I just installed a defrost board and on power up the board

Customer Question
HI, i just installed a...
HI, i just installed a defrost board and on power up the board blew?
JA: I'll do all I can to help. How long have you been dealing with this?
Customer: just found the problem yesterday.
JA: Do you plan on doing the work yourself?
Customer: yes.
JA: Anything else we should know to help you best?
Customer: haven't really checked any thing else yet suspect the control board and economizer motor might be bad.
Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
9/13/2017
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 222
Experience: Owner HVAC company
Verified

Good afternoon, Im sean and look forward to helping you,

Do you have the model number for this unit

Ask Your Own HVAC Question
Customer reply replied 2 months ago
it's 50TCQD09D35S5A0
Customer reply replied 2 months ago
no
HVAC Technician: HvacmanSean, HVAC Technician replied 2 months ago

I will not be able to assist with this particular set up, I will opt out and another expert will hopefully grab this, Please don't respond until someone else joins on!

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, tell me in detail about the board, did it explode, burn or just cease working. Tell me if you can run the compressor by pushing the contactor bar in with the tip of an insulated screw driver.... if so,... remove the two wires that run to the condenser fan motor and measure the resistance across them with an ohm meter.... next measure ohms between each of the fan motor wires and the copper tubing on the unit.

.

Let me know what you can find, we can go from there.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
thanks phil will get back to you with results seems like you think it could be a bad load.
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Yes that is correct I suspect a bad load (shorted fan motor windings) a bad fan motor run capacitor would not ruin the defrost board.

If the compressor will not run, but does not trip the breaker, its run capacitor might be bad as well, especially if you are using a dual run capacitor. ( comm connection in the middle of it, and fan and herm on the opposite sides)

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,022
6,022 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,022 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a replacement condenser from Goodman, the original
i have a replacement condenser from Goodman, the original was a variable speed and they have since discontinued it and as a warranty replacement they sent me a different condenser and the wiring is to… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser not running checked all breakers and thermostat
condenser not running checked all breakers and thermostat settings … read more
Webb-Guy
Webb-Guy
tech.
72 satisfied customers
I changed the condensation pump on my gas furnace and now
I changed the condensation pump on my gas furnace and now the furnace won't start. The old pump was direct wired through the kill switch and the new one had a plug. The new one also had a yellow wire … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My 5 ton condenser unit located on a concrete slab outside
My 5 ton condenser unit located on a concrete slab outside my house was damaged in the Hurricane Harvey flood. It looks like I need a new condensing unit. I just received a quote of $4,000 for a new 4… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a Peerless steam boiler that had a condensate pump
I have a Peerless steam boiler that had a condensate pump that ran when the tank filled. We have changed to a condensate demand pump with a 24 volt controller relay. How do i connect into the Mc D 47 … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR
I'M IN MONROVIA CA AND I NEED THE CONDENSER FAN AND THE FAN MOTOR FOR THIS MODEL. NAC048AKC3 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Condensate pump for a-c in split system ran continuously and
Condensate pump for a-c in split system ran continuously and now Lennox furnace Model GS18Q314E-100-5 will not come on. … read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
I have an Ultra 105 Series 3. Condensation appears on the
Condensation appears on the inside at the top and by the exhaust. It then drips down and fills the bottom of the unit. Is an exhaust leak? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Moved into our new home and they added an AC condenser. In
Moved into our new home and they added an AC condenser. In the mechanical room there is a bundle of three wires that are not hooked up to the main board of the furnace. The bundle goes to the AC conde… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the best way to channel off the condensation water
What is the best way to channel off the condensation water on outside heat pump? When it is heating a lot of water is accumulating. Our lowest temp has only been 54 degrees outside so shouldn't be ove… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Condenser fan running compressor not running or humming.
Condenser fan running compressor not running or humming. Checked capacitor it's good. Checked contact it's also good. Pills in by its self and has just over 240. Could it possibly be something in the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a carrier condenser outside and the relay keeps on
I have a carrier condenser outside and the relay keeps on popping I want to know if I can bypass until I can get a new one … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm gathering information on wall hung non-condensing
Hi. I'm gathering information on wall hung non-condensing boilers. I am the president of my Brooklyn co-op. We have 8 units in our building and each unit has it's own wall hung (Baxi) non condensing b… read more
Phil
Phil
Mechanical Engineer
6,022 satisfied customers
The inside fan is not running, condenser will run, 3 days,
the inside fan is not running, condenser will run, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My refrigerador compressor is running so is the condenser
My refrigerador compressor is running so is the condenser and evaporator fan and all the lights but it wont cool at all … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
C wire problem. A day. Condenser not turning on with
Condenser not turning on with additional wire to c terminal on fan unit … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm in the process of installing a Goodman 2 ton condenser
Good morning! I'm in the process of installing a Goodman 2 ton condenser (GSX140241) however I have a few questions. 1. On the name plate it states that this unit requires 15 amps. Should I connect th… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,070 satisfied customers
Air handler is running but condenser is not with a red &
Air handler is running but condenser is not with a red & green light flashing … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question