Customer Question
HI, i just installed...

HI, i just installed a defrost board and on power up the board blew?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just found the problem yesterday.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

Haven't really checked any thing else yet suspect the control board and economizer motor might be bad.

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
9/13/2017
HVAC Technician: HvacmanSean, HVAC Technician replied 11 months ago
HvacmanSean
HvacmanSean, HVAC Technician
Category: HVAC
Satisfied Customers: 238
Experience: Owner HVAC company
Verified

Good afternoon, Im sean and look forward to helping you,

Do you have the model number for this unit

Ask Your Own HVAC Question
Customer reply replied 11 months ago
it's 50TCQD09D35S5A0
Customer reply replied 11 months ago
no
HVAC Technician: HvacmanSean, HVAC Technician replied 11 months ago

I will not be able to assist with this particular set up, I will opt out and another expert will hopefully grab this, Please don't respond until someone else joins on!

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, tell me in detail about the board, did it explode, burn or just cease working. Tell me if you can run the compressor by pushing the contactor bar in with the tip of an insulated screw driver.... if so,... remove the two wires that run to the condenser fan motor and measure the resistance across them with an ohm meter.... next measure ohms between each of the fan motor wires and the copper tubing on the unit.

.

Let me know what you can find, we can go from there.

Ask Your Own HVAC Question
Customer reply replied 11 months ago
thanks phil will get back to you with results seems like you think it could be a bad load.
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago

Yes that is correct I suspect a bad load (shorted fan motor windings) a bad fan motor run capacitor would not ruin the defrost board.

If the compressor will not run, but does not trip the breaker, its run capacitor might be bad as well, especially if you are using a dual run capacitor. ( comm connection in the middle of it, and fan and herm on the opposite sides)

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a question regarding my Rheem Heat Pump/AC Model RPQL
I have a question regarding my Rheem Heat Pump/AC Model RPQL 024JEZ … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
York Heat pump condenser fan keeps shutting off replaced run
York Heat pump condenser fan keeps shutting off replaced run capacitor replaced fan motor and the board and still shutting down after about 10-15 min could a bad compressor cause this … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
3 amp fuse blowing on air handler board....narrowed it down
3 amp fuse blowing on air handler board....narrowed it down to red wire out to heat pump.... red wire traces directly over to defrost board...I see a little discoloration on two resistors on the board… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
My relatively new furnace won't come on. Installed about
My relatively new furnace won't come on. Installed about four months ago. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a carrier rtu. Runs fine for 5 minutes then shuts down
Have a carrier rtu. Runs fine for 5 minutes then shuts down cooling. Heat pump with no strip heat. Thermostat is calling for cool. Indoor fan is running. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
My Payne heat pump is blowing the 5amp fuse and today the
Hi Pearl. My Payne heat pump is blowing the 5amp fuse and today the condenser was iced up. I replaced the defrost thermostat yesterday but the problem reoccurred last night. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Plus 80t model 312. error code 13. what can i do to fix?
Hi. Plus 80t model 312. error code 13. what can i do to fix? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Praise the Lord & good evening: My son has a heat pump
Praise the Lord & good evening: My son has a heat pump unit that has the name of the unit and the schematic painted over. The condenser fan does not come on, but the compressor does come on.… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
1. Im the building owner. 2. I have two identical Reznor
1. I'm the building owner. 2. I have two identical Reznor gas-fired hot air systems with 10-tons of a/c attached. One is for the first floor, the other is for the second floor. 3. 3-phase power from o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
im working on a trane model 4tee3f37a1000aa that keeps blowing
i'm working on a trane model 4tee3f37a1000aa that keeps blowing the 5A fuse between the transformer and the ICM fan conrol. Any idea what might be causing this? When I replace the fuse and reprogram t… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Heater and Air Conditioning went out about a month ago. No
Heater and Air Conditioning went out about a month ago. No power is getting to either unit. Checked the circuit breakers, checked the furnace power switch, checked and changed the filter, replaced the… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
I have a Trane XL90 TUC series from 1987 that stopped working
I have a Trane XL90 TUC series from 1987 that stopped working yesterday. The exhaust fan turns on, the igniter glows, but no flame. Today is the coldest day of the year so far, any suggestions?… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
I have a Trane XE 90, 75,000 BTU unit with AC purchased and
I have a Trane XE 90, 75,000 BTU unit with AC purchased and installed in 1999. Due to the very hot weather, the AC has been running a large percentage of the time. Now that it's cooler, I've noticed t… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Bryant 6 ton rooftop unit model 580cpv072074 that
I have a Bryant 6 ton rooftop unit model 580cpv072074 that does not blow cold. The main blower [squirrel cage] cycles ok however no compessor. The contactor [s] seems to be ok as they move up & down. … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Need help with Carrier package unit troubleshooting.
I have a rooftop Carrier package unit and cant get compressor(s) to run except when pushing contactors. Fan and blower come on and contactor makes about one second contact then releases. Checked limit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
just installed a model gy8s-uh as soon as i hook up the thermostat
just installed a model gy8s-uh as soon as i hook up the thermostat wires red to red white to white the fuse on the control board blows . what is the problem… read more
Zev Simfukwe
Zev Simfukwe
High School or GED
23 satisfied customers
This is what happened to me and sounds suspect. Can anyone
This is what happened to me and sounds suspect. Can anyone substantiate the repair bill and letter I have received? I have a 10 year old heat pump. A blown 5 amp control fuse for the low voltage circu… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Weil-McLain CG 4 and the transformer blew out. We
I have a Weil-McLain CG 4 and the transformer blew out. We replaced the transformer and got our heater to works for a couple minutes, but then it blew out again. I looked around online that people say… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x