I have a Nordyine funace Everything works as it should

Customer Question
I have a Nordyine...

I have a Nordyine funace Everything works as it should except when it shuts off it will not restart on its own with turning the power switch on and turning it back on again. We cleaned the flame sencer We han a spare therme coil and tried it. The whole sequence of event are as should be ie. call for heat from thermostat , inducer moter start, thermo coil heats up, gass turns on. fires up, thermo coil cools off, then runs for a few minutes but wii not refire when the temperture dops down to point it should kick in again. What else can In chech for? The trans former is putting out 24 volts, 24 volts, at the pressure switch. What else can it be.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The filters are the 1st thing we looked at and replace. the thermostat is a brand new electronic one that he can set with his phone. and it works when we set it 5 degrees above the house temp. But we have to manualy turn the switch off then on. Just pull the wires off leading from the transformer and reinstall. We know the the polarity is correct for these wires

Contractor's Assistant: Do you plan on doing the work yourself?

I'm trying to do the work myself

Contractor's Assistant: Anything else we should know to help you best?

Is there batteries in the thermostate? Thermostate seem to be working as should be

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 27 minutes by:
9/19/2017
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,817
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, it sounds like the high limit switch is tripping (50% chance) if the furnace runs longer than 5 minutes. To test that fit a temporary jumper around it if the furnace keeps running replace the high limit switch. DO NOT LEAVE THE HIGH TEMPERATURE SWITCH JUMPERED DO THAT ONLY FOR A BRIEF TEST NO LONGER THAN 5 MINUTES.

If the furnace runs for less than 20 seconds then the printed circuit board may not be pick up the signal from the flame sensor rod.

You can do a heat stress test on the printed circuit board, warm it up to 125F slowly and gently using a hair drier, if anything changes for the better or worse the board is bad.

.

We can go from there without a time limit after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,817
9,817 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,817 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I am not getting Rh power to my thermostate, Some sort of
I've checked the transformer and I'm getting resistance and the only fuse I could find appears to be intact.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox G40uh-48c-110-15. no LED lights. I replaced
I have a Lennox G40uh-48c-110-15. no LED lights. I replaced the ignition circuit board, and the thermostat. stil nothing. We recently had power brown outs and falures due to storms, the main circuit b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hi I have a GWA Series 2 Boiler boiler model number 1135-601
Hi I have a GWA Series 2 Boiler boiler model number 1135-601 Dropbox Link to Boiler Picture https://www.dropbox.com/s/h2jaluegygoxvco/2014-12-15%2016.56.11.jpg?dl=0 I have a Honeywell YTH8320ZW1007/U … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
hey, i have some questions about wiring a thermostat into my
hey, i have some questions about wiring a thermostat into my existing boiler... is there really a human on the other end of this thing? testing, testing...… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Janitrol furnace has been working have power to the door switch
Janitrol furnace has been working have power to the door switch but not getting red light on board… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am trying to hook up a venstar t1700 thermostat to my intertherm
I am trying to hook up a venstar t1700 thermostat to my intertherm model MGHA-056ABFC-02. The old thermostat was only a two wire hook-up and I cannot seem to get my venstar to work. It powers up but k… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
we have a rheem model thslhm1817ja 2.5 ton. the moter coil
we have a rheem model thslhm1817ja 2.5 ton. the moter coil wouldnt start the motor 48hrs ago. i removed the coil from our other unit and it work fine till now. you can manually turn the squirell fan a… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hot Dawg heater runs for about a minute burners shut down and
Hot Dawg heater runs for about a minute burners shut down and then system restars but keeps shuting down. Have replaced control board and flame sensor plus jump out rollout circuit. could the new boar… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
ok i have no ac. furnace is carrier 8000. i checked the condensor
ok i have no ac. furnace is carrier 8000. i checked the condensor 1st the power switch to test it worked.. it came on line. i check the 24 volt line to the condensor no power. i checked the transforme… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have mastertrol mark V automatic balancing system, when I
I have mastertrol mark V automatic balancing system, when I call to raise the heat it works fine, when I call to lower the temp. ac does not work, can you help me… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
have a nordyne model 03eb-012h furnace need troubleshooting
have a nordyne model 03eb-012h furnace need troubleshooting sequences to find fault,will not come on, getting 240v to heater 24v to thermo. would normally call a tech out but i have 20 of these things… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a 38tra 3ton. Starting contactor will not pull in. can
Have a 38tra 3ton. Starting contactor will not pull in. can hold it in manually and fan and comp. run. Small tubing gets extremely hot. Therm is all right, turns on heat, swaping heating and cooling w… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to wire new thermostate to goodman heat pump furnace,
Trying to wire new thermostate to goodman heat pump furnace, installin hunter 44905 thermostat. followed diagram and heater wont kick on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem Classic 90 furnance and have a question concerning
I have a Rheem Classic 90 furnance and have a question concerning the wiring from an aprilaire 550 humidifier. The reason for my question is the humidifier is not working when the furnance is running.… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have an older (25 years) JVS50 Mini Therm boiler where the
I have an older (25 years) JVS50 Mini Therm boiler where the pilot light comes on but the main valve does not open for the main burner to come on. The flame sense feedback is apparently not working. G… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,817 satisfied customers
I have a coleman evcon presidential furnace model # 356oca8i
I have a coleman evcon presidential furnace model # XXXXX serial 3 XXXXXXXXX I turned off the breaker to work on the duct turned back on unit now blows only cold air? Changed buss fuses, checked conti… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My air handler is not coming on. It is a Goodman A42-5. I removed
My air handler is not coming on. It is a Goodman A42-5. I removed the panel and discovered a wire, leading from the white wire (right)hot feed to the left connection to the boost heat coil, was fried … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier mdl#58gpo75-3 furnace that will not fire the
I have a Carrier mdl#58gpo75-3 furnace that will not fire the burners or kick in the A/C. The pilot light is lit. I have 24+ volts going to a brand new curcuit board and have a brand new Hunter digita… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.