of the techs have been around for a while.I think you and I are on the same page but would like to clear one thing up... You wrote "The sealed combustion units will not be effected by improperly sealed return air as long as all seals on the furnace are intact and good." Are the "seals on the furnace" you mention seals installed at the factory or are these seals that rely on the installers??? I'm more comfortable if the critical seals in this install are installed at the factory (tried and true) than if critical seals in a more-dangerous-than-usual install (because it'll be up on a platform) must be provided in the field by guys who might have only done "normal" side-return installs.I hope the ??? makes sense. As a reference, the configuration under discussion is Fig. 6 on p. 4 of the Lennox Carbon Clean 16 filter housing install manual. To re-state the ???, does this configuration end up relying less on the installer for safety when it is a sealed combustion unit with PVC in/out of the house than when it is a regular furnace that uses air from inside the house for combustion???Thanks. Sorry to be dense but the manual got me scared of the return to the bottom not being sealed perfectly but I'm hoping it's mostly talking about regular, non-sealed installs.Bruce

No problem! The seals are factory installed seals, so no need to worry. However, if there is ever service performed on the internal parts of the gas furnace (would presumably be years down the road) the seals would need to be checked and replaced if cracked or torn.

Yes, the sealed combustion units rely less on the installers for combustion safety than an 80% furnace that would require external combustion air to be pulled into the closet.

Ask Your Own HVAC Question
Customer reply replied 12 months ago
OK, last question regarding a safe raised (or any) install...Sounds like return house air through the bottom of a sealed combustion furnace (PVC in and out of the house) raised on a platform is about as safe as a regular furnace on the floor (with return air through the side) with standard maintenance of the factory seals years down the road. Is carbon monoxide the main danger involved in the installer seals the manual is discussing and the factory seals you've mentioned - that is, would a CO detector in the HVAC closet pick up much of the danger being discussed???After your response I'll rate you which I think means pay you. But, seeing this is a health-related question, I might ask it again for a second opinion - so if you see a similarly worded title, please leave it for someone else. Thanks for your input - I feel better about putting a raised furnace in her place!Bruce
Customer reply replied 12 months ago
Not sure if you initiated the "...switch to a live phone call..." offer or if it was auto-initiated. Unless there is something tricky about what the dangers of bad seals are and if a CO detector would likely pick up much of the danger, I'd prefer a fairly straightforward text answer and then rate and wrap this question up. Something along the line of "CO is much of the danger so a CO detector would help" or "There are many dangerous gases beside CO that arise out of bad seals so a CO detector won't help much"???

The live phone call was an automated response. Please ignore that. Yes, CO is the concern when talking about pulling flu gasses into the return air. I would recommend a low-level CO detector in the house (not the closet unless you add a separate one there) to ensure your mother would be alerted should there ever be a presence of CO in the conditioned space.

Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified
Regan Land and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a model CFM 80 PO CONV Miller fuel oil furnace. Can
Hi, I have a model CFM 80 PO CONV Miller fuel oil furnace. Can I install this model in a mobile home trailer where the furnace is located in a closed closet to where a air vacuume is created to pull r… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
new furnace, Olsen HML80c hiboy upflow oil furnace. Would like
new furnace, Olsen HML80c hiboy upflow oil furnace. Would like to try the low speed on the blower. Trying to overcome negative pressure in the basement when the blower comes on. There's a red wire on … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I live in a Mobile Home Trailer and my furnace is the original
I live in a Mobile Home Trailer and my furnace is the original down flow duct system, all duct work is underneath the flooring. and that furnace had crapped out. So i got a furnace and did nto realize… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Can the return air opening be adjacent the combustion air opening
Can the return air opening be adjacent the combustion air opening on a model PG8JAA furnace. The furnace is located in an interior closet with a louvered door. The combustion air comes in through the … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Lennox SL280UHV funace that uses outside air and my
I have a Lennox SL280UHV funace that uses outside air and my funace is located in basement room that we use for work out and laundry. I would like to install dampers in the 2 cold air ducts to keep th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I live in Port Coquitlam, and am retrofitting my house with
I live in Port Coquitlam, and am retrofitting my house with a Lennox G61V furnace. Am I required to retain the make-up air connection?… read more
HotWired
HotWired
Industrial Electrician
Associate Degree
75 satisfied customers
I am now disabled due to a stroke, but a year and a half ago,
I am now disabled due to a stroke, but a year and a half ago, I was an HVACR contractor. I installed four HVAC systems in a new home that was foam insulated. They are telling me now that I should have… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hi! I have a 1960 home with a (original, Im assuming - so
Hi! I have a 1960 home with a (original, I'm assuming - so OLD) gas furnace in the garage. I am enclosing a corner of the garage for a laundry room. The "best" wall lay-out would enclose one side of t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
On a Goodman 90% efficent furnace can th combustion air have
On a Goodman 90% efficent furnace can th combustion air have to come from the outside or can it come from the inside of the house like an 80% efficent furnace? Please explain?… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
Have a 2005 Nordyne GL1RA090C-16B gas furnace. Its in a hall
Have a 2005 Nordyne GL1RA090C-16B gas furnace. It's in a hall closet on main floor (center of house) behind normal 6panel door. When furnace on, the back of the door gets very warm. And, I see only fr… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
We have a Bryant 80t Perfect Heat two-stage fgas furnace in
We have a Bryant 80t Perfect Heat two-stage fgas furnace in a small closet in the lower level of our tri-level home. We have louvered doors on the closet that holds the furnace and water heater. When … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I am getting intermittent gas odor smells coming through all
I am getting intermittent gas odor smells coming through all the duct work in our house from our furnace. Model G24M series up draft. What could be the problem. Although we have smelled it some in pas… read more
Regan Land
Regan Land
HVAC Technician
Vocational, Technical or Trade Scho
768 satisfied customers
My Coleman Evcon furnace blows cold air every morning but will
My Coleman Evcon furnace blows cold air every morning but will blow warm air when you open the cloet door and shut off power and restart?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My current furnace is in my crawl space. The crawl space
My current furnace is in my crawl space. The crawl space is gererally dry. It has come timeto replace the HVAC unit, should I keep it in the crawlspace? or install in a closet inside the house? All th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I inspected a house in which the forced air furnace was located
I inspected a house in which the forced air furnace was located in a 5'x5' laundry room, which is provided with a normal bedroom door, a window, and a ceiling height of apx 15 ft. The 76,000 BTU Goodm… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am wondering if I have too much combustion air coming in,
I am wondering if I have too much combustion air coming in, and making my home drafty when the heat is not running. My gas furnace is in an inside closet, has two return air openings 9"x18" and 9"x22"… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hello. I live in a condo that was converted from a townhouse.
Hello. I live in a condo that was converted from a townhouse. I am on the bottom floor. My HVAC system is in an outside storage closet. It is a gas unit and just over a year old. The problem is not th… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
Air is coming into the house through my fireplace. After tearing
Air is coming into the house through my fireplace. After tearing the firplace apart, found the air is coming in through the metal seams. What can I use to seal the seams?… read more
Electrifier
Electrifier
Owner - Contractor
Bachelor's Degree
147 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x