I have a Broan 21 ECM18electric furnace, and the fan does…

Customer Question
I have a Broan...

I have a Broan 21 ECM18electric furnace, and the fan does not start.

Contractor's Assistant: Do you have fuel in the tank? If so, is the shut-off valve open and the fuel clean?

There is voltage to blue wire pin 3 and input voltage to motor

Contractor's Assistant: Do you plan on doing the work yourself?

Hopefully

Contractor's Assistant: Anything else we should know to help you best?

Heaters cycle on off, furnace worked fine last fall and then was shut down for winter, when power re-applied it did not start. new control board install. Relay k7 energized putting 24 vac on pin 3 of motor

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 10 months ago
JA what has fuel got to do with an electric furnace, this startment gives me very confused vibs?
Customer reply replied 10 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 10 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 1 hour by:
9/6/2017
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the confusing vibes were from our automated assistant which did not realize you had an electric furnace, and thought for some reason it was oil fired.

I need a close up exceedingly well focused photo of the wiring diagram glued to the inside of the blower access door on your electric furnace, I will mark it up with some trouble shooting instructions.

.

Meantime here is link that covers the ECM motor trouble shooting procedures. You may also want to buy an ECM motor tester that I will link to later.

Click here please

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally..

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime so to speak.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Attach a close up photo of the wiring diagram glued to the inside of the blower access door and I will mark it up with trouble shooting instructions then follow up with step by step training and coaching until you have a solution.

.

Photo must be exceedingly well focused. Use the 'add files' link next to your send button to get the photo to me.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I have added a better copy of 21ECM18/20 diagram
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, CLICK HERE PLEASE

beyond that you will need the ECM motor tester, CLICK HERE.

call these people on the phone give them brand and model number of your furnace and tell them you need and ECM motor tester for that furnace Click here

.

Its time to locate the 'finish and rate your expert...' link and click on it to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... t\

.

That goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my simple answer so far positively.. and I will deliver that training and coaching to you All on the same dime so to speak.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I measured the voltage between N & G and got 124 volts ac. Between L & N voltage is 240 volts ac. Between L & N voltage is 124 volts ac. Depending on K7 and switch VS, The voltage measured between P1-C (24vac common out) to M Pins 1,2 or 3 voltage is 28 vac.I then opened up the back of the motor to check motor and resistance readings on the three pin connector on the motor are:
Pin 1, Pin 2, Pin 3 to ground are infinite. Reading between Pin 1 & 2, Pin 1 & 3 and Pin 2 & 3 all read 21.3 ohms.
HVAC Technician: Phil, Mechanical Engineer replied 10 months ago

Thanks, ***** ***** proven that there is power to the motor and that the DC three phase motor windings are good. the problem is with the electronic speed signal controls. You need an ECM motor tester that I linked to earlier to diagnose that.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
9,701 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,701 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My A/C is blowing hot air. I believe that last person who
My A/C is blowing hot air. I believe that last person who worked on my Ruud furnace disconnected my AC. I am trying to check to make sure wiring is connected correctly. Where should I start? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Question regarding a clicking noise I'm hearing between
Hi! Question regarding a clicking noise I'm hearing between cycles on my electric furnace. Furnace and heat are working fine . The relay was replaced in the fall but still makes this noise between cyc… read more
Phil
Phil
Mechanical Engineer
9,701 satisfied customers
My furnance wont ignite and l1 polarity fault code flashes
My furnance wont ignite and l1 polarity fault code flashes how do i fix to be able for furnance to start up … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
Trying to wire control panel board part numbercan't find a
Trying to wire control panel board part number(###) ###-####can't find a wire diagram. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I just hooked up a two zone controller with the original
I just hooked up a two zone controller with the original thermostat hooked to the independently powered zone controller and the HVAC wires also connected to it. When I energized the heat pump system a… read more
hvacdave84
hvacdave84
53 satisfied customers
Ducane Model CG95TB080D16C with three blink error. It's been
Ducane Model CG95TB080D16C with three blink error. It's been a very intermittent problem all winter. Resetting power a few times works occasionally. This time, no luck. When power is turned on, the in… read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
I have a Carrier heat pump with a x13 blower motor. It
I have a Carrier heat pump with a x13 blower motor. It oscillates but will not spin. 230 voltage at the connector. Shaft spins freely by hand. Motor leads give 7.9 ohms when connected… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a 5 wire furnace and air conditioner green,white,orange,red,black
Hi I have a 5 wire furnace and air conditioner green,white,orange,red,black and I am installing a White Rogers p200 that does not care about colours… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
New rheem combo pack wont turn on. I have a 240 volt supply
new rheem combo pack wont turn on. I have a 240 volt supply and it needs 208 volts. what do i do?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need replace Carrier condensor fan motor HC39 ML500-21 230v
Need replace Carrier condensor fan motor HC39 ML500-21 230v 50Hz EP-oz13..purchased 1982 in Australia… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am working on a Lennox G61MVP-60D-135-01 the problem I am
I am working on a Lennox G61MVP-60D-135-01 the problem I am having is the furnace will not run a cycle in the 1st stage burner kicks on but no main blower motor restarts for 10 minuets and 2nd stage c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Nordyne Model KG6RC-060C-12A Furnace faults with LED flashing
Nordyne Model KG6RC-060C-12A Furnace faults with LED flashing 4 times indicating ignition failure. Ignitor circuit reads 74-86 VAC at all times. Does this indicate a bord problem? What other tests can… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
The gas valve on my 11 year old Goodman GSMS060-3 furnace doesnt
The gas valve on my 11 year old Goodman GSMS060-3 furnace doesn't seem to open when I expect i to. I have a constant 14.74 VAC at all times except when the valve is suppose to open. After the glow ign… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a ComfortMake RPJ Super High Efficiency furnace which
I have a ComfortMake RPJ Super High Efficiency furnace which will not start. I can't find a wiring diagram or even a rudimentary description of how the controller works to try to diagnose it. The labe… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Just switched my Lennox Thermostat with a new Honeywell TH622
Just switched my Lennox Thermostat with a new Honeywell TH622 where does the orange wire go?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Trane XL80 - no flame. I have a 12 year old Trane XL80 furnace
Trane XL80 - no flame. I have a 12 year old Trane XL80 furnace that is not producing heat. The vent motor comes on, the igniter begins to glow, the gas valve 'clicks', but it doesn't look as if any ga… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
No Fan on my Magic Chef Exchanger, I have a alligator clip
No Fan on my Magic Chef Exchanger, I have a alligator clip holding down the contactor armature, outside unit is running, but no inside fan, green and blue thermostat wires have 13.6 volts measured acr… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I JUST SERVICED A TRANE TUD080 TWO STAGE GAS FURNACE, W/ VARIABLE
I JUST SERVICED A TRANE TUD080 TWO STAGE GAS FURNACE, W/ VARIABLE SPEED DRIVE MOTOR. WHEN I APPLY POWER TO FURNACE, THERE IS NO TIME DELAY, VENT MOTOR BEGINS TO RUN ON LOW SPEED. THE SECOND THE FIRST … read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x