Can someone help me with trouble shooting my Daikin VEF

Customer Question
Can someone help me...

Can someone help me with trouble shooting my Daikin VEF system?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

This is an HVAC system

Contractor's Assistant: Are you an HVAC professional?

Yes

Contractor's Assistant: Do you plan on doing the work yourself?

I am getting a fault code of U4 at the master tgermostat

Contractor's Assistant: Anything else we should know to help you best?

Don't understand your question

Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 9 months ago
Who is helping me?
Customer reply replied 9 months ago
I just paid my $$
Customer reply replied 9 months ago
Is anyone out there?
Answered in 5 days by:
9/22/2017
HVAC Technician: MattR757, HVAC Technician replied 9 months ago
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 67
Experience: 18+ Years experience in residential and commercial HVAC service and repair
Verified

Sorry noone responded sooner.

U4 is a communication error between indoor and outdoor units - Make sure that power is on to both units and reset power to both to clear stored errors - Depending on how it was installed, sometimes an external components like a condensate float switch or a smoke detector may be wired into the communication wiring chain and will break communication - check any drain pans for water and look at the wiring to make sure there isn't any damage (landscapers are notorious for damaging outdoor wiring with their weed eaters).

Aside from that you could have a bad board or a dropped address (communication glitch that disconnects the indoor unit from the com loop) and might need a Daikin tech to come investigate.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
I was getting U4 when the system was running off of my emergency generator as a consequence of Hurricane Wilma. Now that permanent power is back up, I am now getting a U7 error code! AHU's are all running as we resent power to all of them, as well as the CU, but no cooling as the CU is not kicking on! Thx...Rich Housh...old energy guy and former HVAC technician
HVAC Technician: MattR757, HVAC Technician replied 9 months ago
U7 error is no communication between the main pc board and the inverter pc board inside the outdoor unit. Almost always means that the inverter PCB is bad. I'm not 100% sure, but I may still have a copy of a Daikin service manual that goes through steps on how to test the board and compressor. I will message you back once I get back to my office to check
Ask Your Own HVAC Question
HVAC Technician: MattR757, HVAC Technician replied 9 months ago

Here is the service manual for VRV III - The VEF units are Vicot European fan coil units and I do not have any manuals for those specifically. This manual is huge, but has a really well organized troubleshooting section and a lot of very specific test procedures outlined in it. Hope this helps some -

https://drive.google.com/file/d/0B5ej3CaCXvZiTVpBcVpjZTBmcWM/view?usp=sharing

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask MattR757 Your Own Question
MattR757
MattR757
MattR757, HVAC Technician
Category: HVAC
Satisfied Customers: 67
67 Satisfied Customers
Experience: 18+ Years experience in residential and commercial HVAC service and repair

MattR757 is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Installing RTH7600 series thermometer. tagged all wires from
Installing RTH7600 series thermometer. tagged all wires from old thermo. Wiring new thermo .. Instr. said to place RH in in red terminal and R wire to RC. All wires were tagged and there is no Red wir… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Also lost power indication in my basement furnace fan unit
Also lost power indication in my basement furnace fan unit and connected thermostat - no indication of power at the unit or thermostat - likely associated with power fluctuation… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a taco zone sentry on my fan coil unit. when I turn
I have a taco zone sentry on my fan coil unit. when I turn on the power to the unit and the fan comes on the green lights do not blink indicating it is on. I took one of the taco zone sentrys office o… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Can the old Fan Coil thermostat's be replaced by any newer
Can the old Fan Coil thermostat's be replaced by any newer programmable models? … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have an old honeywell three speed thermostat in a condo
I have an old honeywell three speed thermostat in a condo and want to replace it but the wires dont match up with the new one … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a Carrier air handler model number FB4ANFO30 it's a
I have a Carrier air handler model number FB4ANFO30 it's a horizontal left with a right slant coil it looks like when I take the blower out I see what looks like mold and a pattern. Should there be a … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a question about my condos heating/cooling system.
Hello, I have a question about my condos heating/cooling system … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I haver carrer 16 seers with a FV4C fain coil,(DEALER CANNOT
I haver carrer 16 seers with a FV4C fain coil,(DEALER CANNOT HOOK THE UNIT UP SO THAT IT WILL WORK (WHAT STEPS CAN I TAKE … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,874 satisfied customers
I install a Goodman heat pump and fan coil whit auxiliar
Second opinion] I install a Goodman heat pump and fan coil whit auxiliar element but heat pump start 5 minutes and it get stop for 2 min and start again … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I install a Goodman heat pump and fan coil whit auxiliar
I install a Goodman heat pump and fan coil whit auxiliar element but heat pump start 5 minutes and it get stop for 2 min and start again … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a Honeywell 4 zone control system in a home from
I have a Honeywell 4 zone control system in a home from 1963. Do you have any manuals I can access … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Have Carrier fan coil unit model FV4CNB003. Have Carrier Fan
Have Carrier Fan Coil unit # FV4CNB003. Seemed to run and change speed during operation. Is this normal? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a fan coil blower motor that rattles something
I have a fan coil blower motor that rattles something fierce, the motor seems okay but I think the bearings are going. Where do you even get replacement ball bearings. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier infinity system. Had power outage. Now thermostat
Carrier infinity system. Had power outage. Now thermostat can't locate outside unit … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Phil, I have one of these: - Firstco Ceiling Fan Coil for a
Hi Phil, I have one of these: https://www.firstco.com/Products/Multi-Family-Residential-Products/Ceiling-Fan-Coils/HX - Firstco Ceiling Fan Coil for a Bryant Heat Pump. We live in a condo. It has only… read more
Michael Ferryman
Michael Ferryman
97 satisfied customers
I have a RAS-10HRNM outside unit 2 fan coil units RPI-5.0
I have a RAS-10HRNM outside unit 2 fan coil units RPI-5.0 FSN2 and 2 wired remote control switches PC-P1H installed 5 years ago.My problem is that one fan coil unit will not operate but the other one … read more
Michael Ferryman
Michael Ferryman
97 satisfied customers
I have a fan coil with a 4 wire thermostat, I am trying to
I am trying to replace with 5 wire stat blue wire is not connected on either end trying to figure our where to land the wire in the fan coil … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a carrier fv4b 02 model fan coil unit in my house.
Hello Paul. I have a carrier fv4b 02 model fan coil unit in my house. Want to know how old it is? Just bought the house in Florida. Plus is in an upstairs cupboard and has condensate pipes discharging… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.