I work at a church with 5 units some of which are 2 stage I…

I work at a...

I work at a church with 5 units some of which are 2 stage I am told. I don't want a thermostat that will make decisions. I have a nest and it changes the temp some times the wrong direction without my permission. I want the best wifi enabled thermostat I can buy. I like gadgets but want control. I was wondering about the Vision Pro 8000 wifi or redlink. What do you recommend?

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Thermostat. the units are 15 ton, and 7.5 ton York units.

Contractor's Assistant: Do you plan on doing the work yourself?

No. I will have a commercial pro do the work

Contractor's Assistant: Anything else we should know to help you best?

I want to control it with my phone even if I am not there.

Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
9/19/2017
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the red link is wireless, you do not need that for the control you want and it adds complexity and failure points that you do not need. The Vision Pro 8000 is not wifi so I will have to locate a wifi version for you

Here is the manual on it.

.

We can go from there without a time limit after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a little about your technical background and instruments on hand so that I can coach you most effectively. We can go from here.

Ask Your Own HVAC Question
Ask Your Own HVAC Question
Customer reply replied 1 year ago
I was looking at the Vision Pro TH-8321 WS which is wifi enabled and the TH-8321 R which is redlink. I am guessing you are saying that the redlink doesn't attach to wires from the thermostat that is there but is wireless back to some type of controller or connection point. I called Honeywell to see what they recommended and they recommended the TH-8321 R.

Honeywell like most manufacturers likes selling their latest and most expensive....nothing wrong with that, it is just that the wireless feature adds complexity you might wish you did not have.

Here is the manual on redlink

Ask Your Own HVAC Question
Customer reply replied 1 year ago
under what circumstances would you recommend the redlink?

I would recommend the red link on new construction but only if all of the system components were also compatible with red link, but with reservations, the more complex a system is the harder and more expensive it is to find qualified repair people

I would recommend red link if there were not sufficient wiring already pulled for the hard wired version.

Ask Your Own HVAC Question
Customer reply replied 1 year ago
Got it. Thanks for your patience. Have a good night.

Its time to select the 'Finish and rate your expert...' link near the top of the page to close the question, that is also the only way the company pays me for time. Thanks in advance

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,880
9,880 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,880 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I've been told the thermostat vision pro 8000 doesn't
I've been told the thermostat vision pro 8000 doesn't dehumidify properly because it reads the humidity in the walls because of the placement of the sensor. The Honeywell IAG doesn't seem to have this… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm a general contractor setting up a new system for a
Hello Pearl! My name is***** a general contractor setting up a new system for a homeowner. Honeywell vision pro 8000 thermostat and Honeywell rem5000R1001 portable comfort control. Do I also need a wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am installing a nest thermostat in lieu of an my
Hi I am installing a nest thermostat in lieu of an my communicating Bryant stat. I currently have ABCD labeled wires. Reading this thread, I understand I can move them in the furnace to RWYG. My quest… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Is it ok to put a honeywell thermostat on a trane AC? Or
Is it ok to put a honeywell thermostat on a trane AC? Or will it drop the warrenty?Thanks.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Carrier ComfortZone II system three zone as well,
Hey - I have a Carrier ComfortZone II system three zone as well, which includes AC. Looking to switch over that allows remote access. Previously you suggested (three years ago) to use the Honeywell Tr… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
hi Douglas I am looking to replace my programable thermostate (Honeywell CT8602 with a ne
hi Douglas I am looking to replace my programable thermostate (Honeywell CT8602 with a newer wifi type. The one I am replacing is a master zone compatible as I have a slave thermostat in another room … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I just moved into a home that has a 2010 trane veritable speed
I just moved into a home that has a 2010 trane veritable speed comfort link II heat pump XL20i unit I want to get a smart thermostat that I can control wi-fi, which one will work? also I have done a l… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am connecting a vision pro 8320 to a York Predator 7 ton,
I am connecting a vision pro 8320 to a York Predator 7 ton, dual compressor heat pump. The York has the following terminals: R, W1, W2, Y1, Y2, G, C, OCC, P, P1, X, SD. I have connected the following … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HVAC Residential- I have a Trane xl16i 2 ton split system with
HVAC Residential- I have a Trane xl16i 2 ton split system with a xc95m furnace. I have NO dehumidifier on system. Will the Honeywell Commercial vision pro 8000 work on my system.? Particular to the fu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a TRANE air conditioner (16I or something like that,
I have a TRANE air conditioner (16I or something like that, the "high efficient one" which has 2 compressors. Is there any thermostat on the market which will handle that, I am not satisfied with the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I now have a question on wiring a thermostat for another unit.
I now have a question on wiring a thermostat for another unit. Please advise as to the wiring from a Carrier thermostat #TSTATCCNHPO-1 to a Honeywell thermostat TH8320U1008 VISION PRO 8000. The unit i… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Carrier split system air/air heat pump. It was installed
I have a Carrier split system air/air heat pump. It was installed with a Honeywell model TH8110U1037 Thermostat. It has connections on one side for S1 and S2 and on the other side RC/RC, R/R, W1/O, Y/… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have Pro TH 4000 Series Programmable Thermostat (Pro TH4110D/Th4210D).
I have Pro TH 4000 Series Programmable Thermostat (Pro TH4110D/Th4210D). My question is are these thermostat able to have code input that will render them unusable to others without the code input. If… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a 10 year old carrier 3.5 ton that has gone kaput. I
I have a 10 year old carrier 3.5 ton that has gone kaput. I am being recomended two units: 1)trane 4 ton 4twr5048 XR15 heat pump with 4tee3f49 air handler and a vision pro 8000 thermostat. 2) comfort … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Bryant 698A 2-speed Plus heat pump (1995) with a Bryant
I have a Bryant 698A 2-speed Plus heat pump (1995) with a Bryant HH07AX113 programmable thermostat - the thermostat is showing some squirrily readings and the AC will only come on occasionally. What d… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I Have a Commercial VisionPro 8000, trying to hook up the terminals.
I Have a Commercial VisionPro 8000, trying to hook up the terminals. My old unit has a terminal “V” for an IFC board that permits gas valve modulation used with modulating heat furnaces. Where do I co… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Greetings, We just installed a York Affinity Y9C modulating
Greetings, We just installed a York Affinity Y9C modulating (multistage) furnace (95% + AFUE) and I am wondering which do-it-yourself installed Honeywell thermostat I should get? Thanks ... XXXXX XXXX… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am having a Lennox G71 furnace installed. Ive been reading
I am having a Lennox G71 furnace installed. I've been reading that the best thermostat to use for this is the Lennox comfort sense 5000. My installer is only including the Honeywell focus pro 6000, wh… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x