My A/C blower is running by my outdoor fan doesn't run.

Customer Question
My A/C blower is running...
My A/C blower is running by my outdoor fan doesn't run.
Submitted: 11 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
9/7/2017
HVAC Technician: Phil, Mechanical Engineer replied 11 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,794
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello.

First make sure that the power is ON to the unit that sits outside.

Next use a multi meter to measure voltage between R and C where the thermostat wires connect to the printed circuit board inside the furnace, behind the blower access panel.

We can go from there without any time limits and as in depth as needed.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,794
9,794 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,794 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Billy. I have another issue with another hvac problem. We
Billy. I have another issue with another hvac problem. We need your help to solve problem.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a goodman A/C and a goodman furnace. A/C is only 1
I have a goodman A/C and a goodman furnace. A/C is only 1 year old. We have the house on the market, yesterday we had the A/C on for a inspection, after the inspection the A/C would not turn on. I res… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My A/C wasnt cooling, but the inside blower is working, blowing air, the outside unit wasn
My A/C wasnt cooling, but the inside blower is working, blowing air, the outside unit wasnt running, i shut power to AC on elec panel inside, and turned off the thermostat; then i founf the red reset … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have whites Rodgers 50a50-241 board. Ac is not working.
I have whites Rodgers 50a50-241 board. Ac is not working. Fan is working when on. No filter issues.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a Lennox cb 29m-21/26-1p. A/C blower was not working.
Have a Lennox cb 29m-21/26-1p. A/C blower was not working. Have replaced capacitor and blower motor. Outside unit is running, but blower still not working. What is next step or what else can be the pr… read more
Jason Whatley
Jason Whatley
60 satisfied customers
Our thermostat says stg 2 and won't turn on the a/c. We have a Honeywell RTHL2510/241
Our thermostat says stg 2 and won't turn on the a/c. We have a Honeywell RTHL2510/2410 programmable thermostat… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Our A/C is not working. The blower inside is working but the
Our A/C is not working. The blower inside is working but the compressor and the compressor fan is not running. It is getting power. If the relay on the compressor is bad won't the compressor fan still… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a YMGI Mini Split with an E1 Error and a HC code on
I have a YMGI Mini Split with an E1 Error and a HC code on the inside unit. What does this mean?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Ruud Heat Pump, about 4 years old. Blowing warm air all the
Ruud Heat Pump, about 4 years old. Blowing warm air all the time, even when thermostat is set to "OFF" or "A/C". Circuit board problem? Fixable by do-it-yourselfer?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
since installing new thermostat,the blower does not come on
since installing new thermostat,the blower does not come on with central air. I have oil heater.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We had a power outrage last night. This morning, after power
We had a power outrage last night. This morning, after power came back up, I went to re-program the thermostat , but it read "battery low". When I open to replace battery, there were no batteries!!! I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
New furnce and heat pump were installed in March of 09. Have
New furnce and heat pump were installed in March of 09. Have a Trane XR 13 Heat pump. Furnace label says International Comfort Products model FSM2X3600A1. Thermostat is set at 70 and it's 76 inside an… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
have a rental house with propane gas furnace with cooling;
have a rental house with propane gas furnace with cooling; compressor outside is running but there is no cool air flowing thru vents… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Trane T800 Series touch screen thermostat. I turned
I have a Trane T800 Series touch screen thermostat. I turned on the A/C and my inside temperature was 30..5 degrees C (I'm in Canada), although I feel cool air coming through my vents, the temperature… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I live in Arizona. Starting today at about 2pm, the A/C stopped
I live in Arizona. Starting today at about 2pm, the A/C stopped blowing cold air. I reset the A/C breaker at the panel, and after 5 minutes it started up again, blowing cold air. However, that only la… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
A/C not blowing cold air. Was fine 2 days ago! Outside fan
A/C not blowing cold air. Was fine 2 days ago! Outside fan not moving. Chg fiter...thought it would help, but no avail. What to do next before calling Sears???… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have installed a Honeywell programmable thermostat. The
I have installed a Honeywell programmable thermostat. The heat works fine, and after I installed the thermostat, the air conditioning works. Now the air conditioning/fan won't turned on no matter if I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My power went out and now the blower for my A/C isnt working.
My power went out and now the blower for my A/C isn't working. Is there a rest button or fuse on it? It's a ruud blower (and A/C) Model # XXXXX / Serial # XXXXX Thanks… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.