Payne PH13NB60-A 5 ton TXV is in a hot attic...and turned in…

Customer Question
Payne PH13NB60-A 5...

Payne PH13NB60-A 5 ton TXV is in a hot attic...and turned in direction that I cannot see....Do you know what size allen to use for adjusting?....Freon was low, when I started charging superheat was + 59 deg.f and sub cooling was - 7 deg. deg. f . Charged till sub cooling is at name plate rating of 18 deg. f and super heat at 14 deg. f

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes ...air flow is normal

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

No, I think if I adjust the TXV ccw a litthe I will bring the super heat down to 7 or 8 degs then I may hve to charg a little to bring the sub cooling up...do you agree?

Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 11 months ago
Just forget the answer...I thought it was $5....for $36 I'll figure it out myself...keep the$5...
Answered in 5 hours by:
9/9/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 11 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. Sub cooling and super heat are going to vary. With Payne and Carrier equipment sub cooling is the important one when charging. Just remember it can vary 2 to 3 degrees each way and it is ok. Let run a day and recheck. Russ

Ask Your Own HVAC Question
Customer reply replied 11 months ago
Just forget the answer...I thought it was $5....for $36 I'll figure it out myself...keep the$5...
HVAC Technician: gotoman for ac, HVAC Technician replied 11 months ago

Ok Thanks for using just answer

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Is it common to mount an expansion valve bulb in a vertical
is it common to mount an expansion valve bulb in a vertical position and will it work correctly … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Goodman 5 ton ac compressor installed 10/17 has a LOUD
My Goodman 5 ton ac compressor installed 10/17 has a LOUD groaning noise when it begins running, then quiets somewhat for rest of operation. A quieting blanket has been installed. What are my options … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
3 years ago a contractor install a 2 ton 16 seer condenser
3 years ago a contractor install a 2 ton 16 seer condenser and air handler for the second floor of my home In the summers hottest days in new york it is not able to cool sufficiently. only about an 8 … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
I have a 2.5 ton 11 seer coil with a 2 ton 13seer ac. if I
I have a 2.5 ton 11 seer coil with a 2 ton 13seer ac. if I change the fixed orifice or add a txv valve will that lower my supply air temp… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Wondering what my sub cooling should be on 3.5. Ton 410a. Goodman
Wondering what my sub cooling should be on 3.5. Ton 410a. Goodman gsz13042 with same size goodman aurhandler… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have only one degree F superheat on this 7.5 ton unit. i
i have only one degree F superheat on this 7.5 ton unit. i have tested the txv. i put the sensing bulb in a cup of ice water, the superheat went up! and when i put it in my palm, the super heat decrea… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
What is the best way to determine a TXVs performance and superheat? I
What is the best way to determine a TXV's performance and superheat? I recently had a unit converted from a piston to a TXV (it's a R410A system) for more efficiency and the unit has about a 40 foot l… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Why does my 14 SEER 3.5 ton Goodman Heat Pump compressor sound
Why does my 14 SEER 3.5 ton Goodman Heat Pump compressor sound like it is being slugged with liquid refrigerant at startup in the Heat mode? It is a R-410A unit. It sounds great in Cool mode. Have che… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
New heat pump shut down on high pressure, 650psi after 2 min.
New heat pump shut down on high pressure, 650psi after 2 min. of running. Cooling works fine 16 deg. diff. Why is this happening… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
York 5 ton outside unit, ADP 5 ton evaporator coil Installed
York 5 ton outside unit, ADP 5 ton evaporator coil: Installed with TXV System runs but unable to cool to desired temp, Called A/C tech. Here are the readings as best as I can make out from his writing… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,358 satisfied customers
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a variable speed air handler mod. # XXXXX Does this have a TXV and do you use the superheat or subcooling method for charging? What are reasonab… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a 2.5 ton split system heat pump. Both condenser and
I have a 2.5 ton split system heat pump. Both condenser and air handler is 2.5 tons, 1150 sq ft. Pressures are 138 suction, 370 head. According to the manual, superheat and subcooling should be 7-9 +/… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,358 satisfied customers
on this 5ton coleman i am getting 140 psi the super heat is
on this 5ton coleman i am getting 140 psi the super heat is 8 this indicates an over charge ? but the sight glass is flashing, what do you reccomend ?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a 4 ton heat pump that I bought used and I just finished
I have a 4 ton heat pump that I bought used and I just finished installing on my home, with sight glass and filter dryer. Started it up and charged runs 80 psi and 205 on high, sight glass not clear b… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Goodmam 4 ton, 16 SEER, R410A, 2years old. In the summer, in cooling mode th
I have a Goodmam 4 ton, 16 SEER, R410A, 2years old. In the summer, in cooling mode the suction press is 140 and a disch of 340. When switched to heat mode the pressures are almost equal (within 25 psi… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
home HVAC--how to determine proper freon level on system w/o
home HVAC--how to determine proper freon level on system w/o a throttling valve-- and should one be added to the system--R22 1996 yr units 2 and 3 tons --Carrier… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My AC is constantly running, just last year we had new ducts
My AC is constantly running, just last year we had new ducts installed and just recently re-insulated our attic and installed radiant barrier. We replace the filter every 30 days or so but still seems… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system.
I have a Rheem RAKA 048 condenser / RCBA 48 coil section system. System is 16 yrs old, had icing problems. Tech diagnosed system had "issues" with metering device, contamination in system, and possibl… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x