MY AC IS NOT COOLING

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

2 DAYS

Contractor's Assistant: Do you plan on doing the work yourself?

YES, i AM TRYING

Contractor's Assistant: Anything else we should know to help you best?

I HAVE replaced the cap, the fans are running, 240 V contactor seems to be working. Compressor is not running.

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
9/15/2017
HVAC Technician: Regan Land, HVAC Technician replied 11 months ago
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist
Verified

Hello and welcome to Just Answer - my name is ***** ***** I'll be happy to assist you today. Does your meter happen to have an amp clamp?

Ask Your Own HVAC Question
Customer reply replied 11 months ago
I have one of those somewhere around here. Purchased a new contactor. looks good. single pole sealed from ants.
HVAC Technician: Regan Land, HVAC Technician replied 11 months ago

Okay, turn off the high voltage at the condenser and turn the thermostat to cool. Put the amp clamp on the black wire that goes to the compressor and turn the power on. Watch the meter closely and see what it reads then let me know.

Ask Your Own HVAC Question
Customer reply replied 11 months ago
The thing that concerns me most is that my old board does what the amazon reviewer pg318 says " I had to wire into a couple of the relays from that system, since I have a 240V reversing valve, and this one is configured for a low voltage valve coil, and I used the existing fan control contactor to prevent the full current going through the relay on this board, for better reliability."
Is this "Universal defrost controller" going to work for me?
Today, I have received this new defrost controller and would like to install it now. https://www.amazon.com/Rheem-Protech-Defrost-Control-47-102685-85/dp/B004W10H7O/ref=pd_sbs_60_2?_encoding=UTF8&pd_rd_i=B004W10H7O&pd_rd_r=RBW2S7KKZKERRP20J6XR&pd_rd_w=XE58N&pd_rd_wg=nQqPI&psc=1&refRID=RBW2S7KKZKERRP20J6XR I am attaching a picture of my old board which looks similar to this one: http://www.ebay.com/itm/Rheem-Ruud-1157-***-**-****84-01-Defrost-Control-Board-NEW-Priority-Mail-Ship/351327526336?_trkparms=aid%3D222007%26algo%3DSIM.MBE%26ao%3D2%26asc%3D41375%26meid%3D00e14b0a010c4a82b80ea81862ee2a11%26pid%3D100005%26rk%3D1%26rkt%3D6%26sd%3D291827823249&_trksid=p2047675.c100005.m1851
Customer reply replied 11 months ago
on the new board , what do I select for the AB dip switch setting?
Customer reply replied 11 months ago
I am going to need you to draw me a picture using the photos so I can correctly connect the dozen or so wires.
Customer reply replied 11 months ago
I am going to need some directions on how to correctly position the two sensors onto my Heat Pump Unit. thanks.
HVAC Technician: Regan Land, HVAC Technician replied 11 months ago

Sorry, I just got your reply. Are you positive the board is bad? It looks like there's oil all over the suction line at the compressor. If the unit has a low pressure switch it's possible that the compressor isn't coming on due to an open pressure switch.

Ask Your Own HVAC Question
HVAC Technician: Regan Land, HVAC Technician replied 11 months ago

If the board is bad then the second one (from ebay) is the one you want - however you will want the sensors that come with it. try this one:

https://arnoldservice.com/product/47-102684-83-rheem-ruud-heat-pump-defrost-control-board/

Ask Your Own HVAC Question
Customer reply replied 11 months ago
I think the board is bad because I shorted the two pins on the corner and blew a 24V 3 amp fuse on the main board in the heating unit (inside). I have replaced it with a 5 amp fuse from a similar board for now. This unit is like 15 years old. I have not had regular (yearly) maintenance performed on it. So you are suggesting after a replace the board with a proper unit and get the Freon topped up, it will all be good. That sounds promising if I can add a little from a pressurized can and not pay someone 150 USD to do it.
HVAC Technician: Regan Land, HVAC Technician replied 11 months ago
Popping the fuse by shorting test pins does sound like a board issue - as long as everything else is hooked up properly. It looks like everything is from what I can see in the pictures - but I can't see the contractor. If you feel comfortable, you could try to use a piece of wire and jump the C terminal to CC (with thermostat calling for cool) and see if the outdoor unit comes on. If so then the board is definitely bad. If not, then we need to continue checking.
Ask Your Own HVAC Question
Customer reply replied 11 months ago
yeah, I guess I can do that. I think you mean the HVac on the left side of the board. c and cc
Customer reply replied 11 months ago
nothing good to report , something got hot and popped.
HVAC Technician: Regan Land, HVAC Technician replied 10 months ago

Not sure I follow. All that jumping C and CC would do is bypass the relay that's built in to the board. Do you know what it was that popped? Can you take a picture of the contactor for me and post it here?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Regan Land Your Own Question
Regan Land
Regan Land
Regan Land, HVAC Technician
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Over 20 years of experience, NATE Certified, Licensed HVAC Contractor, Certified IAQ Specialist

Regan Land is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My outside unit does not come on at all but my inside unit
Hello my outside unit does not come on at all but my inside unit is on and blowing hot air. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
I set the thermostat, outside fan tries to come on, and has
Good day sir! I set the thermostat, outside fan tries to come on, and has 2x. I was pretty sure it was the start cap so I replaced it, then it started up the first time for about 5 mins or so then has… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
Billy. My ac unit outside. The compressor isn't running. Fan
Hey Billy. My ac unit outside. The compressor isn't running. Fan was running but now it's not. I looked at our previous conversations and tested the contractor and it does op out but the compressor is… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I get 26 volts to the contactor without power but when I put
Hi I get 26 volts to the contactor without power but when I put the 240 v on the 26 volts goes away and the contacts go open … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Lennox merit series 13acx. Was working fine all of sudden
Lennox merit series 13acx. Was working fine all of sudden yesterday won't kick on now. Check breakers and they're fine. What should I check next?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
THIS QUESTION IS FORCustomer Tim, you were helping me
THIS QUESTION IS FORCustomer Hi Tim, you were helping me a few days ago to hook up a new motor for my central air. I have bought a second new motor for my other system, which is the same as the first … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I replaced my old fan motor today. It had 3 wires and the new
I replaced my old fan motor today. It had 3 wires and the new fan has 5 wires. I don't understand the wire chart where to hook up the wires.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Gotoman. Tim here. Got a call from the tenant this morning
Hi, gotoman. Tim here. Got a call from the tenant this morning that the AC wasn't working last night. It's a Trane XE 1000, manufacture date 2002. Said the condenser fan was not turning. My chest swel… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Frozen compressor. Thawed out working again, haven't been able
Frozen compressor. Thawed out working again, haven't been able to check if the compressor and outdoor fan keeps running after the thermostat cooling setting is reach, possible due to a shut contactor;… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier 25HBR360A310 heat pump with a HK32EA001 defrost board
Carrier 25HBR360A310 heat pump with a HK32EA001 defrost board in it. When thermostat (TSTATCCPHP01-B) is set to heat or cool, the inside blower motor (on Carrier model 58MCB120) works just fine, but t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Rheem AC unit for the downstairs is humming when the power
My Rheem AC unit for the downstairs is humming when the power is on, does not turn the fan motor, and the compressor does not run. The fan spins freely by hand. I am told that it might be a capacitor … read more
GreenHeating
GreenHeating
Owner / Installer
Boiler / Steam Engineering
59 satisfied customers
carrier 5 ton Ac unit 5 years old plus.Outdoor unit not running
carrier 5 ton Ac unit 5 years old plus.Outdoor unit not running nor cooling currently high temps outside 100 plus, thermostat seems to be communicating with furnace and outdoor temp sensor. Was readin… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hi, I have a Lenox 10acc, and it is not cooling as of yesterday.
Hi, I have a Lenox 10acc, and it is not cooling as of yesterday. The fan runs, but I believe the compressor is nor running. It looks like I had a short on the outside disconnect...I replaced the disco… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a lennox 10acb42-11p. Fuses blew, replaced, turned
I have a lennox 10acb42-11p. Fuses blew, replaced, turned on unit, now getting a buzzing sound from the unit. Fan is not running. Any suggestions what to check next?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a 10acc-036 ,i replaced the motor & condensor, with
i have a 10acc-036 ,i replaced the motor & condensor, with dayton 4m205 & condensor,this is the second motor in 2 days either turn on, the dayton, has black to l1 purple l2,solied brown to condensor f… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
my trane xl 1600 works fine all day, then about 630 compressor
my trane xl 1600 works fine all day, then about 630 compressor will not stay on. it will not blow cool air, fan will continue to work. about 3 hrs later compressor will will start to work again an ac … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Compressor wont turn on, buzzing sound from unit. Fan at the
Compressor won't turn on, buzzing sound from unit. Fan at the furnace is on, no tripped breaker power to unit. Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Goodman CE30-1HB condensor unit is not running....does it need
Goodman CE30-1HB condensor unit is not running....does it need a contactor replacement? where is that?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x