My Lennox Elite Series Gas Heater will not ignite, Only

Customer Question
My Lennox Elite Series...

My Lennox Elite Series Gas Heater will not ignite

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Only recently. The unit responded by turning the power off and on at the unit but now will not ignite. You heat a switching click noise but no ignition is achieved.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I have adjusted the thermostat putting the temperature a little higher than the ambient temperature and much higher, have put the fan on both auto and on but to no avail. The filter at the air return is clean.

Contractor's Assistant: Do you plan on doing the work yourself?

If possible. I don't want to get a servicemen out if it is only a simple remedy. Last night the unit was operating, producing heat before going off, when it was set on on rather than auto and blew cold air

Contractor's Assistant: Anything else we should know to help you best?

It was serviced less than two years ago

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 21 minutes by:
9/7/2017
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,391
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like the igniter module has failed, checking that will be the first step. Locate the ignition module on the wiring diagram glued to the inside of the blower access door, then remove the igniter and inspect the hot glow plate area for any cracks or thin black lines across the element. If you see any replace the module.

http://www.cozyparts.com

will have a new module all they need is the furnace model number.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I have inspected the inside of the blower access door. Therein a wiring diagram as you suggested but also advice from the manufacturer that only a licensed gas fitter should attempt repairs upon the unit. I advised Just Answer that I would attempt to do so if the works were simple. I do not view your suggested solution to my problem to be simple. It requires an expert assessment of the state of the igniter module and also the undertaking of works that the Manufacturer specifically restricts to being performed by a Qualified Person. Furthermore I have no doubt that were I to undertake the works you suggest and something goes wrong I would invalidate my insurance. I will now be doing as recommended by the Manufacturer, that is engaging a Gas Fitter.
Customer reply replied 8 months ago
No
HVAC Technician: Phil, Mechanical Engineer replied 8 months ago

Hello again, calling in a locally licensed pro will be a very good idea, that said, many home owners do some of the simpler repairs themselves and there is an entire industry selling them parts and books about how to do so.

.

You need Lennox dealers tech to do the work if you are going to hire the work done, a gas fitter without furnace experience will generally not be up doing the diagnosis, especially the electronic aspects.

If you need help finding a well rated Lennox dealer in your area, tell me which direction you are from the center of the nearest larger town or city and I will hunt one for you.

.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,391
9,391 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,391 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Honeywell CT87N and CT87K thermostat troubleshoot
Just installed honeywell CT87N AND CT87K neither will work. Heat comes on when 2 wires are touched together but not when run through thermostat… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Baxi Luna 3 comfort boiler. The problem Im having
I have a Baxi Luna 3 comfort boiler. The problem I'm having is that the hot water turns cold after a few minutes. This happens especially when i try to get a warm water temeperature by running both th… read more
Phil
Phil
Mechanical Engineer
9,391 satisfied customers
Weil McLain Gas boiler does not fire. What do I do?
I have a Weil McLain gas boiler, pilots lit but it won't fire off. I put 24 volt relay power to the main gas valve, the one with the two blue wires and bam it fired off and running good. But it is not… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
The pilot is out on my Burnham steam boiler. There is no
The pilot is out on my Burnham steam boiler. There is no on/off/pilot there is just an on/off switch on a pilot control box. Nothing I've seen references this type of pilot. Can you pls help me with t… read more
Bill
Bill
Service Mgr
100 satisfied customers
Regarding steam boilers wiring to pressure controls and
Regarding steam boilers wiring to pressure controls and switches … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Having a problem with my Weil Mclain boiler. It's hot but no
having a problem with my Weil Mclain boiler. It's hot but no heat to radiators … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Buderus GB142 wall hung boiler with in concrete floor
Buderus GB142 wall hung boiler with in concrete floor radiant heat. Boiler Temp is set at 135, the attached AM10 has the target temp point set at 135 as well and the base temp point at 110. On cold da… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a cg5 boiler for my home. The boiler ignites and runs
I have a cg5 boiler for my home. The boiler ignites and runs for 10 seconds or so, turns off for 1 or 2 seconds and then reignites, that happens over and over again for 30 minutes or so and then shuts… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
EcoTecplus 428 boiler,after reset boiler not coming on,but
ecoTecplus 428 boiler,after reset boiler not coming on,but pcb has power. … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Can you refer me to a Weill McLain boiler repairman? Boiler
Can you refer me to a Weill McLain boiler repairman? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Boiler not lighting. Control module 1013-200. Power light
Boiler not lighting. Control module 1013-200. Power light on, tstat circ light on, limit light flashes and motor runs, press sw light flashes twice. then motor shuts down and system waits about 30 sec… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
TACO SR506 Switching Relay is not turning on.
I have a TACO SR506 Switching Relay that won't turn on. The power appears to be off at the green light indicator but the boiler is on. This happened once before and I turned the boiler off at the brea… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How do I increase the water level in my furnace (the low water
How do I increase the water level in my furnace? (the low water cut off has kicked in)… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have a 15 year old VanEE HE2000 air exchanger and have never
i have a 15 year old VanEE HE2000 air exchanger and have never had any problems with the unit. Last week, the lights on the wall control unit began flashing continuously and the fan also runs continuo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have a baxi luna 310 fi and i am not getting hot water and
i have a baxi luna 310 fi and i am not getting hot water and heat both.… read more
canuck the pro
canuck the pro
253 satisfied customers
I have a Honeywell pressuretrol control installed on my boiler
I have a Honeywell pressuretrol control installed on my boiler as well. for some reason, though, the boiler shuts off due to the emergency shut-off controller (which I don't see the model name or numb… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x