I have a Carrier FE4ANB006, and the controller/Thermostat (Infinity System) says it cannot find the inside or outside units. But if I disconnect the condenser, it can find the air handler. Is there a way to bypass the communication and connect s simple standard thermostat?
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 59 minutes by:
9/19/2017
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, we can discuss this without any time limit, yes you can fit a standard thermostat, but Carriers wiring diagram on that is complex and you will loose some of the advance features with a communicating themostat.

So far it sounds like you have two of the bus wires crossed... had you used wire nuts or are there some wire nut connections in the mix (thats where the error generally occurs).

.

Tell me which wires go to which terminals on the thermostat, and also on the outside unit.

I will take a look at if for you

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am trying to find out the approximate manufacuring date of
I am trying to find out the approximate manufacuring date of a furnace manufactured by Olsen Manufacturing Co, Ltd. It's got to be over 25 years old. The model # XXXXX XXXXX 140 and the serial # XXXXX… read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
What Carrier thermostat will replace a Carrier Thermidistat
What Carrier thermostat will replace a Carrier Thermidistat installed in 2000? I want an exact functional replacement. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
What is size of clear tubing for condensation for Friedrich
What is size of clear tubing for condensation for Friedrich room air conditioner PH14B … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a carrier infinity 25hnb624c0031203o that is giving me
have a carrier infinity 25hnb624c0031203o that is giving me an error 179 - How do I fix this? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i was told that my condensing unit was no good by a company
i was told that my condensing unit was no good by a company that want yo sell me a new one i asked how come i was told my compressor was not working but when i put my gages on i get a reading lowside … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Inside uint blowing but outside condenser not coming on.
inside uint blowing but outside condenser not coming on … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
The condensate pump on my xe90 is cycling on and off. 1st
the condensate pump on my xe90 is cycling on and off … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
How does the cover get removed on a Carrier Carrier
How does the cover get removed on a Carrier Carrier TSTATBBP2S01B thermostat so I can replace it with an Ecobee? … read more
hvacdave84
hvacdave84
53 satisfied customers
Condenser fan going counterclockwise. Just notice it. put a
just notice it. put a new motor in it , but has differ color wiring … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC question I have a Carrier condenser unit that was
HVAC question I have a Carrier condenser unit that was running this morning when the heat was on in the house. The thermostat was set for heat? Model number 38TGO30300. I through the outside breaker b… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Buderus Wall Hung Modulating-Condensing Gas Boiler.
I have a Buderus Wall Hung Modulating-Condensing Gas Boiler. Two weeks ago an error message 6A appeared. The flame would not ignite and therefore we had no hot water. … read more
Bill
Bill
Service Mgr
100 satisfied customers
I have a carrier heat pump and my condenser unit continually
I have a carrier heat pump and my condenser unit continually runs even when the thermostat is turned off. can you help … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My rhino e75CN/e110cn high efficiency condensing gas boiler
my rhino e75CN/e110cn high efficiency condensing gas boiler will not heat the house above 64 degrees. have set the thermostats to 78 and still will not het the house above 64. the LED display on the u… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
My high efficiency condensing furnace (Carrier) emits a
My high efficiency condensing furnace (Carrier) emits a terrible eye-stinging odor when heating. The furnace runs quiet and otherwise appears to be trouble free, however I see (and smell) a fresh (wet… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Carrier 58SX gas fired condensing furnace that will
I have a Carrier 58SX gas fired condensing furnace that will not start. The pilot flame comes up upon the thermostat calling for heat but the flame is a bit lazy and it goes out after about 5-7 second… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier condenser Model#: 38HDC060321. Relay opens after
Carrier condenser Model#: 38HDC060321. Relay opens after about 1 minute of running. I've replaced the capacitor (usually burns out about every two years) and the main fuses (1 blew, replaced both). Go… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x