Customer Question
I have a water...

I have a water furnace. can low pressure in the ground loop cause poor cooling and heating performance

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes the room thermostat is set correctly and the filter is clean

Contractor's Assistant: Do you plan on doing the work yourself?

No

Contractor's Assistant: Anything else we should know to help you best?

A service man came and without testing said i needed a new pump pack because mine is 13 years old. in had him check the loop presure and it was 10 lbs

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 26 minutes by:
9/19/2017
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,818
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, low pressure *differential in the ground loop, (measured between the water in and water out connection on the water furnace can cause poor performance.. If the differential pressure was 10 lbs then thats fine, if the pressure measured at just one connection was 10 lbs then thats low.

Dirty air filters will also cause poor performance, so can the incorrect ounces of refrigerant cause poor performance.

.

the water furnace should be good for 15 to 20 years or a bit longer, so far it sounds like were talking to person on a sales commission.

.

We can go from there without a time limit after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,818
9,818 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,818 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trying to charge my Goodman 410a heat pump. This is a new
Yes this is a new system that was purchased about 10 months ago and just installed it is a package unit … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My relatively new furnace won't come on. Installed about
My relatively new furnace won't come on. Installed about four months ago. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My WaterFurnace Envision system just gave me a low
My WaterFurnace Envision system just gave me a low pressure/compressor alarm. Any specific steps I should take? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
I have a Trane 2GX Geothermal System, the High Pressure Status
I have a Trane 2GX Geothermal System, the High Pressure Status light is on and it is not cooling properly. The unit has an electronic air cleaner, I have cleaned the filter unit, the third red led was… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
we have a geothermal furnace and the thermostat fault light
we have a geothermal furnace and the thermostat fault light is blinking 10 times and then it pauses. It's very cold in the house.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
We have a geothermal water furnace system with closed ground
We have a geothermal water furnace system with closed ground loop. Everything is contained within the house except the ground loop. The system is not cooling. We just cleaned the filter. We are gettin… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am having diagnostic trouble on a tetco heatpump. Generaly
I am having diagnostic trouble on a tetco heatpump. Generaly poor performance 86 f supply air temp. with call for heat it takes 20 min to bouild to 250 lbs. have added refrigerant R22 to the point of … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have a 5ton Waterfurnace Synergy3, about 7 years old.
Hi, I have a 5ton Waterfurnace Synergy3, about 7 years old. Has performed flawlessly but now locks out on low flow once or twice a day. Have had technicians look at it without luck. Work to date inclu… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The installer of my Waterfurnace is out of business and the
The installer of my Waterfurnace is out of business and the present technicians believe the loop is too small. Is there any way to add loop capacity to the end of the loops or do we have to dig up the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
I had a Mcquay 5-ton HeatPump installed recently and have had
I had a Mcquay 5-ton HeatPump installed recently and have had problems with getting it to run correctly. This Heatpump replaced an old Mammoth unit (24 years old) and used it's vertical closed loop. T… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
I have a 4 ton Nordyne heat pump heating and cooling unit for
I have a 4 ton Nordyne heat pump heating and cooling unit for maaunfactured homes. I have only had this unit for 3 yrs now and about a week ago the blower motor got hot while running the AC. I had an … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi, I have a force hot air system that heats a five room apt.
Hi, I have a force hot air system that heats a five room apt. Two of the rooms don't get warm. The furnance is old but not sure if that's the problem. How can I find out what I need to do to get these… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a problem with a Climate Master Tranquility 20 manufactured
I have a problem with a Climate Master Tranquility 20 manufactured in early 2010. The unit will run fine if left off for several hours. However, after that run time when the thermostat calls for cooli… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,818 satisfied customers
My air conditionor compressor runs for ten minutes then shut
My air conditionor compressor runs for ten minutes then shuts down for six and then runs ten minutes. What would cause it to cycle like that? The air handler fan runs constantly, thermostat set at 68 … read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
Keepright furnace with an a/c unit. Not blowing cold air.
Keepright furnace with an a/c unit. Not blowing cold air. new filter, a/c service man testing the freon lines and said the pressure was good. It was blowing cold air fine a few days ago, now it only b… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
We have a ground source heat pump unit, Climate Master Classic,
We have a ground source heat pump unit, Climate Master Classic, with a Honeywell themostat (9812). It started blowing cold air when the green light comes on and blows continuously. Do we have a thermo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an American Standard boiler with hot water baseboard
I have an American Standard boiler with hot water baseboard heat in my tri-level house. There are two zones, one for the main living area and the lower level family room, the second zone for the upsta… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I keep having an ignition lockout code on my furnace. Two
I keep having an ignition lockout code on my furnace. Two different companies have been out here to fix it. The First company cleaned the Flame Sensor. The other Company came 2 weeks later and replace… read more
Jim Eastwood
Jim Eastwood
Lead service
High School or GED
100 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x